Vaillant flow rates, Delta T, buffer sizing - trying to get ASHP running well but hit a brick wall.
The only way to be certain would be to physically trace the pipework from your heat pump to your buffer tank, and then from your buffer tank to heat emitters. Also ensure that any water pumps that may be installed are pumping in the correct direction.Posted by: @derek-m
Unfortunately where the pipes run under the floor would make it a very big job to trace the full length. The only pump in the system is in the UFH circuit. Doubting myself I went back with a different thermometer today - a physical one rather than ip-enabled sensors - so no chance of getting mixed up. This is what I found (temps in red)
@squonk It must be the case that the direction of flow on your two connections to/from the ASHP, on the left side of the buffer, is the opposite of what you show your diagram. The temperature is unarguable (you've measured it twice with two different thermometers) so it must be the direction. For you diagram to be 100% correct for temperatures and directions the buffer has to be inputting energy. Which (unless it has an immersion or similar - but it doesn't look like it?) it isn't. so the direction must be wrong.
so you must actually have this (the box is the buffer). which is going to issues with too much mixing in the buffer .all the flow inside the buffer will be vertical rather than mostly horizontal as per proper buffer use. this is nothing to do with the losses due to the way buffers work even when well implemented, this is worse.
BTW there must be another circulating pump on the heat pump side of the circuit. probably in the heat pump outdoor unit if you cant' obviously see it. given that it'll be in the outdoor unit, factory fit, it's extremely unlikely to be pumping the wrong way w.r.t the outdoor unit itself - we can reasonably assume that that is right. you 've said can't trace the pipework route under the floor and I'm not sure there's much point anyway. But it all points to flow direction into the buffer bring wrong. the obvious thing to do next is to look at reversing flow direction on the ASHP side into the buffer, as simply as you can. you want to get to this - note the flow inside the buffer is horizontal.
moving pipes on the input to the buffer will be hard work as its fixed pipework and in a tight space. I'd suggest that a larger project to turn the buffer into a volumiser and make it a single circulation loop, probably over the summer when you don't need heating, might be a time to look at this.
However, having just fitted my own outdoor unit , the thought occurs to me is that reversing the outdoor unit connections would be a) an easy mistake to have made b) easy to revert back. So there is a possible quick fix.
can you do this?
Do you have isolating valves somewhere in the pipework just before the flexible hoses? are you confident enough with a spanner to tackle this? if not then this is easy for any competent plumber, doesn't have to be an ASHP specialist.
1. close isolators
2 disconnect the hoses - at the house end or the outdoor unit end, whichever is easier. The water in the hoses and in the outdoor unit will leak out at this point and will be under enough pressure to spray for the first second or two. the isolating valves stop the whole houses worth leaking.
3 reverse hoses and reconnect
4. open isolators and check for leaks in the connections you just re-made
5. repressurise system . you need to replace the water that was lost in step 2. there'll be some air in it now as well.
6. run pumps if the ashp has a self-test mode to get the air out
7. test heating
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
The temperatures that you mention are all quite low, which is great for efficiency (but not for a warm house when it's cold out). What really matters for efficiency, is the flow temperature out of the ASHP itself - does it report this? The low flow multiplied by the low deltaT indicates that the heat out of the heatpump is low, I'm sure associated with a cold house. I don't think this is directly related to COP - COP is most affected by the flow temperature, which appears ok, which is a puzzle.
I had a quick look at the arotherm plus spec sheet, and it claims a sCOP of 3.6 even with a flow of 55C. It doesn't say, but I expect that the datasheet assumes weather compensation is enabled for that figure. I can't understand why weather compensation wouldn't be suggested for your setup.
How do you measure the COP? ASHP COP measurements are not MID certified so of unknown accuracy, and it's cheaper to design using less accurate parts. I recommend at least getting an MID certified electrical meter for the heatpump (£50 item). Better to get an MID certified heat meter too (£300 item).
Did you run the original storage heater solution before the ASHP - so do you know the heating requirement? You could look at your EPC (downloadable, just google)- it estimates heating loss/m^2.
I'm not familiar with the arotherm interface, but can you be absolutely sure that the internal immersion is off ?
