IVT Greenline high pressure switch and electrical cassette errors
I have an IVT Greenline HT Plus C heat pump that is continually having errors when heating the hot water cylinder.
Both “Electrical cassette” and “High pressure switch” errors are happening several times a day. Acknowledging the error lets the heat pump continue, but clearly something is wrong. Previously I had problems with “High HTF Delta” that seemed to be this problem, which seemed to be fixed by changing the pipes.
Any thoughts on what needs to be done?
Hi, are you able to see the delta between GT8 vs GT9 temps? If this is more than 10 degrees then it would suggest that there is a flow issue again. When you changed the hoses did you flush out the system, especially the heat exchanger? I had the same errors as well as high HTF before I changed out the hoses, does the electrical cassette trip out?
The temperature diff remains fairly low during operation.
I didn't do the hose change myself, but I know that the radiator circuit was flushed out.
And yes, the "electrical cassette" error, as well as the "high pressure switch" error happen and cause the heat pump to cut out. Acknowledging the error resets things and allows the heat pump to run again (until the next error). These errors are happening several times a day.
This only happens when running the hot water. The radiators are not problematical (not that they are on now). I seem to recall that the same happened last year - these problems started once the radiator heating was no longer needed.
I know you will probably have tried this, but if the GT8/GT9 temp differential is low, it may not solve the issue? However, Pressure Switch High (HP) error indicates there is not enough flow over the heat pump. Check the heat carrier pump is working (it's the central heating type pump just to the left of the compressor), and try increasing the speed if it is. There is a switch on the pump, which has 3 settings, turn anti-clock to speed 3.
Also check that there is no air in the hot water tank. There is a thumb screw valve at the top of the tank.
As you have said that it's in hot water mode then there is no other valves or filters, unless your technician added these when changing the flexi-hoses?
Poor flow over the cassette would normally trip the overheat protector (not just tripping out the heatpump), this is a small button on the control box below the cassette. It is not obvious that this has tripped and even less positive to reset, which you do by pushing it back in.
Other than that it could be poor or corroded connections, or a problem with the PCB or sensors, sorry not very helpful.
How long ago did you change the hoses?
Here are the reported most common causes for both.
Common Causes High Pressure Switch error:
Blocked or dirty condenser coil (insufficient airflow)
Faulty fan (not expelling heat from the condenser)
Overcharged refrigerant
Non-condensable gases in the system
Faulty high-pressure switch
Closed or restricted water circuit (e.g., blocked heat exchanger)
Troubleshooting Steps:
Check outdoor fan operation – Is it running when the unit is on?
Inspect and clean condenser coils – Remove debris and dust.
Verify flow in water circuit – Check for pump operation, airlocks, or valve closures.
Measure refrigerant pressure – Requires a licensed technician.
Reset the system – Some models allow manual reset after the pressure drops.
Common Causes: Electrical Cassette
Faulty PCB
Loose or corroded electrical connections
Power fluctuations or unstable voltage
Failed sensor input or internal relay
Troubleshooting Steps:
Power cycle the unit – Turn off power for a few minutes, then restart.
Check cable connections – Look for loose terminals or moisture in connections.
Inspect PCB for burnt spots or corrosion.
View error code specifics – IVT systems often display a numeric code; let me know the code for detailed steps.
Check fuse and power supply – Ensure stable voltage and no blown fuses.
@abbote thanks for that advice.
There was a bit of air in the cylinder, but removing it hasn't helped.
The trip on the electrical cassette seems OK (in that it can't be pressed in).
The hoses were changed last summer.
OK, so when the HP comes on it becomes obvious.
It's on the setting on the right (one one where the curves are curves, not straight lines).
Your system seems to be more modern than mine, mine was installed in 2011. My advice would be to speak to Zak @Alto Energy. zak.crozier@altoenergy.co.uk, www.altoenergy.co.uk. www.altoenergy.co.uk Tel: 01993 220699. They were extremely helpful if you can't get hold of Zak try Sam Keats who is their design manager. They also sell spare parts. I got my hoses direct from them and saved over £500 from what a 'so called' heat pump expert maintenance company tried to charge me.
Hi, apologies for piggybacking on this thread. I also have a C11 IVT Greenline Heat pump. The company that I got to install it back in 2011 are no longer in business and I always find it difficult to get anyone to service the pump or even ask for advice on the pump. I am having an issue at the minute with low pressure registering on the pressure gauge at the top of the pump. It is currently sitting at around 1/2 a bar and I think it is supposed to be set between 1 and 2 bar. I noticed it low and let air out of the water tank by loosening the nut at the front. The air is all out but I noticed the gauge dropping even lower after doing this. I have no idea how to get the air pressure back up to the correct setting. Would anyone be able to advice how to reset the pressure. Thank you.
Posted by: @get. I noticed it low and let air out of the water tank by loosening the nut at the front. The air is all out but I noticed the gauge dropping even lower after doing this. I have no idea how to get the air pressure back up to the correct setting. Would anyone be able to advice how to reset the pressure. Thank you.
I know absolutely nothing about this unit but it sounds like either it needs topping up with water or the expansion vessel needs to be repressurised. Is the air from the heating side or the ground loop side?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi, thanks for the reply. The air is from the domestic hot water cylinder that is contained inside the heat pump.
- 26 Forums
- 2,220 Topics
- 49.2 K Posts
- 210 Online
- 5,880 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
Interesting. So if you set blocade it can't know the c...
By JamesPa , 7 minutes ago
-
RE: Widespread failure of insulation installation
@jeff Along with a phone-in on BBC Radio Four today, mu...
By Toodles , 15 minutes ago
-
RE: What is the Heat Geek Guarantee?
@editor Thanks Mars, it is encouraging that Heat Geek a...
By colinc , 29 minutes ago
-
RE: 5 Star Service from Havenwise
Ok…a bit tumbleweed. From our own experience we were ...
By benson , 57 minutes ago
-
RE: Renewables & Heat Pumps in the News
Love the thought of it! simplification and sometimes me...
By Batpred , 58 minutes ago
-
RE: New Fogstar 15.5kWh upright solution
That's good news for the moment anyway. Can we try to...
By Transparent , 1 hour ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
Hi, I've always found Henri to be super helpful. From ...
By davidnolan22 , 1 hour ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk Will not even get started... The power of the ...
By Batpred , 2 hours ago
-
Sounds like you got it working for monitoring! With wel...
By Batpred , 3 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Thank you Aadil. We appreciate you taking the time to r...
By Mars , 3 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I must confess that I am unconcerned by the buffer/volu...
By vsmith1 , 6 hours ago
-
RE: Say hello and introduce yourself
@chris12 Let us hope that next year will be a bumper so...
By Toodles , 6 hours ago
-
RE: Isolating the system for a planned power cut
@batpred - that Solis installation page is too vague. ...
By Transparent , 6 hours ago
-
RE: Heating Turned Off but Radiators Still Warm
I love Necromancy... but to follow James, heat pumps WI...
By DREI , 7 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
12kW Gen 6 AE120BXYDEG (currently NOT performing well a...
By DREI , 7 hours ago
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
Buffer tanks can best be thought of as part of a 'produ...
By JamesPa , 9 hours ago
-
Very Much Awake – Renewing the Heating Industry One Step at a Time
Like any industry that touches so many lives, and is so...
By Aadil Qureshi , 10 hours ago
-
Ah.... I'd like to make a couple of observations: &nb...
By Transparent , 10 hours ago
-
RE: Battery storage to run Heat Pump.
Hats off to the ones that persist, @Transparent ! ...
By Batpred , 11 hours ago