IVT Greenline high pressure switch and electrical cassette errors
I have an IVT Greenline HT Plus C heat pump that is continually having errors when heating the hot water cylinder.
Both “Electrical cassette” and “High pressure switch” errors are happening several times a day. Acknowledging the error lets the heat pump continue, but clearly something is wrong. Previously I had problems with “High HTF Delta” that seemed to be this problem, which seemed to be fixed by changing the pipes.
Any thoughts on what needs to be done?

Hi, are you able to see the delta between GT8 vs GT9 temps? If this is more than 10 degrees then it would suggest that there is a flow issue again. When you changed the hoses did you flush out the system, especially the heat exchanger? I had the same errors as well as high HTF before I changed out the hoses, does the electrical cassette trip out?
The temperature diff remains fairly low during operation.
I didn't do the hose change myself, but I know that the radiator circuit was flushed out.
And yes, the "electrical cassette" error, as well as the "high pressure switch" error happen and cause the heat pump to cut out. Acknowledging the error resets things and allows the heat pump to run again (until the next error). These errors are happening several times a day.
This only happens when running the hot water. The radiators are not problematical (not that they are on now). I seem to recall that the same happened last year - these problems started once the radiator heating was no longer needed.
I know you will probably have tried this, but if the GT8/GT9 temp differential is low, it may not solve the issue? However, Pressure Switch High (HP) error indicates there is not enough flow over the heat pump. Check the heat carrier pump is working (it's the central heating type pump just to the left of the compressor), and try increasing the speed if it is. There is a switch on the pump, which has 3 settings, turn anti-clock to speed 3.
Also check that there is no air in the hot water tank. There is a thumb screw valve at the top of the tank.
As you have said that it's in hot water mode then there is no other valves or filters, unless your technician added these when changing the flexi-hoses?
Poor flow over the cassette would normally trip the overheat protector (not just tripping out the heatpump), this is a small button on the control box below the cassette. It is not obvious that this has tripped and even less positive to reset, which you do by pushing it back in.
Other than that it could be poor or corroded connections, or a problem with the PCB or sensors, sorry not very helpful.
How long ago did you change the hoses?
Here are the reported most common causes for both.
Common Causes High Pressure Switch error:
Blocked or dirty condenser coil (insufficient airflow)
Faulty fan (not expelling heat from the condenser)
Overcharged refrigerant
Non-condensable gases in the system
Faulty high-pressure switch
Closed or restricted water circuit (e.g., blocked heat exchanger)
Troubleshooting Steps:
Check outdoor fan operation – Is it running when the unit is on?
Inspect and clean condenser coils – Remove debris and dust.
Verify flow in water circuit – Check for pump operation, airlocks, or valve closures.
Measure refrigerant pressure – Requires a licensed technician.
Reset the system – Some models allow manual reset after the pressure drops.
Common Causes: Electrical Cassette
Faulty PCB
Loose or corroded electrical connections
Power fluctuations or unstable voltage
Failed sensor input or internal relay
Troubleshooting Steps:
Power cycle the unit – Turn off power for a few minutes, then restart.
Check cable connections – Look for loose terminals or moisture in connections.
Inspect PCB for burnt spots or corrosion.
View error code specifics – IVT systems often display a numeric code; let me know the code for detailed steps.
Check fuse and power supply – Ensure stable voltage and no blown fuses.
@abbote thanks for that advice.
There was a bit of air in the cylinder, but removing it hasn't helped.
The trip on the electrical cassette seems OK (in that it can't be pressed in).
The hoses were changed last summer.
OK, so when the HP comes on it becomes obvious.
It's on the setting on the right (one one where the curves are curves, not straight lines).
Your system seems to be more modern than mine, mine was installed in 2011. My advice would be to speak to Zak @Alto Energy. zak.crozier@altoenergy.co.uk, www.altoenergy.co.uk. www.altoenergy.co.uk Tel: 01993 220699. They were extremely helpful if you can't get hold of Zak try Sam Keats who is their design manager. They also sell spare parts. I got my hoses direct from them and saved over £500 from what a 'so called' heat pump expert maintenance company tried to charge me.
Currently viewing this topic 1 guest.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 34 Online
- 3,410 Members
Latest Posts
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 12 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
@cathoderay i will have to take a look at that, tbh as ...
By Grantmethestrength , 12 hours ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 13 hours ago
-
RE: Benefits of an extra horizontal loop for GSHP
I have no direct knowledge of GSHP ground loops but it ...
By Abernyte , 21 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 23 hours ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 24 hours ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 2 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 2 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 2 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 2 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 3 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 3 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 6 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 6 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 6 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 6 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 1 week ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 1 week ago