Underfloor heating: Diagrams with COP 'per water flow'
Anyone ever seen diagrams or tables that give COP per water flows; something like L/min versus COP (and of course for a certain temperature of water and Power...)
Just wondering how water flow impacts performance.
Posted by: @wvtienen1Anyone ever seen diagrams or tables that give COP per water flows; something like L/min versus COP (and of course for a certain temperature of water and Power...)
Just wondering how water flow impacts performance.
Unless its 'out of range' I dont think it materially affects COP (directly) which is why you wont see it plotted. The essentials of water flow are
- there must be sufficient volume flow to carry the required heat to the emitters at a deltaT of 5C, or the figure specified in the heat pump documentation. Your heat pump will probably complain if it isn't, unless the installer has fitted a buffer tank or bypass valve to mask the problem
- the linear speed of water in the pipes must be sufficiently low that you dont get noise in the pipes or worse still pipe erosion ~1 m/s max in noise sensitive areas, up to perhaps 1.5m/s in less noise sensitive areas. (In some circumstances these limits can be exceeded). I dont know the recommended flow rates through the actual heating pipes in UFH (which is in the title) as opposed to the feed pipes.
Some heat pumps adjust water flow to achieve a constant deltaT whatever the thermal load, others don't, it doesn't matter much.
There are a few more constraints if you are unlucky enough to have an LLH, buffer or PHE
COP varies mostly with OAT and Flow temperature. You cant do anything about the former, you want flow temp as low as possible.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I was in two minds whether to comment here or start a new post - I decided the latter as this was specifically about reference material for CoP vs flow temps, but it is probably related, given @jamespa response - see https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/flow-rate-vs-emitter-openness-and-cop#post-42153
Posted by: @rhh2348I was in two minds whether to comment here or start a new post - I decided the latter as this was specifically about reference material for CoP vs flow temps, but it is probably related, given @jamespa response - see https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/flow-rate-vs-emitter-openness-and-cop#post-42153
I read the post you referenced and Im not wuite sure what the question you are trying to answer is.
If its this "In summary, if I had the choice of a lower flow rate and opening up the emitters more, or a higher flow rate and them being more closed, which should theoretically be better for efficiency / reducing flow temps / cycling?"
Im not sure you really have the free choice or what you are assuming is kept constant/varied in the two scenarios
Im assuming that you want to keep the heat output from the emitters constant, to preserve the room temperatures.
The heat output from the emitters is determined by the difference between the average emitter temperature and IAT, not directly by flow rate.
However if you can increase the flow rate through the emitters you will reduce the deltaT across the emitters which means that the average temperature is closer to the flow temperature, which in turn means that the flow temperature can be lower (but only by a degree or so) for a given average emitter temperature. This will be more efficient and is one of the reasons we operate heat pumps at a lower deltaT (across emitters) than boilers.
This answer is independent of the emitter type.
Does that answer the question?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,367 Topics
- 53.7 K Posts
- 384 Online
- 6,042 Members
Join Us!
Worth Watching
Latest Posts
-
RE: A Smarter Smart Controller from Homely?
@toodles Just to follow up. I have made a little pro...
By Papahuhu , 13 minutes ago
-
RE: Setback savings - fact or fiction?
I agree, and I think there are two things in play here....
By cathodeRay , 18 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Do you have the reference for this? I have never seen i...
By cathodeRay , 2 hours ago
-
RE: Changing from 4-port buffer to volumizer
Thank you so much for your help. After New Years I'll g...
By Andy1618 , 3 hours ago
-
RE: Water Hammer After Heat Pump Install
That's really helpful. Yor last sentence confirms it'...
By JamesPa , 6 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
Having had another little look around, it seems Growatt...
By Majordennisbloodnok , 6 hours ago
-
Data Accuracy Problem: Daikin 8kW Heat Pump's Onecta App vs MMI Power Consumption
Good Evening. Has anyone found the following when usi...
By Nursethescreens , 19 hours ago
-
RE: Help needed with Grant Aerona 3 issues
First time posting so bear with me. Some bits that have...
By Adamp , 23 hours ago
-
RE: Mitsu PUHZ-SW120YHA + EHSC-VM20Uk - Performance
All understood. Obviously its a bit house de...
By JamesPa , 23 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@majordennisbloodnok This may be a better thread to ...
By Batpred , 2 days ago
-
RE: Best Heat Pump Brand in the UK
Last Call to Vote & Win! Haven't voted for your Hea...
By Mars , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
The video shows the JK balancer, but the connection of ...
By Batpred , 3 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 3 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
You are in essence right. Adia only works with selecte...
By JamesPa , 3 days ago
-
No, you haven’t missed out, @batpred. This thread’ll st...
By Majordennisbloodnok , 3 days ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
Also, though they weren’t prepared to match the price t...
By Toodles , 3 days ago
-
RE: How long will your energy contract last?
My INTELLI-FIX-12M-25-08-29 has less than 12 months to ...
By Batpred , 3 days ago