The good, the bad a...
 
Notifications
Clear all

The good, the bad and the not that great – my heat pump installation

224 Posts
15 Users
77 Reactions
21.1 K Views
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2130
 

There is also enough info there to calculate calculate power output, which is LWT/RWT delta t x flow rate/3.6 x circulating fluid specific heat (the divide by 3.6 is to get from m^3/h to litres per second.

Thus we get 6 x (0.54/3.6) x 4.2 = 3.78 which is close enough to the 3.83 shown. This suggests the flow rate is sufficient for that level of power output (another way of getting to that conclusion is to rearrange the equation to get the flow rate needed to get 3.8kW power at a delta t of 6:

flow rate = kW x 3.6 / (delta t x specific heat) = 3.8 x 3.6 / (6 x 4.2) = 0.54m^3/h...).

The next question is how long does your heat pump take to heat the water from X to Y (assuming a 200L or thereabouts tank, it should take about 30-40 minutes to raise the temp by around 15 degrees, today, mine did 34 degrees to 50 degrees in 30 mins at a flow rate of around 1.48m^3/h at an average delta t of 5 and with some glycol in the system). Very roughly pro rata, at a third of the flow rate yours should take three times as long.

What I am getting at here is the credibility of the data.


Midea 14kW (for now...) ASHP heating both building and DHW


   
👍
1
ReplyQuote
Burtis
(@burtis)
Reputable Member Member
Joined: 12 months ago
Posts: 109
Topic starter  

@cathoderay 

Will try and grab these next time or I may force it to go to 50⁰ just to check. I keep it at 45⁰ and just let it top up we have a 150L tank.

Yeah it doesn't take long to heat up 

Cheers for you insight buddy


This post was modified 9 months ago by Burtis

   
ReplyQuote
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2130
 

Posted by: @burtis

Will try and grab these next time

If you know when it will go into DHW heating mode (because it is on a timer?) then it won't take much to get useful readings, say flow rate, LWT/RWT (so you can calculate delta t) and DHW tank temp every 5 minutes will be enough to show the outline of how you tank heats up. Or if it is 'always on', you can force a reheat by running a tap (which incidentally is what the Freedom annual service requires, to confirm the system is working correctly).

DHW heating is when the heat pump normally works hardest, and is therefore a good time to see what it is actually putting out, and the fact that there is a directly measurable outcome makes things easier. 

I have become increasing suspicious of Midea flow rates and their control. For a start, they are not directly measured, they are instead inferred from the pump's 'running parameters' (electrical?) and is known to be somewhat inaccurate (though tolerable): "The flow rates parameters are calculated according to the pump running parameters,the deviation is different at different flow rates,the maximum of deviation is 15%" (source: Midea M-thermal Mono Installation and Owners Manual Apr 2020 p64). The same manual on page 5 gives the range of flow rates for each model: 

image

  

Assuming you model is one of the 12/14/16kW models, then you flow rates are below their expected range. In my case, they are in range, but fixed (~1.45m^3/h) and this appears to cause my 14kW model to be only a 6-8kW model. In both our cases something is not right.

It would be very helpful if other Midea (or Midea clone) heat pump owners could report their heat pump running data (especially flow rates). 

All this said, I happen to have an analogue flow meter installed in my primary circuit which is totally independent of the Midea monitoring, and it shows that in general terms the Midea reported flow rate on my system is broadly in line with the analogue readings. 


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote



Burtis
(@burtis)
Reputable Member Member
Joined: 12 months ago
Posts: 109
Topic starter  

@cathoderay 

Interesting 🤔 

Mines being the 6KW looking at that data you provided there it's running right on the bottom end for flow.As long as It doesn't drop below 0.4 it should be fine. 

MideaUK said it could be a poorly wired up secondary circulation pump that stays running after the heat pump is done it job causing a flow issue or E0 fault code would be down to the installer to check this is suppose. 

Ideally i guess if the buffer was re piped as a volumiser on the return and that circulation pump removed it would be more efficient and less pump noise issues and less energy used to run the pump. 

Another point to note I was chatting to the phone bloke from MideaUK he mentioned that they don't like using glycol and to use anti freeze valves instead for efficiency sake.

We shall see it's all a waiting game now anyway to see what MCS and the installer say



   
ReplyQuote
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2130
 

@burtis - what seems to be happening in both our heat pumps is the flow rate is somehow capped at the lower end of their respective ranges, with the result that in more demanding conditions they can't cope.

I'm not sure who MideaUK are - last time I looked it was some sort of shell office, the real 'MideaUK' was Freedom, but maybe Midea now have their own presence here. Be that as it may, there advice ("most likely a plumbing problem" and "could be a poorly wired up secondary circulation pump") is of the "there seems to be a lot of it about" variety, insofar as it doesn't add much. Nor am I sure why they think the secondary (emitter circuit pump) could be causing primary circuit flow rate problems.

From the research @jamespa and I have done, it seems the primary circulating pump is supposed to be PWM (pulse width modulation) controlled, and that is supposed to be how it achieves its full range. On inspection, my heat pump does at least appear to have the relevant cable to do this in place, but for what ever reason it isn't doing anything. 

