Why is my heat pump...
Why is my heat pump cooling my DHW?
6 Users
2 Reactions
SUNandAIR
(@sunandair)
Just wondered -can you lower the temperature when your hot water reheat starts?
You seem to only have a 5 deg drop. That also means the
start of the reheat is at 43 degC which might be a bit high.
I’ve got an 8.5kw HP and have the temp  set to 48degC with reheat kicking in at 38degC. That means it’s got a 10 deg drop and so, not switching continually to DHW. And perhaps equally  importantly the reheat temp starts when pipe temps roughly match the radiator temps if they’ve been heating the radiators.
I hope this is of interest
(@trbob)
Posted by: @sunandair
@grnmeira
“The cylinder seems to hold the temperature quite well. The problem happens when the system is totally idle, no demand for space heating, no use of hot water. When the temperature drops to 43 (due to normal loss) and the HP starts up to reheat the DHW back to 48, that's when it does the sharp drop.”
I think I’ve encountered something similar. Your paragraph above seems to describe my thoughts.
If HP was idle then the primary pipes are probably cold. HP is slow to build temp up so while water is circulating it’s re absorbing heat from your DHW cyl. This could be confusing for the system (for a while) since the return will be warmer than the flow.
perhaps try to coincide DHW reheat while the space heating has been running then the primaries will already have some heat in them. Just a thought from a newbie.
My DHW has always been like this, it drops about 7 or 8 degrees if I recall correctly when it starts heating, I attributed it to what SUNandAIR describes. Since summer I have it set to only heat at midday for an hour and do a manual start if more is required, so its not as noticeable because the tank is mostly cold anyway and I don't watch it like I did when it was first installed.
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
Page 2 / 2