British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
I realise now that I was replying to an earlier message! I was replying to your brain knot comment. Sorry! It's not surprising you didn’t understand what I was saying. Well done for making so much progress and getting the right wattage pump and 2 bigger radiators out of Octopus!
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
I now have a radiator schedule - total output 5353w [with 6kw Daikin + Daikin water tank 180 litres] Yes, I have a couple more upgrades. [🤫]
They've designed for 50º and are absolutely refusing to budge on that.
The bathroom is keeping the towel rail and I'm adding a small aluminium 'designer' radiator at 493w @ d30 - my expense.
I think the rads now give me a bit of room for manoeuvre on the flow temps - what are your thoughts please?
Why is the bedroom rad over twice what is required yet the lounge barely covers the heat loss. I may be talking rubbish but logically doesn’t that say to keep your lounge at 21C your bedroom is going to be very hot unless you turn the rad off with a trv which defeats the purpose don't you just fit a smaller rad in the bedroom and you will need bigger in the lounge if you want to run at lower flow temps?
This is the reason they won’t lower the design flow temp as then the rads in the lounge won’t cover the heat loss.
Thats my interpretation hopefully someone else will come along and make more sense of it.
You are absolutely correct! They won't lower the design temp because they want to keep costs low.
I had a discussion on Twitter with one of their head honchos the other night - he freely admitted that they tried to plot a path that keeps installs lower cost.
The bedroom rad was upped because it's an office too but I agree about the living room it's a pain they're not bigger.
Basically what they're doing is slot-ins - they don't want to do any pipe work - even though my pipes are visible/easy access in my cellar.
Originally they were only going to change the two living room rads. The rest I've negotiated since.
@gary I can’t help feeling that the surveyors have a phobia about fitting the minimum size emitter that might possibly provide enough heat (as long as the system has a design temperature of 50 degrees C) in any given room. Maybe they fear that if they even suggest a larger emitter, the customer will run shrieking from the room TOO BIG - TOO BIG!
When our surveyor sized the emitters, I expressed my feelings that I wanted the emitters to be fit for the task as well as fit the room! As it happened, most of the emitters are the same width and height as the ones they replaced but deeper which I felt was a minor loss of space. I reviewed the list when I received their suggestions and *‘shrunk’ one and enlarged another - the result is very satisfactory to us, and we like it warm!
*The shrinking of one was because I knew the room stayed warm by conduction from the hall and the adjacent room and I felt the emitter left insufficient room to access drawers in a dressing table.
Despite MCS guidelines, I feel there should be more communication between surveyors and the users- a few minutes talk and explaining could save a lot of agro later! Regards, Toodles (Or was I just lucky?!)
Toodles, he heats his home with cold draughts and cooks his food with magnets.
hopefully the heat loss is less than calculated and the living room will be warm enough at lower flow temps not a lot else you can do you seem to have squeezed as much as possible out of them so kudos to you for that
@gary I agree. It's a lot better than it started out. I have been insistent throughout that 50º was passing the running & maintenance expense on to me.
I was miffed that it flies in the face of the entire theory of low flow, efficient heat pumps and I told them that. Repeatedly. 😁
But it has become a 'papal edict' from HQ I think.
The rads are a bit out of balance particularly those in the living room. However, it is a bungalow with all the rooms coming off a square central hall and hopefully leaving doors open & running a totally open loop system should allow me to level it out and run it at 40º at least. 🤞🏻
Posted by: @lucia@gary I agree. It's a lot better than it started out. I have been insistent throughout that 50º was passing the running & maintenance expense on to me.
I was miffed that it flies in the face of the entire theory of low flow, efficient heat pumps and I told them that. Repeatedly. 😁
But it has become a 'papal edict' from HQ I think.
The rads are a bit out of balance particularly those in the living room. However, it is a bungalow with all the rooms coming off a square central hall and hopefully leaving doors open & running a totally open loop system should allow me to level it out and run it at 40º at least. 🤞🏻
Overall you seem to have done as much as you can to get a good deal. In fairness to Octopus they have decided on a broad methodology and they are sticking to it. A minimum upgrade route compensated to some extent with tariffing has the merit that it gets the transition we need to make done at a price more people can afford. It could be argued these the latest building regs take a similar approach by specifying a max design temperature for the flow (whatever the heat source) of 55C, not ideal from the point of view of a later heat pump retrofit, but not a disaster.
I guess one might argue for a subtle variation, namely that those emitters which are upgraded to meet the chosen design temp of 50 should be sized for 45 or even 40 thus paving the way for future improvement. However otherwise it's a valid design philosophy imho, certainly no less valid than the 'rip everything you can out and start again' approach taken by the grant chasing fraternity, that seems to make up the majority of the industry.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I agree about their strategy. They're plotting a middle route. Their Cosy thingy is a step further along with that thinking. Heat Pump as plug-and-play gas boiler substitute.
I couldn't afford anyone else and I think that's fairly representative of lots of potential customers. The problem however, is that most people won't want to go deep into it and thus will be left running 50º systems that will cost them in energy bills. Lets hope Mr Miliband starts to shift the weight off electricity tariffs and onto gas.
Meanwhile, as someone pointed out in one of Mars' videos, this will then reach a level where it has grid impact.
@lucia My efforts stalled as the Octo surveyor did not supply enough information for the tech designers. So they want to resurvey next week. In the meantime I was contacted by an installer who is doing a survey on Thursday. I am hoping that this guy has practical experience rather than the Octopus guy who came from a software background. If octo come through (though maybe they will decline if the installation does not suit their rigid criteria) then I will upgrade more radiators myself so I can run way cooler than 50C. The next hurdle is which tariff to go for in conjunction with a battery or solar or even an EV!! I will update next week.
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
-
Vaillant arotherm plus heat pump frost protection
4 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
4 months ago
-
Daikin Error Code 7H05
6 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
6 months ago
-
Vaillant Arotherm monobloc error f.788 - ASHP is not working!
7 months ago
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 66 Online
- 3,353 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
Well we finished this month with an all time record! Ev...
By Andris , 7 hours ago
-
RE: 5 Star Service from Havenwise
Oh good! I was wondering when/if you might pick them ...
By Transparent , 9 hours ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
update - my old installer insisted on a heat loss of 11...
By MatWin , 10 hours ago
-
I agree it's not very helpful. Generally, the max heat ...
By Old_Scientist , 12 hours ago
-
RE: Commencing on an ASHP Installation Process
I think therein lies the problem. Ratio of quotes to i...
By JamesPa , 1 day ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
Hive and most other smart thermostats don't play well w...
By JamesPa , 1 day ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Thanks for the input. I've been running various experim...
By Grahamh-uk , 1 day ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet Hi, this sounds great is you are getting 5...
By ASHP-BOBBA , 2 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 2 days ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 3 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 4 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 4 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 4 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 5 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 5 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 6 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 6 days ago
Members Online
No online members at the moment