You have a buffer, as you know these are contentious. At times Freedom have insisted on them (or a plate heat exchanger, which is what I have), otherwise you can kiss your warranty goodbye, at other times they have not insisted on them. Others have got freedom to agree to their removal. I have decided to live with my plate heat exchanger, and accept it compromises my heating a bit, because on the other hand I do like the idea of hydraulic separation (I won't for example get radiator crud, not that I have any, blocking the primary circuit filter, as you have had). If I had a buffer I am pretty sure I would remove it, or as you suggest turn it into a volumiser.

The use of either glycol or antifreeze is a trade off. I prefer glycol on the grounds that it manages a potential freeze up better, as in it just does its thing. If you have antifreeze valves, then you have to manually refill the system to get it going again after a freeze up. That said, another school of thought says the real risk of a heat pump freeze up is extremely small - you need prolonged cold weather plus a power cut or heat pump malfunction to get to the risk - and so why bother. I think the answer to that question may be to ask it again after an owner has had their heat pump freeze up. 

Yes, you need to wait to hear what MCS and your installer have to say, but in the meantime do try to get that DHW reheat data. I'm hoping it will reveal what your system is actually doing.     


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2468
 

Posted by: @cathoderay

From the research @jamespa and I have done, it seems the primary circulating pump is supposed to be PWM (pulse width modulation) controlled,

I wonder if the Installers have appreciated the difference between a pump which has PWM inbuilt within the pump itself, and one where the Heat-Pump controls the speed by sending PWM signals down a wire?

Them simply stating that a pump is 'PWM controlled' isn't sufficient.

 

 


Save energy... recycle electrons!


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2468
 

Posted by: @burtis

It's all a bit over my head all this maybe one day I will dig into it deeper but really I shouldn't have to.

Ofgem and DESNZ are both aware that there is a dearth of knowledge holding up the implementation of future energy strategy.
There's no point having a Minister making a policy decision if those who are required to implement it don't adequately understand the issue.

Here's a snapshot from part of Ofgem's recent Consultation on Energy Innovation:

image

That Consultation closed last week. But I submitted responses, both to their fixed Question Set and also to other comments in the accompanying Guidance Notes.

What gets discussed in forum topics like this one are providing me with evidence to inform my responses.

Instead of merely answering questions in Government Consultations, I tend to present one or two examples which support my observations.
Those in turn, contain links back to forum discussions.

 

Here's another snapshot from a different part of the same Ofgem Consultation:

image

Ofgem is the Energy Industry Regulator.

They create and monitor the regulations which are implemented by the likes of MCS and NAPIT.

Although that section is specifically about enabling Innovation, it does seem to suggest that they want to hear from the ordinary members of the public, rather than just those working in the Energy Sector. Is this perhaps an opportunity for @editor to write something based on what @burtis is reporting here?

 


This post was modified 9 months ago 2 times by Transparent

Save energy... recycle electrons!


   
ReplyQuote
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2130
 

@transparent - I summarised the results here. What we actually found were wiring diagrams showing the PWM control cable (in addition to the power cable) and on my actual heat pump you can see two cables (multicore) physically attached to and presumably (?) connected to the circulating pump. I'm pretty sure we also found something on how the external PWM controls the pump, including no signal = max RPM, but I can't seem to track that down. I don't think my installer touched any of this, the heat pump came out of its box and went into place, with minimal work done on it bar making the actual piping mains supply and wired controller connections. Neither is there anything in the Freedom installation manual (which my installer used) that says anything about doing anything to the circulating pump.

 

Edit: changed 'two wires physically' to 'two cables (multicore) physically'


This post was modified 9 months ago by cathodeRay

Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2468
 

Posted by: @cathoderay

on my actual heat pump you can see two cables (multicore) physically attached to and presumably (?) connected to the circulating pump

Good. Two cables.
So that suggests a power-supply cable, and a separate control cable.

What does @burtis have?


Save energy... recycle electrons!


   
ReplyQuote



cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2130
 

@transparent - here's the page with more details and images on what my heat pump has.


Midea 14kW (for now...) ASHP heating both building and DHW


   
👍
1
ReplyQuote
Burtis
(@burtis)
Reputable Member Member
Joined: 12 months ago
Posts: 109
Topic starter  

@cathoderay

20241202 101517
20241202 101523
20241202 102009
20241202 102003
20241202 102515
20241202 102520
20241202 103007
20241202 103507
20241202 103012
20241202 104024
20241202 104029
20241202 104512
20241202 104518
20241202 103513


   
ReplyQuote
Burtis
(@burtis)
Reputable Member Member
Joined: 12 months ago
Posts: 109
Topic starter  

@cathoderay

20241202 104959
20241202 105006
20241202 105101
20241202 105105
20241202 105109
20241202 105113
20241202 105120
20241202 105124


   
ReplyQuote
Page 12 / 19



Share:

Join Us!

Latest Posts

Members Online

Click to access the login or register cheese
x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
ShieldPRO