(@samiebon1)
Trusted Member Member
217 kWhs
Joined: 12 months ago
Posts: 25
Topic starter  

@jamespa thanks James! Ive read through the manuals and found the Eco DHW setting on the Heat Pump controller. I've set it to Manual to see if that gives me the energy in tonight charge cycle.


   
ReplyQuote
(@judith)
Honorable Member Member
2549 kWhs
Joined: 1 year ago
Posts: 298
 

@samiebon1 our DHW gets to 48C with a heating temp of ~55C within ~ 45mins but it’s not usually empty (residual ~35 in bottom third of tank).

The layout of our house meant that some upstairs radiators had to be virtually off to ensure the flow went on to downstairs or else the bedroom radiator took all the water.

2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC


   
ReplyQuote
(@samiebon1)
Trusted Member Member
217 kWhs
Joined: 12 months ago
Posts: 25
Topic starter  

@judith did you manage to solve heating the downstairs? Or are you upstairs still off? ... Or when you mean 'off' do you mean the lock shields are only just open? 😄


   
ReplyQuote



(@judith)
Honorable Member Member
2549 kWhs
Joined: 1 year ago
Posts: 298
 

@samiebon1

 

When adjusting lockshields its worth bearing in mind that some have a tiny range over which the adjustment makes any difference.   Sometimes half a turn or less takes it from fully closed to fully open.  This makes getting it 'right' quite tricky. 

If you want to know more about this view Heat Geek on 'valve authority'.

 

 

This post was modified 2 months ago by JamesPa

2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC


   
ReplyQuote
Page 2 / 2



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security