What impact does compressor not running at low LWT have?
Helllo everyone, I'm new to the forum as we've just had a 6kW Daikin Altherma 3 Monobloc R32 ASHP installed by Octopus Energy in the last fortnight, replacing a gas boiler for DHW and CHW to radiators (all our radiators were replaced with doubles during the install).
It's been an interesting couple of weeks finding more and more information about ASHP on this forum and places like the Heat Geek YT channel. I've followed the advice to use weather dependent control, and to set an appropriate WD curve in our system, and it is keeping the house at a consistent 20C, which is perfect for us. Though clearly it is relatively mild right now, so I haven't been able to see if the curve is good for colder temps (ASHP geekery is making me want temperatures to go back to sub-zero so I can experiment some more, guess I'll just have to wait for next winter now!)
Early on we found that evening temperatures were a bit too warm for us, even with quite extreme setback values (which I understand is not best practice). The system had been commissioned with minimum LWT of 25C, I 've adjusted this setting to allow minimum LWT of 20C and since then our evenings have been more pleasent, with a setback of just -3C. In this video from Heat Geek (in what looks to be the Daikin training centre), he's going through the settings of the Altherma monobloc system and notes that the ASHP will disable the compressor at LWT below 25C and I've confirmed that is the case from the controller itself when our LWTs are below 25C.
My question to you knowledgeable folk is this; what is the impact of the ASHP disabling the compressor at the low LWTs that I've set?
Hello and welcome to the forum! It's great to hear that you've recently had a Daikin Altherma 3 Monobloc R32 ASHP installed and that you've been finding the information on this forum.
Regarding your question about the impact of the ASHP disabling the compressor at low LWTs, it's important to note that the compressor is the component of the ASHP that consumes the most energy. When the LWT falls below a certain threshold, the ASHP will disable the compressor to prevent it from running inefficiently and consuming more energy than necessary. In your case, since you've adjusted the minimum LWT setting to allow for a lower temperature, the ASHP will disable the compressor when the LWT falls below 20C instead of the default setting of 25C.
The impact of the ASHP disabling the compressor at low LWTs will depend on the temperature outside and how well-insulated your home is. If the outside temperature is mild and your home is well-insulated, the ASHP may be able to maintain a comfortable indoor temperature without the compressor running at all. However, if the outside temperature is very cold and/or your home is poorly insulated, the ASHP may struggle to maintain a comfortable indoor temperature without the compressor running, and you may experience reduced heating performance or even cold spots.
It's great that you've been experimenting with different settings to find what works best for your home and your preferences. If you do experience any issues with heating performance or comfort, you may want to consider adjusting the minimum LWT setting back to the default value of 25C.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Welcome @mortstar. 🙂 Compressors are very well protected in ASHPs, and user and installer configurable setting adjustments to the water side controls won't have adverse impact. But if you think about the physics of it, setting the minimum leaving temperature to be 20degC when you want the house at 20degC isn't logical. You're consuming energy via the circulating pump motor to pump water round a system that's not conveying any energy for either heating or cooling. That's probably why the OEM default setting is 25degC, a few degrees above the comfort temperature most people want their homes. The compressor might de-energise on minimum turn down anyway. Compressors tend to modulate down to about 25% minimum output. For heating loads lower than minimum turn down, they'll start to cycle the compressor on and off. That's why oversizing ASHPs isn't a good idea. Most ASHPs will run at part or low output in a typical heating season, only getting near full 'nameplate' output when heating a house from cold, or providing hot water generation.
The input power consumed by a compressor is the energy required to compress refrigerant gas from a low to a high pressure. The bigger the pressure increase, the more power is required. The evaporating pressure and temperature determines the low side pressure, and the condensing pressure and temperature determines the high side pressure. The evaporator temperature has to be lower than the outdoor air temperature in order to capture heat energy from outside, and the condensing temperature has to be higher than the leaving water temperature in order to transfer that heat energy into the heating system water. The greater the difference, the greater the power consumed. ASHP power consumption increases significantly in colder weather, but that's just physics - outside it's cold, but the house needs warmer water to provide sufficient heating. Running costs go up massively in the colder October-March months, which alarms people new to ASHP who have not run their system through a winter season. That said, you get very good efficiencies at other times & seasons so, over a year, you realise a net saving in energy bills. You're consuming massively less energy as a household too 🙂
- 21 Forums
- 1,964 Topics
- 42.6 K Posts
- 30 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Towel rails. An unexpected final hurdle
I had a similar issue but convinced the installer to le...
By Pie_Eater , 21 minutes ago
-
Cliff, welcome to the forum. You’re running into one ...
By Mars , 28 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 39 minutes ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 1 hour ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa @bontwoodyHeat loss calculations found and att...
By BAMi , 2 hours ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 3 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 4 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 4 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 6 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 6 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 8 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 11 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 day ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 2 days ago
Latest Topics
-
By cliffhanger 41 minutes ago
-
Heat Pump Sizing & Installation Costs
By Mars 14 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 15 hours ago
-
SolarPV tables / online calculator
By MichelleC 22 hours ago