Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Arotherm monobloc error f.788 - ASHP is not working!
@william1066 so my system did the experiment for me today.
I currently have a commissioned ASHP, the flow side goes to a 50L volumiser, then there is temporary shortcut (i.e. a bypass) back into the return side. I temporarily created demand so the ASHP has warmed up the water in the circuit and volumiser. the routes from the ashp's f+r circuit into the house are currently capped - there is no load on the ashp. the house is still on the boiler.
the graph starts when I got modbus working yesterday evening. RWT goes below 25 right at the start but nothing comes on. When Outside temp goes below 4C, the system switches the circulation pump on. But not the compressor. the lukewarm water in the circuit must be enough to satisfy the warmth needs of the outdoor unit. After that, the pump is leaving "off" gaps of 60 minutes then running for about 6-8 mins each time. I'm not sure what the "off" trigger is at the end of the "on" period. It'll be interesting to see how cool it gets before it puts the compressor on.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankI'm not sure what the "off" trigger is at the end of the "on" period.
Probably just "x" amount of time
Hi,
I have the same Error F788 did you finally fix it?
Coule you please tell me Howell did you do?
thanks for tour help
@bobshopsupreme did you ever get this matter sorted out?
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained – use AUDIO50 at checkout for 50% off.
@editor Hello. Yes and no! The original problem was indeed a dead water pump, killed by contamination in the circuit and possibly the power cut during freezing conditions (we do have anti-freeze valves). It took two months to get a replacement part.
We have then had another 2 years of fun with shutdowns caused by low flow due to under-dimensioned pipes, and then we still have a contamination issue which seems to be coming from the radiators. At the moment the flow rate gradually decreases over several weeks until the system cuts out with a low flow error, and then is fine again after cleaning the filters. They are trying to find the right product to protect the inside of the radiators because whatever inhibitor they have in there at the moment clearly isn't working.
@bobshopsupreme very interesting. Do you have a buffer tank or is it an open zone?
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained – use AUDIO50 at checkout for 50% off.
@editor We have a 200 litre buffer between the hydraulic station and the radiator and underfloor heating circuits. The flow rate problem was due to undersizing of the pipes between the outdoor unit and the hydraulic station. Those pipes have now been changed and it now meets the >2000l/hr nominal flow rate when the filters are clean.
-
Has anyone seen this problem before? Huge anticycling times
1 week ago
-
Heat pump done right first time? Installation in Kent.
2 months ago
-
Vaillant arotherm plus heat pump frost protection
3 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
2 years ago
-
ASHP Reliability Poll - Hall of Fame vs Hall of Shame?
2 years ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,744 Topics
- 64.5 K Posts
- 1,324 Online
- 7,148 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu Yup, and our daughter was sitting in her back...
By Toodles , 15 hours ago
-
@DavidB, I think @Majordennisbloodnok has already naile...
By Mars , 17 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks, however that's an answer to a subtly different ...
By JamesPa , 2 days ago
-
RE: Flushing system, cleaning and inhibitor
Yes, my 50L volumiser uses the two lower ports, so ther...
By Old_Scientist , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Such elegant symmetry. look at my lumpy bag of...
By Papahuhu , 3 days ago
-
RE: PV and battery long payback - sense check query
Quite probably not, but you can get a 32A relay and a S...
By JamesPa , 3 days ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s Look forward to making contact soon! Regards, To...
By Toodles , 3 days ago
-
I don't notice mine defrosting, and most of the time Im...
By JamesPa , 4 days ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
Kind of you, @calumm, but it was @f1p who did the heavy...
By Majordennisbloodnok , 4 days ago
-
RE: Electricity price predictions
2. As EV ownershp increases it'll certainly increase de...
By EtchedPixels , 5 days ago
-
I meant to say I cannot register my kit at Energyplus… ...
By Batpred , 5 days ago
-
RE: HomeTherma Is Live: A New Home-Energy Platform Built Around the Homeowner
Signed up!
By bobflux , 6 days ago