Vaillant Arotherm Plus Help needed
I installed Vaillant Arotherm Plus as per diagram, replaced gas boiler:Appliances: aroTHERM plus VWL < 10 kW, VWZ MEH 97 , VWZ MWT 150 Controls: VRC720, VR71, underfloor heating.
VRC720 shows now HP control module fault: anyone knows what is this about and which control module is this? Vaillant seems got no idea how to find the source of this fault. On top of it, getting F.1100 fault whenever VWZ MEH 97 gets switched on. I am in the middle of nowhere in france, getting someone to help going to be a nightmare and will cost me a fortune. ( i should have bought reliable asian appliances, grm made now looks like crap, sorry for my french). i checked all ebus cables, connections all setup correctly. do i miss smtg, like do i need to get another control installed, like vwz-ai vwl control module? thanks in advance
Posted by: @vlp2024I installed Vaillant Arotherm Plus as per diagram, replaced gas boiler:Appliances: aroTHERM plus VWL < 10 kW, VWZ MEH 97 , VWZ MWT 150 Controls: VRC720, VR71, underfloor heating.
VRC720 shows now HP control module fault: anyone knows what is this about and which control module is this? Vaillant seems got no idea how to find the source of this fault. On top of it, getting F.1100 fault whenever VWZ MEH 97 gets switched on. I am in the middle of nowhere in france, getting someone to help going to be a nightmare and will cost me a fortune. ( i should have bought reliable asian appliances, grm made now looks like crap, sorry for my french). i checked all ebus cables, connections all setup correctly. do i miss smtg, like do i need to get another control installed, like vwz-ai vwl control module? thanks in advance
I would suggest that you read through the attached guide and see if it throws any light onto your problems.
Posted by: @vlp2024I installed Vaillant Arotherm Plus as per diagram, replaced gas boiler:Appliances: aroTHERM plus VWL < 10 kW, VWZ MEH 97 , VWZ MWT 150 Controls: VRC720, VR71, underfloor heating.
VRC720 shows now HP control module fault: anyone knows what is this about and which control module is this? Vaillant seems got no idea how to find the source of this fault. On top of it, getting F.1100 fault whenever VWZ MEH 97 gets switched on. I am in the middle of nowhere in france, getting someone to help going to be a nightmare and will cost me a fortune. ( i should have bought reliable asian appliances, grm made now looks like crap, sorry for my french). i checked all ebus cables, connections all setup correctly. do i miss smtg, like do i need to get another control installed, like vwz-ai vwl control module? thanks in advance
Did you resolve your problem?
Feedback is required to prevent wasted effort.
@derek-m thank you for a wonderful guide, i know it i think by now by heart :). HP control module fault i found is due to bended cable. F.1100 i could not solve, just will not go away unless i set heater to external type. But now i got a new challenge: it will not run DHW and Heating same time, wonderful engineering, very clever. so, i am struggling now to solve this puzzle. for f1100 i probably have ot purchase new cut off thermostat. it costs around 110euros. I tried different circuits to get both heating and DHW same time with no success, ( heating goes via HEX) and tried circuits from 8 to 16. why engineers did come up with that idea. vaillant reminds me expensive but useless skin care for ladies: lots of marketing with horsesht but in reality suppose to heat only.
Posted by: @vlp2024@derek-m thank you for a wonderful guide, i know it i think by now by heart :). HP control module fault i found is due to bended cable. F.1100 i could not solve, just will not go away unless i set heater to external type. But now i got a new challenge: it will not run DHW and Heating same time, wonderful engineering, very clever. so, i am struggling now to solve this puzzle. for f1100 i probably have ot purchase new cut off thermostat. it costs around 110euros. I tried different circuits to get both heating and DHW same time with no success, ( heating goes via HEX) and tried circuits from 8 to 16. why engineers did come up with that idea. vaillant reminds me expensive but useless skin care for ladies: lots of marketing with horsesht but in reality suppose to heat only.
Heat pumps are not designed to provide central heating and DHW heating at the same time.
DHW heating requires a much higher leaving water temperature than central heating would normally need. The heat pump therefore cannot do both at the same time.
It would appear that the safety cut-out has operated, which is causing the F.1100 fault to appear. I would suggest you check to see if the fuse has blown, also see if there is a reset pushbutton that may need to be pressed.
@derek-m thanks Derek, any idea where that magic fuse i located? i imagine engineers did design this system with fuse in mind, but i could not find it (for cut-off thermostat). reset is clear, it was pressed with no luck.
Posted by: @vlp2024@derek-m thanks Derek, any idea where that magic fuse i located? i imagine engineers did design this system with fuse in mind, but i could not find it (for cut-off thermostat). reset is clear, it was pressed with no luck.
All that I can suggest is that you trace back along the cable to the place from which the heater is supplied.
Is this heater the DHW cylinder immersion heater or the back-up heater used to help out the heat pump in very cold weather? If it is the latter, do you actually need it?
Download and read through this document.
Posted by: @vlp2024@derek-m have you seen built in immersion heater in 97/6?
It is actually called a 'back-up heater' and is in addition to the immersion heater, which would be located in the hot water cylinder. The purpose of the back-up heater is to provide addition thermal energy if the outside heat pump cannot provide sufficient thermal energy. Obviously, it is direct electrical heating with a COP of 1, so should only be used when absolutely necessary.
It would appear that you probably have the choice of disabling the back-up heater by deselecting it, as I think you have already done, or replace the cut-out unit which would then make the back-up heater available for use once more.
The choice is yours to make.
@derek-m you just made entire arotherm plus technology useless, by notion it should heat both DHW and UFH in parallel. what i have so far achieved is having hydraulic stations to up cylinder and then auto switch to heating and so on, unfortunately no parallel operation. i am going to phone vaillant to clarify if this thing will ever work in parallel. (don't tell me this is not possible, mitsubishi, daikin and samsung do it). my cop so far is above 4.32, electrical heating? i got PV for electricity and solar to water to cylinder
Good morning,
Arotherm owner for 18 months here.
@Derek-m is indeed correct. Arotherm will do one, or the other, not both together. Ours is set for hot water priority so kicks the heating off for the time it takes for the water tank to heat.
its all about planning when is best. We heat our water in the early morning, cheap electricity, and in the afternoon when we get the highest solar gain.
atb
Drew
Posted by: @vlp2024@derek-m you just made entire arotherm plus technology useless, by notion it should heat both DHW and UFH in parallel. what i have so far achieved is having hydraulic stations to up cylinder and then auto switch to heating and so on, unfortunately no parallel operation. i am going to phone vaillant to clarify if this thing will ever work in parallel. (don't tell me this is not possible, mitsubishi, daikin and samsung do it). my cop so far is above 4.32, electrical heating? i got PV for electricity and solar to water to cylinder
If you wish to supply your central heating and DHW heating from one heat pump at the same time then please feel free to do so.
- 22 Forums
- 2,057 Topics
- 44.9 K Posts
- 38 Online
- 3,302 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
A lot of things can work if you are SCoP chaser, do the...
By Johnmo , 3 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo yes that is the current workaround to access th...
By benson , 3 hours ago
-
RE: Rate the quality of your heat pump design and installation
Yes the HP is running weather compensation and I’ve lef...
By Davesoa , 6 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 20 hours ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 21 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 2 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 2 days ago
-
RE: Is your heat pump insured?
@johnmo sorry it comes across like that. The post is au...
By KevinPotts , 2 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 3 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 3 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 3 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 3 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 4 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 4 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 4 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 4 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Took a while to find on the OFGEN site: ”The FIT sche...
By AgentGeorge , 4 days ago