Pipes and cables exposed on roof
Hi Hope someone can help. We've saved up and had a local installer put solar thermal on our roof for hot water. But the pipes and wires are visible on top of the roof at the front of the house as you walk/drive up to the house. They look all ragged and are just attached with lots and lots of cable ties. Is this normal? We've said we're worried birds/weather might damage them, and asked for the installer to cover them in some sort of tubing, but they have refused, saying they've always done it this way and have never had any problems. Does this look standard practice? Don't know as have never seen any other solar thermal pipes on roofs. Thanks, Michelle
Apologies for not responding earlier to this @michellec
There are three factors which dictate the pipe coverings for solar thermal:
- adequate insulation... especially on the heat output leading back into the house
- preventing ingress of rain
- preventing degradation by the UV component in sunlight
I can see how the installers have used a secondary layer of plastic to keep rain and sunlight off the inner insulation.
So they're clearly aware of the issues.
But I don't understand why they didn't use UV-resistant nitrile-rubber insulation in the first place.
That looks like the standard black Class-O closed-cell insulation, but is usually marked specifically for 'solar' or 'external'.
In any case, it's still important that the upper end of the insulation tube is sealed, usually with mastic.
Otherwise rain will get between the insulation and the pipe. As it runs out, it carries away the heat.
I don't like seeing nylon cable ties used on insulation because it compresses the 'foam', reducing its insulating properties.
Cable-ties can also become brittle in sunlight.
The sides of the split in the insulation should be stuck together.
If the split doesn't already have pre-glued strips, then apply your own glue.
The correct glue for nitrile rubber is a contact adhesive.
Whereabouts are you in the UK?
The slate roof suggests Wales or the West Country.
Is the scaffolding still in place for you to get these photos?
Save energy... recycle electrons!
@transparent Thank you so much for replying. Yes the scaffold is still there (the roof they did is still leaking!) Can the insulation you describe be put on now? Could you recommend someone in the southwest (we are near Bude)? Many thanks, Michelle
Hi Michelle,
It's a pity you didn't mention that earlier.
There was a visit by a renowned exponent of good building practice holding a walkabout seminar at Nansledan earlier this week.
That's just 40-miles along the coast from you.
He'd brought along a couple of civil servants from London, to show them how things should be done...
Yes, the UV-resistant pipe insulation can be fitted now.
Are you sure that you don't want to put it in place yourself?
It's not that difficult a job.
Alternatively, you need a teenager with OCD!
I don't know of a builder/plumber who undertakes pedantically-correct work in Bude.
But the usual approach in the West Country is to ask at the post office or the pub.
This an area of UK where you can still get recommendations by simply talking with neighbours. 🙂
Save energy... recycle electrons!
@michellec I suspect @transparent means neat and tidy work, which you have reasonably expected. Plus with the detailed implementation to keep water out and heat in.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
No Michelle, I'm not making any assessment of your own skills 🤣
The issue here is that work you need doing is pretty straightforward.
There will plenty of people who would have a go at it.
But the quality of the work is important.
For many years I was working with a German software programmer.
His coding was amazingly slick and accurate...
... as was his grasp of the English language, because he used to correct my grammar.
That's the sort of approach needed to properly insulate those two pipes.
Save energy... recycle electrons!
@michellec, this is an area where the classic 80:20 rule is most evident - 80% of the benefit for 20% of the effort.
Any tradesperson will inevitably be applying the rule since their time costs you and them money, but the insulation job you describe is DIY- friendly enough that, with that bit of pedantry applied, brings that other 20% well within reach. It’s not that you have been pedantic thus far but rather that you could probably afford the extra time to apply the attention to detail that marks out a piece of work as first-rate.
Context matters, of course; I am pedantic to the point of anal retention with my woodwork but rather slapdash with any plumbing I (rarely and under duress) undertake.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 37 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 51 minutes ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 11 hours ago
-
My Samsung Gen6 (probably same controller as yours) onl...
By Old_Scientist , 21 hours ago
-
@drei When I was in local government we were of cours...
By JamesPa , 21 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 23 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
@rob-nezard you can see more of Drei's rad dramas here ...
By Mars , 23 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@drei I will say again that Im sorry to heat about your...
By JamesPa , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 2 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 2 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 2 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 3 days ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 3 days ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 3 days ago