Vaillant Arotherm monobloc error f.788 - ASHP is not working!
@william1066 so my system did the experiment for me today.
I currently have a commissioned ASHP, the flow side goes to a 50L volumiser, then there is temporary shortcut (i.e. a bypass) back into the return side. I temporarily created demand so the ASHP has warmed up the water in the circuit and volumiser. the routes from the ashp's f+r circuit into the house are currently capped - there is no load on the ashp. the house is still on the boiler.
the graph starts when I got modbus working yesterday evening. RWT goes below 25 right at the start but nothing comes on. When Outside temp goes below 4C, the system switches the circulation pump on. But not the compressor. the lukewarm water in the circuit must be enough to satisfy the warmth needs of the outdoor unit. After that, the pump is leaving "off" gaps of 60 minutes then running for about 6-8 mins each time. I'm not sure what the "off" trigger is at the end of the "on" period. It'll be interesting to see how cool it gets before it puts the compressor on.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankI'm not sure what the "off" trigger is at the end of the "on" period.
Probably just "x" amount of time
Hi,
I have the same Error F788 did you finally fix it?
Coule you please tell me Howell did you do?
thanks for tour help
@bobshopsupreme did you ever get this matter sorted out?
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Hello. Yes and no! The original problem was indeed a dead water pump, killed by contamination in the circuit and possibly the power cut during freezing conditions (we do have anti-freeze valves). It took two months to get a replacement part.
We have then had another 2 years of fun with shutdowns caused by low flow due to under-dimensioned pipes, and then we still have a contamination issue which seems to be coming from the radiators. At the moment the flow rate gradually decreases over several weeks until the system cuts out with a low flow error, and then is fine again after cleaning the filters. They are trying to find the right product to protect the inside of the radiators because whatever inhibitor they have in there at the moment clearly isn't working.
@bobshopsupreme very interesting. Do you have a buffer tank or is it an open zone?
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor We have a 200 litre buffer between the hydraulic station and the radiator and underfloor heating circuits. The flow rate problem was due to undersizing of the pipes between the outdoor unit and the hydraulic station. Those pipes have now been changed and it now meets the >2000l/hr nominal flow rate when the filters are clean.
-
Vaillant arotherm plus heat pump frost protection
8 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
11 months ago
-
Has anyone seen this problem before? Huge anticycling times
11 months ago
-
ASHP Reliability Poll - Hall of Fame vs Hall of Shame?
12 months ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
12 months ago
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 79 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Inventor (Midea) Heat Pump short cycling advice
I installed the 80L tank (volumizer) things got better ...
By immunity , 5 minutes ago
-
RE: Mitsubishi Ecodan F8 error
I absolutely love this. This is the quintessential heat...
By Mars , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@papahuhu at the end of the day if you are happy with h...
By benson , 12 hours ago
-
RE: Can you recommend a Mitsubishi service engineer in the Rochdale area?
@dgclimatecontrol We'll all need annual servicing. How...
By Suzy-shadow , 12 hours ago
-
RE: Renewables & Heat Pumps in the News
@transparent I’ve understood your point now. The point ...
By Judith , 13 hours ago
-
RE: Octopus tariffs - a quick comparison
Does indeed need checking, @tim441. Neither Homely ...
By Majordennisbloodnok , 13 hours ago
-
RE: How not to install a heat pump
Delighted to hear that the buffer has been replumbed as...
By JamesPa , 14 hours ago
-
-
RE: Daikin 9kW to 8kW Swap Offer from Octopus
Yes but 9kW is similarly the 16kW derated. So 8kW subs...
By JamesPa , 15 hours ago
-
Actually, there's a rather greater degree of cattle-her...
By Majordennisbloodnok , 16 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@davidnolan22 So far as I can tell from the 'other p...
By JamesPa , 20 hours ago
-
RE: 5 Star Service from Havenwise
I keep getting havenwise ads on my Facebook feed, so cl...
By benson , 22 hours ago
-
Automation options to maximuse efficiency & ToU tariffs
I started a conversation with ChatGPT. What automation...
By Tim441 , 1 day ago
-
RE: 4 Year Ongoing Heat Pump Battle With Poor Heat Pump Installation
@jamespa Oh, I know some that are good and some not so....
By ASHP-BOBBA , 1 day ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
I don't know how many pumps you have but I guess it's o...
By JamesPa , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
That's just human nature unfortunately, not special to ...
By JamesPa , 1 day ago
-
@bontwoody how long has it been now since you started t...
By Mars , 2 days ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Yes, over the last few days I've been keeping a very cl...
By Steelbadger , 2 days ago
-
Absolutely. I am one of those members and I most certai...
By Majordennisbloodnok , 2 days ago