Underfloor heating: Diagrams with COP 'per water flow'
Anyone ever seen diagrams or tables that give COP per water flows; something like L/min versus COP (and of course for a certain temperature of water and Power...)
Just wondering how water flow impacts performance.
Posted by: @wvtienen1Anyone ever seen diagrams or tables that give COP per water flows; something like L/min versus COP (and of course for a certain temperature of water and Power...)
Just wondering how water flow impacts performance.
Unless its 'out of range' I dont think it materially affects COP (directly) which is why you wont see it plotted. The essentials of water flow are
- there must be sufficient volume flow to carry the required heat to the emitters at a deltaT of 5C, or the figure specified in the heat pump documentation. Your heat pump will probably complain if it isn't, unless the installer has fitted a buffer tank or bypass valve to mask the problem
- the linear speed of water in the pipes must be sufficiently low that you dont get noise in the pipes or worse still pipe erosion ~1 m/s max in noise sensitive areas, up to perhaps 1.5m/s in less noise sensitive areas. (In some circumstances these limits can be exceeded). I dont know the recommended flow rates through the actual heating pipes in UFH (which is in the title) as opposed to the feed pipes.
Some heat pumps adjust water flow to achieve a constant deltaT whatever the thermal load, others don't, it doesn't matter much.
There are a few more constraints if you are unlucky enough to have an LLH, buffer or PHE
COP varies mostly with OAT and Flow temperature. You cant do anything about the former, you want flow temp as low as possible.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I was in two minds whether to comment here or start a new post - I decided the latter as this was specifically about reference material for CoP vs flow temps, but it is probably related, given @jamespa response - see https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/flow-rate-vs-emitter-openness-and-cop#post-42153
Posted by: @rhh2348I was in two minds whether to comment here or start a new post - I decided the latter as this was specifically about reference material for CoP vs flow temps, but it is probably related, given @jamespa response - see https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/flow-rate-vs-emitter-openness-and-cop#post-42153
I read the post you referenced and Im not wuite sure what the question you are trying to answer is.
If its this "In summary, if I had the choice of a lower flow rate and opening up the emitters more, or a higher flow rate and them being more closed, which should theoretically be better for efficiency / reducing flow temps / cycling?"
Im not sure you really have the free choice or what you are assuming is kept constant/varied in the two scenarios
Im assuming that you want to keep the heat output from the emitters constant, to preserve the room temperatures.
The heat output from the emitters is determined by the difference between the average emitter temperature and IAT, not directly by flow rate.
However if you can increase the flow rate through the emitters you will reduce the deltaT across the emitters which means that the average temperature is closer to the flow temperature, which in turn means that the flow temperature can be lower (but only by a degree or so) for a given average emitter temperature. This will be more efficient and is one of the reasons we operate heat pumps at a lower deltaT (across emitters) than boilers.
This answer is independent of the emitter type.
Does that answer the question?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,055 Topics
- 44.8 K Posts
- 17 Online
- 3,289 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 6 hours ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 6 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Isn't that the whole point of homely - it does that fun...
By Johnmo , 8 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 9 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
@jamespa So settings to date are as follows for now. ...
By Alfapat , 9 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 10 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Hi, are you able to see the delta between GT8 vs GT9 te...
By abbote , 11 hours ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 18 hours ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 1 day ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 1 day ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 1 day ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 1 day ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Took a while to find on the OFGEN site: ”The FIT sche...
By AgentGeorge , 2 days ago
-
RE: why solar diverters for HW instead of the heat pump?
For me there are few factors why you may want to heat w...
By Johnmo , 2 days ago
-
RE: Hydronic plinth heaters and ASHPs
@editor yes I think so. It will be a while until I get ...
By benson , 2 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I’m an Aira customer with a 6kW Outdoor Unit in a small...
By KevinPotts , 2 days ago
-
RE: Is your heat pump insured?
@richard24738 good to hear. I’ll also review them this ...
By Mars , 2 days ago
-
RE: Warm weather and heat pumps.
Just looked at my WC setting, it is programmed for 25 D...
By Johnmo , 2 days ago