IVT Greenline multi...
 
Notifications
Clear all

IVT Greenline multiple alarms

6 Posts
4 Users
0 Likes
1,073 Views
 AF1
(@af1)
Active Member Member
34 kWhs
Joined: 1 year ago
Posts: 3
Topic starter  

Hi, Newbie here needing help.  Initial alarm was CT8 & CT9 at 37C heat pump would run for about 5 minutes. Now multiple alarms CT1 through CT11 HP runs for 5 seconds. Any assistance greatly appreciated.  There are more alarm displays but have reached maximum permissible.

WhatsApp Image 2023 03 17 at 14.56.01
WhatsApp Image 2023 03 17 at 14.56.25
WhatsApp Image 2023 03 17 at 15.26.13
WhatsApp Image 2023 03 17 at 15.26.30
WhatsApp Image 2023 03 17 at 15.26.53
WhatsApp Image 2023 03 17 at 15.27.11
WhatsApp Image 2023 03 17 at 15.52.41
WhatsApp Image 2023 03 17 at 15.55.18
WhatsApp Image 2023 03 17 at 15.56.40
WhatsApp Image 2023 03 17 at 15.57.08
WhatsApp Image 2023 03 17 at 15.57.24
WhatsApp Image 2023 03 17 at 15.57.37
WhatsApp Image 2023 03 17 at 15.57.55
WhatsApp Image 2023 03 17 at 15.57.55
WhatsApp Image 2023 03 17 at 15.56.40

 

This topic was modified 1 year ago by AF1

   
Quote
 AF1
(@af1)
Active Member Member
34 kWhs
Joined: 1 year ago
Posts: 3
Topic starter  

I have run some checks. The power supply is good, the refrigerant is clear (not yellow) there is considerable pressure in in the refrigerant citcuit, the Ground Loop Pump works when on separate cable.

Question: Should the Ground Loop Pump come on when the Central Heating Pump comes on? Because it doesn't.


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
16595 kWhs
Veteran
Joined: 3 years ago
Posts: 2298
 

@heacol, do you have any insights or thoughts to answer AF1's question?

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU

Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk


   
ReplyQuote



(@heacol)
Prominent Member Contributor
1882 kWhs
Expert
Joined: 3 years ago
Posts: 328
 

Posted by: @af1

I have run some checks. The power supply is good, the refrigerant is clear (not yellow) there is considerable pressure in in the refrigerant circuit, the Ground Loop Pump works when on separate cable.

Question: Should the Ground Loop Pump come on when the Central Heating Pump comes on? Because it doesn't.

The ground loop pump must run when the heating is on, it may be a connection problem or the board has failed. You can as a temporary measure try connecting the brine pump to a separate source and then run the heat pump.

 

Professional heat pump installer: Technical Director Ultimate Renewables Director at Heacol Ltd


   
ReplyQuote
 AF1
(@af1)
Active Member Member
34 kWhs
Joined: 1 year ago
Posts: 3
Topic starter  

Posted by: @heacol

Posted by: @af1

I have run some checks. The power supply is good, the refrigerant is clear (not yellow) there is considerable pressure in in the refrigerant circuit, the Ground Loop Pump works when on separate cable.

Question: Should the Ground Loop Pump come on when the Central Heating Pump comes on? Because it doesn't.

The ground loop pump must run when the heating is on, it may be a connection problem or the board has failed. You can as a temporary measure try connecting the brine pump to a separate source and then run the heat pump.

 

Thank you Brendon Uys for responding.

Should the Ground Loop Pump (GLP) come on with the other one - i.e. at the same moment?

I didn't think of trying to run the unit when I had the GLP  connected to a separate supply - good idea. Should I leave the loom plug disconnected for this test?

The problem I have is that all the alarms now come on almost immediately after the Hot pump starts and lock the unit. Acknowledging the alarms makes no difference.

I could not see how to clear the error log in the manual, do you know please?

If after clearing the alarms the unit works with the GLP on a separate supply, why do you think caused no power to it from te unit?

 


   
ReplyQuote
(@fgasengineer1066)
New Member Member
20 kWhs
Joined: 4 months ago
Posts: 1
 

Hi I was an engineer for ice b4 they went bust that many alarms could possibly be the rego, gt8 and 9 alarms only really an issue once they get 15 degrees apart normally a good service will clean out any magnetite, ice never fitted magnetic filters which all gshp and ashp should have as standard. You can call alto energy basically the ppl from ice who started again without the main director they do a call out service and repair depending where u are in the UK? I'm based Yorkshire and North East 


   
ReplyQuote