What is the maximum output of the Vaillant 7kW Arotherm Plus
Data badges are performance labels for heat pumps that show how much heat they can produce at different outdoor temperatures. For example, a heat pump might output 8 kW at 7C but only 5 kW at -3C. These numbers are crucial because they tell you how well your heat pump will perform in different weather conditions.
Since you have a Vaillant 7 kW Arotherm Plus. At 7C, it should output around 7 kW, which is its rated capacity. At -3°C, the output drops to about 5.5–6 kW, depending on settings.
Your heat loss is 5.58–6.8 kW, so the Arotherm Plus should be able to handle most of your heating needs. However, during extreme cold (e.g., below -3C), it might struggle to meet the upper end of your heat loss (6.8 kW), and you might need to rely on backup heating during those cold snaps.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
According the the Vaillant app, my 7kW Arotherm+ produced 7.6kW when the outside temperature was -7C.
Posted by: @adamkwhat is the max this HP can output? are they under the rating or over?
heat loss on my property is 5.58kw-6.8kw depending on surveyor.
There is a table here showing figures generally well above 7kW
However there has been recent speculation that these figures are gross output and do not take into account defrost cycles (which, if it is the case, is rather misleading).
https://community.openenergymonitor.org/t/vaillant-maximum-output-capacity-testing/27221
https://community.openenergymonitor.org/t/vaillant-maximum-output-capacity-testing/27221/62?page=4
It might be wise to ask the question explicitly of Vaillant Tech support if you are marginal. They are generally very helpful at least in my experience.
My heat loss is 7kW (or 16kW if you believe two surveyors!); the 7kW Vaillanthas worked for me in practice, Ive only had it since November though, design OAT-2.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks all. Think it should be ok. If not I’ll start upgrading rads in cold rooms.
On the Vaillant app our 7kW showed9.1kW at ~+2C. I suspect that is a bit on the high side of the measurement accuracy though.
@adamk your surveyor may suggest radiator changes for some rooms, but but you can decline.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
- 26 Forums
- 2,123 Topics
- 46.7 K Posts
- 97 Online
- 4,531 Members
Podcast Picks
Latest Posts
-
RE: Is your heat pump insured?
My home insurance renewal is due soon meaning I am doin...
By cathodeRay , 14 hours ago
-
New Vaillant aroTherm Plus in black - When will it come to the UK?
It looks like Vaillant are updating the aroTherm plus l...
By Sandy , 16 hours ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 16 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Ive called most of them over the years. By far the best...
By dgclimatecontrol , 17 hours ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 21 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
I've certainly seen that on their Ts & Cs page but ...
By Majordennisbloodnok , 2 days ago
-
RE: ASHP heat output monitoring
@carlo - not much better, is it. It looks more like a u...
By cathodeRay , 2 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 2 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 3 days ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 3 days ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 3 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
Cross references for @martingale Background discussi...
By Transparent , 4 days ago
-
@ecobaker May I ask a question of you please. I too hav...
By Papahuhu , 4 days ago
-
It's unclear to me how the Smart Control project work b...
By Transparent , 4 days ago
-
RE: Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
@pavel, this isn't about discrediting Chinese products....
By Mars , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 6 days ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 7 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 7 days ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 7 days ago