Vaillant Arotherm monobloc error f.788 - ASHP is not working!
@william1066 so my system did the experiment for me today.
I currently have a commissioned ASHP, the flow side goes to a 50L volumiser, then there is temporary shortcut (i.e. a bypass) back into the return side. I temporarily created demand so the ASHP has warmed up the water in the circuit and volumiser. the routes from the ashp's f+r circuit into the house are currently capped - there is no load on the ashp. the house is still on the boiler.
the graph starts when I got modbus working yesterday evening. RWT goes below 25 right at the start but nothing comes on. When Outside temp goes below 4C, the system switches the circulation pump on. But not the compressor. the lukewarm water in the circuit must be enough to satisfy the warmth needs of the outdoor unit. After that, the pump is leaving "off" gaps of 60 minutes then running for about 6-8 mins each time. I'm not sure what the "off" trigger is at the end of the "on" period. It'll be interesting to see how cool it gets before it puts the compressor on.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankI'm not sure what the "off" trigger is at the end of the "on" period.
Probably just "x" amount of time
Hi,
I have the same Error F788 did you finally fix it?
Coule you please tell me Howell did you do?
thanks for tour help
@bobshopsupreme did you ever get this matter sorted out?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Hello. Yes and no! The original problem was indeed a dead water pump, killed by contamination in the circuit and possibly the power cut during freezing conditions (we do have anti-freeze valves). It took two months to get a replacement part.
We have then had another 2 years of fun with shutdowns caused by low flow due to under-dimensioned pipes, and then we still have a contamination issue which seems to be coming from the radiators. At the moment the flow rate gradually decreases over several weeks until the system cuts out with a low flow error, and then is fine again after cleaning the filters. They are trying to find the right product to protect the inside of the radiators because whatever inhibitor they have in there at the moment clearly isn't working.
@bobshopsupreme very interesting. Do you have a buffer tank or is it an open zone?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor We have a 200 litre buffer between the hydraulic station and the radiator and underfloor heating circuits. The flow rate problem was due to undersizing of the pipes between the outdoor unit and the hydraulic station. Those pipes have now been changed and it now meets the >2000l/hr nominal flow rate when the filters are clean.
-
Vaillant arotherm plus heat pump frost protection
9 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
11 months ago
-
Has anyone seen this problem before? Huge anticycling times
12 months ago
-
ASHP Reliability Poll - Hall of Fame vs Hall of Shame?
1 year ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
1 year ago
- 26 Forums
- 2,255 Topics
- 50.2 K Posts
- 392 Online
- 5,915 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Thanks @grantmethestrength and @cathoderay . The reas...
By benson , 9 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@old_scientist and @allyfish , thank you both for this....
By colinc , 11 hours ago
-
RE: PV Panels on roof in Conservation Area
@jamespa Thanks for the input James, recording Oil usag...
By colinc , 12 hours ago
-
RE: Midea ASHP – how to set weather compensation
@dgclimatecontrol - you have awoken me from my several ...
By batalto , 12 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa mine seems changing albeit not by much, 3.21, ...
By AdamK , 13 hours ago
-
@majordennisbloodnok The migration hasn't started in th...
By HCas , 13 hours ago
-
RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems
Yep that's it, but the current design would re...
By DREI , 14 hours ago
-
RE: Buying large amp bidirectional RCD and RCBO
There won't be many RCBOs with a 100mA trip rating beca...
By Transparent , 14 hours ago
-
RE: Electricity price predictions
Because its what the investors demand, simple as that. ...
By JamesPa , 15 hours ago
-
RE: One room is colder than the rest of the house
@jamespa thanks for all the advice. Just so you know, ...
By AndrewJ , 17 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
@dgclimatecontrol I only have 1 cylinder and I can conf...
By Ecoste , 17 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
My MMI is in the loft but I checked the pump flow rate ...
By RadWhisperer , 18 hours ago
-
RE: Grant Aerona 3 and Drayton system questions
Good man/woman that plumber! Very likely....
By JamesPa , 18 hours ago
-
RE: New build installation query
@paullacey Hi I have managed to save the fil...
By JamesPa , 19 hours ago
-
Thanks for the response @batpred Your conversational ...
By Transparent , 21 hours ago
-
RE: What should we do with our Aga?
One slightly off-the-wall suggestion is that, if you li...
By Majordennisbloodnok , 22 hours ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
If you paid for any of the assessments try asking for t...
By JamesPa , 2 days ago
-
I've created a separate post here, wondering about radi...
By DREI , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@ecoste, @walnut-tree-cottage these are both great piec...
By JamesPa , 2 days ago