@pooneil That can be moved quite easily into another room if necessary. Mine acts as a limiter in case the room gets too hot because of solar gain and also stops the heat pump cycling too much in very mild weather at low flow temperatures.
Will be interested to hear how it goes today with the changes you have made. I have a limit on how low I can take my flow temperature on the WC curve caused by the size of my radiators.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
This morning it's reading 20°. But what is measuring that number? Because if it's that controller unit on the tank, that is in a cupboard in the unheated utility, which I would guess is at least a couple of degrees lower than the house, which still feels uncomfortably hot, especially now in the bedrooms with the TRVs open. I certainly wouldn't be able to sleep in that temp.
Is there a way to move the controller wirelessly?
The thing I'm having trouble understanding is why the heating cycle wants to come on when there's a tank of hot water and it's +20° in the house. If I'm understanding the installer correctly, it's measuring the outside temp and supplying heat based on that, is that correct?
If so that makes no sense to me because it couldn't possibly know how much heat is being lost through the fabric of the house.
@bontwoody I have been looking at your graphs on emoncms. Could you explain how you are controlling the water pump? It seems to be running at a constant 8.9 l/min except, when a new cycle starts, there is a big spike in both pump speed and HP power output. There is no graph of room temperature, so what swing are you getting (if any) of room temperature?
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
I assume that's directed at me rather than bontwoody 🙂
I don't really understand what you are asking. I personally don't know how the water pump is controlled. The radiators seem to be constantly warm -- unless TRVs are turned down, and I'm only popping in to check every now and then.
@pooneil Unfortunately the controller is wired with a two wire cable. It is measuring your internal temperature so if its in a cupboard, thats not ideal.
If its too hot then I would lower the WC set points again and see how that goes. As I said its a bit of trial and error, ideally done on a very warm and very cold day to get you outlying flow temperatures right. All you need to do is match the heat loss of the house with heat input and that is determined from the flow temperature.
Domestic Hot Water heating and room heating are totally separate. Its one or the other not both at once and they use very different flow temperatures. You should have a schedule set up to do the DHW.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @pooneil
The thing I'm having trouble understanding is why the heating cycle wants to come on when there's a tank of hot water and it's +20° in the house. If I'm understanding the installer correctly, it's measuring the outside temp and supplying heat based on that, is that correct?
If so that makes no sense to me because
The answer to the first question will (hopefully) be because its cold outside and the heat pump is (effectively) preparing for the effect of the cold outside on the house (which responds slowly so it needs to prepare in advance).
The heat pump does know pretty well how much heat is being lost through the fabric of the house, because this is proportional to inside temperature - outside temperature (ignoring solar gain).
The whole principle of weather compensation is to measure the outside temperature and supply heat dependent on this figure, on the assumption that you want a constant inside temperature. The advantage of this over simply measuring inside temperature is twofold namely
- If correctly adjusted it ensures the lowest possible flow temperature consistent with heating the house = greatest efficiency and greatest comfort
- Because outside temperature is a leading indicator, unlike inside temperature which is a lagging indicator, it makes for a more stable and more reactive control loop (there is a whole branch of engineering called 'control theory' behind this statement)
Weather compensation is not unique to heat pumps, boilers also have it. For some (suspect) reason known only to plumbers we don't typically enable it in this country, but others do and in some, more enlightened, countries its been mandatory for many years. As a consequence of our decision not to enable WC on boilers we have, since the introduction of condensing boilers, typically paid ~10% more for our heating than we needed to , and 'enjoyed' poorer comfort as a result.
To make weather compensation work (and it does work) you need to follow this procedure to adjust your WC settings, ideally when its consistently cold outside (ie now isnt the best time to do it, so you can start now but may need to revisit in winter)
1. Set all your TRVs and thermostats to max
2. Set your heat pump to run 24x7
3. Ensure your controller is set to run on pure water law
4. Adjust the high OAT end of the WC curve to (something like) OAT 20, FT 27
5. Slowly adjust the programmed FT at the low OAT end downwards until the house is just at the right temperature, making changes of a degree once per day (you can start faster and slow down as you approach the right value)
If rooms end up at different temperatures you may have to balance the radiators.