Posted by: @squonkThe only way to be certain would be to physically trace the pipework from your heat pump to your buffer tank, and then from your buffer tank to heat emitters. Also ensure that any water pumps that may be installed are pumping in the correct direction.Posted by: @derek-mUnfortunately where the pipes run under the floor would make it a very big job to trace the full length. The only pump in the system is in the UFH circuit. Doubting myself I went back with a different thermometer today - a physical one rather than ip-enabled sensors - so no chance of getting mixed up. This is what I found (temps in red)
Ian has already come to the same conclusion, that the flow through the buffer tank is incorrect. To prove that the problem is not within the heat pump, which I also doubt, identify the water in and water out pipework at the heat pump and measure the temperature. The water out should obviously be warmer than the water in.
Personally I would be inclined to get your installer back to rectify the problem at their expense, since it may require new insulation and antifreeze top up. It may also educate them to confirm that equipment has been correctly installed before they dash rapidly off into the sunset.
Actually, paying more attention to the photo's, is this actually a buffer tank or thermal store? Can you provide a photo of any nameplate?
@derek-m the OP already said, the installer was out of his depth and has since retired so the "back to the installer" option doesnt work in this case. Hence my suggestion of hopefully a relatively do-able pipe swap. If the OP isn't comfortable doing it then any plumber can. good point though , if its got glycol in, more careful procedure needed than what I described.
also the OP said its a 45L vaillant buffer. their pics match what you get if you google that.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbank@derek-m the OP already said, the installer was out of his depth and has since retired so the "back to the installer" option doesnt work in this case. Hence my suggestion of hopefully a relatively do-able pipe swap. If the OP isn't comfortable doing it then any plumber can. good point though , if its got glycol in, more careful procedure needed than what I described.
also the OP said its a 45L vaillant buffer. their pics match what you get if you google that.
Thanks for the clarification. I'm old, and easily confused. 🙄
@derek-m no worries! have to say though this one is a perfect demonstration case for "don't assume; check the basics; measure it to be sure". Its only the OP's measurement of temperatures at your request 👍 that has pointed to what must be happening.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@squonk further to my previous note regarding pipe swap: If the system has glycol in its not as simple as I described. Plenty of info googleable for further reading. I am not able to advise on how to this. May be best to get a plumber used to handling glycol in.
If that is the case , thus adding complexity to the pipe swap and making it not a zero cost option, I would be tempted to hang on for a month or two until its warm enough to take the system down, then think about a rebuild with the buffer turned into a volumizer, single circulation loop.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Thanks for the various answers. The tank is a 45l buffer, no immersion or anything else. I’m not sure it’s as simple as swapping the pipes at the pump end (which would be easy) as I also have a 300l hot water tank which feeds off the pump via a diverted valve.
Getting the installer back is unlikely, so I will need to find someone capable to resolve it.
@squonk run the system in DHW mode and with your thermometers, see if the water going through the diverter valve, on what should be the Hot input to the DHW tank, is actually the hot ?
that tells you more about where the crossed pipe is.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I assume it does have glycol … but I also assumed the guy knew what he was doing, and look where that got me! There are numerous other problems with the install, so I have asked a proper company to quote for a complete re-install, I think that’s the only way I’ll know it’s done right.
- 25 Forums
- 1,442 Topics
- 30.2 K Posts
- 26 Online
- 1,225 Members
Join Us!
Latest Posts
-
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Yes, it is one of those two who first alerted me to the...
By IvanOpinion , 13 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
The fact that the MCB is rated 16A tells us what we nee...
By Transparent , 13 hours ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
Thanks, @editor. Ideally it’d be someone who would li...
By Majordennisbloodnok , 15 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Unless adequately controlled it could devour your bank ...
By Derek M , 16 hours ago
-
RE: Effect of buffer tank or volumiser on heat pump system
I think that you will find that the best location for a...
By Derek M , 16 hours ago
-
RE: ASHP Commissioning: What Questions Should I Ask the Installer?
@derek-m thanks - will look out for the point regarding...
By Declan90 , 1 day ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor @kenbone Thanks, I would be very interested ...
By Elton , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
This is all a bit too frequentist for my liking. The pr...
By scrchngwsl , 1 day ago
-
Relax with 4K drone footage of lawn mowing to a smooth Motown tune
Sending out some chilled weekend vibes to everyone. Lis...
By Mars , 2 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
The starting point of that discussion on Camelot-Forum ...
By Transparent , 2 days ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 2 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 3 days ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 3 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 3 days ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 3 days ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 4 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 4 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 4 days ago
Heat Pump Humour
Latest Topics
-
By David999 12 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 7 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 7 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago