Underfloor heating: Diagrams with COP 'per water flow'
Anyone ever seen diagrams or tables that give COP per water flows; something like L/min versus COP (and of course for a certain temperature of water and Power...)
Just wondering how water flow impacts performance.
Posted by: @wvtienen1Anyone ever seen diagrams or tables that give COP per water flows; something like L/min versus COP (and of course for a certain temperature of water and Power...)
Just wondering how water flow impacts performance.
Unless its 'out of range' I dont think it materially affects COP (directly) which is why you wont see it plotted. The essentials of water flow are
- there must be sufficient volume flow to carry the required heat to the emitters at a deltaT of 5C, or the figure specified in the heat pump documentation. Your heat pump will probably complain if it isn't, unless the installer has fitted a buffer tank or bypass valve to mask the problem
- the linear speed of water in the pipes must be sufficiently low that you dont get noise in the pipes or worse still pipe erosion ~1 m/s max in noise sensitive areas, up to perhaps 1.5m/s in less noise sensitive areas. (In some circumstances these limits can be exceeded). I dont know the recommended flow rates through the actual heating pipes in UFH (which is in the title) as opposed to the feed pipes.
Some heat pumps adjust water flow to achieve a constant deltaT whatever the thermal load, others don't, it doesn't matter much.
There are a few more constraints if you are unlucky enough to have an LLH, buffer or PHE
COP varies mostly with OAT and Flow temperature. You cant do anything about the former, you want flow temp as low as possible.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I was in two minds whether to comment here or start a new post - I decided the latter as this was specifically about reference material for CoP vs flow temps, but it is probably related, given @jamespa response - see https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/flow-rate-vs-emitter-openness-and-cop#post-42153
Posted by: @rhh2348I was in two minds whether to comment here or start a new post - I decided the latter as this was specifically about reference material for CoP vs flow temps, but it is probably related, given @jamespa response - see https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/flow-rate-vs-emitter-openness-and-cop#post-42153
I read the post you referenced and Im not wuite sure what the question you are trying to answer is.
If its this "In summary, if I had the choice of a lower flow rate and opening up the emitters more, or a higher flow rate and them being more closed, which should theoretically be better for efficiency / reducing flow temps / cycling?"
Im not sure you really have the free choice or what you are assuming is kept constant/varied in the two scenarios
Im assuming that you want to keep the heat output from the emitters constant, to preserve the room temperatures.
The heat output from the emitters is determined by the difference between the average emitter temperature and IAT, not directly by flow rate.
However if you can increase the flow rate through the emitters you will reduce the deltaT across the emitters which means that the average temperature is closer to the flow temperature, which in turn means that the flow temperature can be lower (but only by a degree or so) for a given average emitter temperature. This will be more efficient and is one of the reasons we operate heat pumps at a lower deltaT (across emitters) than boilers.
This answer is independent of the emitter type.
Does that answer the question?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 21 Forums
- 1,960 Topics
- 42.5 K Posts
- 44 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@johnr Hadn't thought about secondary glazing - definit...
By BAMi , 2 minutes ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 31 minutes ago
-
RE: SolarPV tables / online calculator
By Gary , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 11 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 12 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 14 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 16 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 18 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 19 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 20 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 23 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
Latest Topics
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 31 minutes ago
-
SolarPV tables / online calculator
By MichelleC 7 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 19 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 22 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago