Hi, Newbie here needing help. Initial alarm was CT8 & CT9 at 37C heat pump would run for about 5 minutes. Now multiple alarms CT1 through CT11 HP runs for 5 seconds. Any assistance greatly appreciated. There are more alarm displays but have reached maximum permissible.
I have run some checks. The power supply is good, the refrigerant is clear (not yellow) there is considerable pressure in in the refrigerant citcuit, the Ground Loop Pump works when on separate cable.
Question: Should the Ground Loop Pump come on when the Central Heating Pump comes on? Because it doesn't.
@heacol, do you have any insights or thoughts to answer AF1's question?
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
The ground loop pump must run when the heating is on, it may be a connection problem or the board has failed. You can as a temporary measure try connecting the brine pump to a separate source and then run the heat pump.Posted by: @af1I have run some checks. The power supply is good, the refrigerant is clear (not yellow) there is considerable pressure in in the refrigerant circuit, the Ground Loop Pump works when on separate cable.
Question: Should the Ground Loop Pump come on when the Central Heating Pump comes on? Because it doesn't.
Posted by: @heacolThe ground loop pump must run when the heating is on, it may be a connection problem or the board has failed. You can as a temporary measure try connecting the brine pump to a separate source and then run the heat pump.Posted by: @af1I have run some checks. The power supply is good, the refrigerant is clear (not yellow) there is considerable pressure in in the refrigerant circuit, the Ground Loop Pump works when on separate cable.
Question: Should the Ground Loop Pump come on when the Central Heating Pump comes on? Because it doesn't.
Thank you Brendon Uys for responding.
Should the Ground Loop Pump (GLP) come on with the other one - i.e. at the same moment?
I didn't think of trying to run the unit when I had the GLP connected to a separate supply - good idea. Should I leave the loom plug disconnected for this test?
The problem I have is that all the alarms now come on almost immediately after the Hot pump starts and lock the unit. Acknowledging the alarms makes no difference.
I could not see how to clear the error log in the manual, do you know please?
If after clearing the alarms the unit works with the GLP on a separate supply, why do you think caused no power to it from te unit?
Hi I was an engineer for ice b4 they went bust that many alarms could possibly be the rego, gt8 and 9 alarms only really an issue once they get 15 degrees apart normally a good service will clean out any magnetite, ice never fitted magnetic filters which all gshp and ashp should have as standard. You can call alto energy basically the ppl from ice who started again without the main director they do a call out service and repair depending where u are in the UK? I'm based Yorkshire and North East
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 46 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
@editor fortunately we have a boiling water tap in the ...
By bontwoody , 25 minutes ago
-
RE: Low Flow Rate Error - 8 kW Ideal Logic ASHP - Help!
@wh0am3ye super, glad your back up and running.
By ASHP-BOBBA , 2 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A DNO allowing 5kW export on a single-phase supply is u...
By Transparent , 2 hours ago
-
As promised, here's Cap'n Burrows delivering on his pro...
By Mars , 2 hours ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
@Fiona, I really don’t want to disappoint you, but I ha...
By Mars , 3 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
@dgclimatecontrol, hard to disagree with that. “Zero di...
By Mars , 3 hours ago
-
RE: Daikin 9kW to 8kW Swap Offer from Octopus
@matban I would have to check the CIBSE guide as we hav...
By ASHP-BOBBA , 3 hours ago
-
RE: Ecodan Energy Monitoring Pack
Hi @carpenterstation Did you ever resolve the energ...
By CAMorgan , 4 hours ago
-
RE: is a home battery without an EV worth it?
I would find it difficult to justify a battery without ...
By Batpred , 4 hours ago
-
RE: What is the Heat Geek Guarantee?
Very useful post, one observation: I can see why instal...
By Batpred , 5 hours ago
-
RE: Widespread failure of insulation installation
And there are different kinds I guess. One fri...
By Batpred , 5 hours ago
-
@drei - there is definitely something not right, notwit...
By cathodeRay , 5 hours ago
-
RE: Octopus tariffs - a quick comparison
Great summary, @majordennisbloodnok! I'd take the ho...
By Batpred , 6 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick I'm no expert... but believe your ASHP is...
By Tim441 , 8 hours ago
-
RE: Renewables & Heat Pumps in the News
Good News from NESO released today which d...
By Transparent , 8 hours ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
I agree with your last last sentence, but for another r...
By JamesPa , 9 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Just wanted to share my experience with this kit, as I ...
By Batpred , 13 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@jamespa And then there was the window company I had...
By davidnolan22 , 14 hours ago