IVT Greenline high pressure switch and electrical cassette errors
I have an IVT Greenline HT Plus C heat pump that is continually having errors when heating the hot water cylinder.
Both “Electrical cassette” and “High pressure switch” errors are happening several times a day. Acknowledging the error lets the heat pump continue, but clearly something is wrong. Previously I had problems with “High HTF Delta” that seemed to be this problem, which seemed to be fixed by changing the pipes.
Any thoughts on what needs to be done?

Hi, are you able to see the delta between GT8 vs GT9 temps? If this is more than 10 degrees then it would suggest that there is a flow issue again. When you changed the hoses did you flush out the system, especially the heat exchanger? I had the same errors as well as high HTF before I changed out the hoses, does the electrical cassette trip out?
The temperature diff remains fairly low during operation.
I didn't do the hose change myself, but I know that the radiator circuit was flushed out.
And yes, the "electrical cassette" error, as well as the "high pressure switch" error happen and cause the heat pump to cut out. Acknowledging the error resets things and allows the heat pump to run again (until the next error). These errors are happening several times a day.
This only happens when running the hot water. The radiators are not problematical (not that they are on now). I seem to recall that the same happened last year - these problems started once the radiator heating was no longer needed.
I know you will probably have tried this, but if the GT8/GT9 temp differential is low, it may not solve the issue? However, Pressure Switch High (HP) error indicates there is not enough flow over the heat pump. Check the heat carrier pump is working (it's the central heating type pump just to the left of the compressor), and try increasing the speed if it is. There is a switch on the pump, which has 3 settings, turn anti-clock to speed 3.
Also check that there is no air in the hot water tank. There is a thumb screw valve at the top of the tank.
As you have said that it's in hot water mode then there is no other valves or filters, unless your technician added these when changing the flexi-hoses?
Poor flow over the cassette would normally trip the overheat protector (not just tripping out the heatpump), this is a small button on the control box below the cassette. It is not obvious that this has tripped and even less positive to reset, which you do by pushing it back in.
Other than that it could be poor or corroded connections, or a problem with the PCB or sensors, sorry not very helpful.
How long ago did you change the hoses?
Here are the reported most common causes for both.
Common Causes High Pressure Switch error:
Blocked or dirty condenser coil (insufficient airflow)
Faulty fan (not expelling heat from the condenser)
Overcharged refrigerant
Non-condensable gases in the system
Faulty high-pressure switch
Closed or restricted water circuit (e.g., blocked heat exchanger)
Troubleshooting Steps:
Check outdoor fan operation – Is it running when the unit is on?
Inspect and clean condenser coils – Remove debris and dust.
Verify flow in water circuit – Check for pump operation, airlocks, or valve closures.
Measure refrigerant pressure – Requires a licensed technician.
Reset the system – Some models allow manual reset after the pressure drops.
Common Causes: Electrical Cassette
Faulty PCB
Loose or corroded electrical connections
Power fluctuations or unstable voltage
Failed sensor input or internal relay
Troubleshooting Steps:
Power cycle the unit – Turn off power for a few minutes, then restart.
Check cable connections – Look for loose terminals or moisture in connections.
Inspect PCB for burnt spots or corrosion.
View error code specifics – IVT systems often display a numeric code; let me know the code for detailed steps.
Check fuse and power supply – Ensure stable voltage and no blown fuses.
@abbote thanks for that advice.
There was a bit of air in the cylinder, but removing it hasn't helped.
The trip on the electrical cassette seems OK (in that it can't be pressed in).
The hoses were changed last summer.
OK, so when the HP comes on it becomes obvious.
It's on the setting on the right (one one where the curves are curves, not straight lines).
Your system seems to be more modern than mine, mine was installed in 2011. My advice would be to speak to Zak @Alto Energy. zak.crozier@altoenergy.co.uk, www.altoenergy.co.uk. www.altoenergy.co.uk Tel: 01993 220699. They were extremely helpful if you can't get hold of Zak try Sam Keats who is their design manager. They also sell spare parts. I got my hoses direct from them and saved over £500 from what a 'so called' heat pump expert maintenance company tried to charge me.
Currently viewing this topic 1 guest.
- 26 Forums
- 2,152 Topics
- 47.2 K Posts
- 33 Online
- 5,671 Members
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
Yes, I see that now, but I wonder what its internal dia...
By cathodeRay , 4 minutes ago
-
RE: Electricity price predictions
It's windy down South today, which means our electricit...
By Scalextrix , 7 minutes ago
-
RE: Octopus tariffs - a quick comparison
I'm on Tracker at the moment and intend to remain on it...
By Scalextrix , 21 minutes ago
-
RE: is a home battery without an EV worth it?
In fairness when the grant went from £5000 to £7500, wh...
By JamesPa , 12 hours ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 12 hours ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 14 hours ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 18 hours ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 19 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
@transparent The only reason my DNO knows of these is b...
By Lucia , 23 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
🙁🙁🙁🙁🙁
By Lucia , 23 hours ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, interesting point. I’ve not focused much on Hea...
By Mars , 1 day ago
-
Intelligent Octopus Flux (IOF) Review
I promised @toodles that I would provide an update and ...
By Old_Scientist , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@julianc Our solar PV has produced more this August tha...
By Toodles , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 3 days ago
-
RE: How Do I Know When the Hot Water Has Run Out?
@transparent that is a very interesting suggestion, tha...
By GrahamF , 4 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Sorry to resurrect this thread, but it is sort of relev...
By cathodeRay , 4 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I missed your 22nd June post on this. I am sure it can ...
By cathodeRay , 4 days ago
-
Now posting on the right topic.... With general build...
By benson , 4 days ago