@cathoderay do you have neighbours with similar buildings for their annual heating energy usages? in case the oil figures is some how off?
Posted by: @bristoljoedo you have neighbours with similar buildings
I do, but they either use different fuels (one still uses coal!) or heat their homes differently (different patterns and or warmth levels or main boiler eg Aga/Raeburn). My oil usage is a pretty solid figure, you can't really cook the books on usage because a tank is finite, what goes in and what comes out have to match, otherwise the tank will explode/implode!
When I used kerosene I used 3000 Litres per year so as a comparison the heatpump is a lot cheaper
@cathoderay Crikey, that is a staggering amount of electricity! The amount and cost doesn’t seem to equate to anything like your old system… and your heat output looks absolutely massive, so it’s hard to understand why you don’t seem to be feeling the benefit…
I have absolutely massive radiators in my very modest – I would say really quite small – semidetached ex-council house here up on the north-west coast of Scotland. I think that heat pumps are always more likely to offer good results in smaller properties.
I think that heat pumps are always more likely to offer good results in smaller properties. The insulation values in my house are not 21st-century, but they are still pretty good. Masonry cavity walls, now insulated, with 3 inches of stud/mineral wall layer on the inside. So the house doesn’t have brilliant thermal mass properties, but it does respond well to 35, maximum 40°C flow temperatures even on the coldest of mornings.
I am experimenting with the heat curve, currently set at 0.6, and if I set it to self adjusting mode, it usually sits around the .6 mark, plus or minus a point or two. So I drop it by .05 and 0.1 every few days – to try and get a reasonably average/ambient stretch of time/temperature - and I may return to this thread – or as you say, maybe head off to a new one - in a few weeks, if there is anything to report. Thing is, although it is still only February, we are moving towards spring, and the more daylight hours there are means the ambient temperature is going up by a degree or two every two or three weeks. Nights when it drops to 0 or below are quite rare here on the West Coast. I was going to say fortunately, but the other side of the coin is that it is often very wet, and when there are gales blowing, as they often do, you can literally feel the house struggling to hold onto temperature. Wind-chill is not something that only affects humans outdoors!
Posted by: @murchison2003When I used kerosene I used 3000 Litres per year
Again, the numbers (not you!) don't make sense. 3000 litres is very roughly 30,000 kWh. You say at the top of this page, you are currently using approximately 24kW (I think you may mean kWh) per day. If that is correct, that is roughly 24 x 30 x 9 6480kWh for a nine month heating season (you are in NE Scotland...), and at a 'normal' (S)COP of say 3.5 that comes out at 22,680 kWh. I know I have made some wild assumptions, but even so 22,680 and 30,000 kWh are a long way apart.
The point I am trying to make is that there seems to be something wrong with the numbers.
CathodeRay
Currently using 1 kWh for 24 hours = 24 kw (currently February)
I put in 3000 litres of heating oil every year.
I’m not a mathematician or whiz with formulas
I’m only saying that’s what I spent and that’s the consumption I have.
@cathoderay It does sound pretty screwy to be honest! I would normally expect fossil fuels to be more expensive than, for example, mains gas (not available here, so comparison with that is not possible) and for a well installed and commissioned air source heat pump to certainly be cheaper than coal, almost certainly cheaper to run than oil, and LPG possibly coming out of the mix fairly well.
There is another possible thing to consider – with fossil fuel boilers of any type, the flow temperature is naturally going to be, probably, at least 60°C, and at lower flow temperatures, with average radiators for such systems, you will never be warm enough. But if you open the door to the outside with such a system, because the heat source is pretty hot, room temperature recovers quite quickly. With the low flow temperatures of heat pumps, and with large rooms, especially if the calculations for radiator capacity hasn’t been done. Well, you might never feel warm enough. Then you bump the temperature settings up on the controller, then Bob’s your uncle, massive bills. However, even with the maximum flow temperature of my system set to 45°, I have never seen the flow temperature exceed 40°, as the weather compensation/heat curve calculates the right flow for the system.
With all of the TRVs fully open, it should be possible to regulate the temperature in the house without the system ever shutting off. This is what you should be looking for, absolute minimal cycling, whilst keeping the temperature where you want it. I am getting on in Age now, have a couple of health issues, and I have the house at 23° all day, set back to 21 at night. Even at these values, I think my power consumption is really very reasonable. Although compared to the cost of heating my old house down in Bristol, 600 miles south by road, I was gobsmacked at what I was spending on heating when I was first in Wester Ross. I got used to the cost of staying warm here very quickly, and stopped fretting about it when I realised how many of my friends and neighbours were spending similar amounts of money. It doesn’t necessarily get that much colder here than down south, but it is cooler for more of the year, and it is not unusual for the heating to come on at any point during the summer. It is not unusual for the heating to come on at any point during the summer. Days above 20 C are relatively rare, and often only come in single days. Our sunniest days are in spring, when it can often be very cold at night. And because houses here don’t benefit from much solar gain, it often remains cooler in the house than it is outside, so a day when it is 20 or 22° outside it might still only be 17 or 18° in the house.