This procedure adjusts the WC to be as low as possible while heating your house, which is (more or less) the most efficient operating point for a heat pump
Once you have done this you can, if you need to, reinstate TRVs or the temperature sensor in the controller acting as temperature limiters (but not temperature controllers), particularly in rooms where there is solar gain. You can do various other tweaks if the above doesn't work perfectly in your house (in many it will work very well, in some it will generally work well but can be tweaked to make it even better). In all cases the above adjustment is the starting point
Essentially this is a long form version of what @bontwoody has advised above
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@heatgeek Hi, its run on pure WC, open loop system with a PWM controlled pump. The controller is in the living room and set to stop the heat pump if the room overheats.
Here is a graph showing room temperature
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I understood that the Samsung Gen 6 does not have PWM pump control so your system is not a simple, straight-forward installation. You have a third-party PWM controller?
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
@heatgeek No. I can confirm it does have the facility for PWM control. Just an appropriate pump and a lead is needed
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Interesting. Thanks. This explains your steady DT control.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
@bontwoody Your Samsung Gen 6 has interesting behaviour which is different to the stereotypical belief. It boosts output at the beginning of the cycle to get temperature up quickly and then settles into a relatively constant flow (blue line in diagram). In the diagram it is modulating heat output from below 2kW to around 3kW but it does this by changing the DT interestingly. Popular belief would have it that the Samsung would modulate the flow and maintain a steady 5C DT. This is taxing my brain.🤨
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
- 22 Forums
- 2,008 Topics
- 43.8 K Posts
- 41 Online
- 3,166 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
@alsocold123456 I would have thought it would last a bi...
By ASHP-BOBBA , 8 hours ago
-
RE: Are Homeowners Being Silenced Over Faulty Heat Pumps?
This is sad to hear and should not happen, to give you ...
By ASHP-BOBBA , 8 hours ago
-
RE: Is my Samsung heat pump working too well?
@pooneil It sounds like the settings are all over the p...
By Heatgeek , 12 hours ago
-
ive had solar PV for just over 10 years and havent cons...
By AdamK , 12 hours ago
-
@editor Thank you for the information,do you have any i...
By Potatoman , 12 hours ago
-
@cathoderay Years ago (40+) I enquired about moving our...
By Toodles , 15 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
I didn't realise that Samsung even had customer support...
By JamesPa , 15 hours ago
-
RE: New Heat Pump - mixer shower pressure
Just a little update, I eventually decided to put a pre...
By Spanners , 20 hours ago
-
RE: Grant Aerona fine tuning advice needed
@grantmethestrength thank you interesting numbers. Did...
By Stopbar , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Our March generation was 133% of our PVGIS prediction a...
By Old_Scientist , 1 day ago
-
RE: Setback savings - fact or fiction?
I'm not a statistician, but I have had to use statistic...
By cathodeRay , 1 day ago
-
@jamespa thanks. I will take some time to make a head-t...
By Eliuccio , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@matthew_w It's a complex area and every case is diff...
By JamesPa , 2 days ago
-
RE: Multiple simultaneous connections to Samsung R290 heat pump via Modbus
Thanks for the various replies. I've tried to summari...
By Angus , 3 days ago
-
RE: Help me keep the faith with my installation
@adamk Yes, it's a good way and an alternative to (o...
By JamesPa , 3 days ago
-
RE: Frequent power outages in the Southeast – A sign of things to come?
That's a useful observation @majordennisbloodnok I'd ...
By Transparent , 3 days ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
Glad to hear that things are moving forward. The photo...
By JamesPa , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@judith Our peak is 5.4 kWp today and so far (16:35) we...
By Toodles , 4 days ago
-
RE: Forum updates, announcements & issues
@transparent I rather think that your LPA might refussi...
By Toodles , 4 days ago
Most Active This Week
# | Name | kWhs |
---|---|---|
1 | Mars | 364 |
2 | JamesPa | 150 |
3 | Pooneil | 113 |
4 | Majordennisbloodnok | 112 |
5 | Toodles | 108 |
6 | bontwoody | 101 |
7 | Heatgeek | 98 |
8 | cathodeRay | 94 |
9 | Transparent | 87 |
10 | Tim441 | 65 |