Apologies again for my wordiness…
To @Yogabob's point, do you know anyone with one of those little thermal cameras that attached to smartphones? I got one (after borrowing one from a friend) and found a few gaps in loft insulation and draughts that I didn't know were there.
@murchison2003 - I don't doubt your observations on what you have spent at all, I am just trying to highlight the fact that it is often far from clear what is actually going on at the coalface so to speak.
I think you are probably using 1kWh per hour for 24 hours, making a total of 24kWh over 24 hours. I too find all this confusing, because the names overlap, and distinguishing between power (kW) and energy (kWh) is not intuitive. The way I try to remember the difference is power is about how powerful something is, how much work it can do in a given period of time, while energy is what is burnt, literally or figuratively, to do the work (heat the house, move the car, whatever the energy is being used for).
Thus a 2kW convector heater has a power of 2kW, and so is twice as powerful as a 1kW heater. If we run the 2kW heater for an hour, it will 'burn' at 2kW for an hour, and so 'burn' 2kW x 1h = 2kWh of energy. If we ran it for half an hour, it would 'burn' 2kW x 0.5h = 1kWh. Likewise, a 1kW heater running for two hours would 'burn' 1kW x 2h = 2kWh of energy.
The maths isn't complicated. 1 litre of kerosene contains just over 10kWh of energy (10.35 to be exact), meaning you can easily convert litres of kerosene into the amount of energy in kWh it will produce. At 100% efficiency, an oil burner using 3000L of kerosene will produce 31,050 kWh of energy (heat), I knocked a bit off for efficiency losses, but kept it at a round figure, 30,000 to keep things simple. Likewise, the heat pump energy output is a simple calculation, energy input multiplied by the COP, For each kWh in, you get 1 x COP kWH back. I then took your current daily use, 24kWh, multiplied it by 30 days and then by nine months, and then by the COP (I used 3.5 as being a more realistic overall COP) to get what your heat pump will put out per year, 22,680kWh. It is a very rough and ready calculation, but the results, 30,000 vs 22,680 are a long way apart.
Which brings us back to my original point, there is something seriously wrong with the calculations, especially in my case, but also in yours, and what's more, yours goes the other way (your case: oil needs more kWh to achieve the same heating, my case: heat pump needs more kWh to achieve the same heating). They should be the same, a kWh doesn't know where it came from or where it is going, if your house remains unchanged, the heat demand will remain unchanged, and the kWh needed to meet that demand will remain the same (with adjustments for different weather etc but over long periods of time, like a year, it will remain broadly the same).
The key point is our houses should need very similar amounts of heat energy delivered to heat our homes to our preferred level of comfort, wherever the kWh came from. The problem is the calculations don't confirm this. Ergo, there is either something wrong with the calculations, or I have gone mad.
There is in your case one remote possibility: your old oil boiler was extremely inefficient. It had to burn 30,000 kWh of energy to produce 22,680 kWh of delivered heat (the rest literally went up the chimney). I wonder, might that have been the case?
I don't have an easy answer to your oil/ASHP comparison. However, the average house using gas, uses about 12000kWh per year. From what you say your house is older and leakier than average. Is it really feasible that your older, leakier than average house used less than the average amount of energy to heat all of it to the average indoor temperature? What did your EPC say the heating requirement was?
I think it's possible that your COP calculation (or rather, Midea's numbers) is out by quite a lot. You have an ASHP that's struggling in cold weather, running flat out at (I think) quite a high flow temp. You also (I think) have a LLH or PHE. Your COP could easily be in the low 2s rather than the mid 3s you report. You say somewhere up-thread that your rooms may be a few degrees warmer with the ASHP than with the oil CH. If this is true and you're heating more of the house for longer (IIRC your heating is now on all night) then that's going to use a lot more energy than before.
I might be barking up the wrong tree but I think you need to (1) compare how you used your oil system - temperatures, rooms, timings - with what you do now with the ASHP and work out the difference in energy required and (2) Try and find a way to calculate/estimate/measure a more realistic COP.
A new thread sounds like a good idea.
Viessmann Vitocal 250-A in the UK
1 year ago
Vaillant Arotherm Settings for New Installation
1 year ago
Slash Your Heat Pump Bills Overnight
1 year ago
Does your heat pump calculate and provide you with a COP figure?
2 years ago
Daikin EDLA14D3V3 COP is now below 1
3 years ago
- 2,131 Topics
- 24 Online
- 5,656 Members
By Tim441 , 10 hours ago
Anyone still weathering it out with Agile?
Being curious, I have continued to monitor the daily ra...
By Toodles , 16 hours ago
By JamesPa , 20 hours ago
By Tim441 , 2 days ago
By Abernyte , 2 days ago
By Eliuccio , 4 days ago
By Scalextrix , 4 days ago
By JamesPa , 5 days ago
By Mars , 5 days ago
By Scalextrix , 5 days ago
By Toodles , 6 days ago
By Judith , 1 week ago
By Old_Scientist , 1 week ago