[Solved] Sudden drop in COP
I've had a sudden drop in COP, from around 3.8-4.4 a few weeks ago, to 2.4-3.0 recently. Any thoughts as to why?
I have a Samsung 8kw ASHP that for the last month or two I've only been using for DHW. I don't have any advanced monitoring, just the energy use and generation output by the unit itself. Over the last week the COP has been way down and I'm not sure why.
I heat up the DHW once a day between 2pm and 3:30pm, 200L water tank with 3m square heating coil. The unit switches into quiet mode when DWH is active. It's not a heavy use set up, one shower a day and maybe some washing up.
I don't have the heating on this time of year and don't want to turn it on to see what that is running at.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
My guess would be that the unit is measuring combined COP for heating and hot water. Therefore because now you are only heating water at a lower COP than heating your average drops.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I don't have any advanced monitoring, just the energy use and generation output by the unit itself.
How do the energy use and generation output differ between the good COP and bad COP weeks? Is it that the energy used has increased or the energy generated has decreased to give you the lower COP?
My Samsung Gen6 8kw had a bit of brain fade earlier in the year when the recorded energy generation figures became ridiculously high - 1,398kWh for one week in February. The energy consumption was recorded as a (more believable) 90kWh, so a fantastic COP of over 15 🤗 . I knew something was really wrong when I saw that the recorded weekly operation time for that week was 524 hours - around 75hrs a day. Samsung Technical Support talked me through a reset of the Wired Remote Controller and that appeared to sort the issue.
@bontwoody The thing is I have been using it for only DHW for a month or two, i was getting higher cop just on the hot water, so it can’t be that I’ve turned off the heating.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@sjn Okay so it was a software issue. It appears my energy use is going up, but my energy generation is staying about the same according to the numbers.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker Yes, it must have been a software bug disrupting my historic energy numbers. I haven't looked at them recently so I should check to see if they are still ok.
Your generation staying about the same makes sense for a consistent use of DHW so it is the increased usage that is unexpected.
One thing I have noticed is that there is some rounding going on with the displayed energy numbers - the sum of the energy figures for each day does not add up to the displayed total for the week. I wonder if with DHW only the usage and generation will be quite low so the rounding errors may have a bigger significance to your COP calculations, possibly amplifying any week to week changes due to different outside air temperature 🤔 .
@sjn I've seen this on other brands as well. Rounding for small consumption (for instance only hot water) really messes up the accuracy.
Another thing we've seen is that some manufacturers just add on a flat energy use per hour (during periods when the heat pump is not running). Maybe Samsung did a software update recently and started doing this as well?
CEO and co-founder at HavenWise
@hcas Thing is I've not updated the software, that's actually quite hard to do with Samsung as its not directly connected to the internet.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
SOLVED
So it turns out the problem is, I am a massive Idiot.
A few weeks ago, I had used most of my hot water, and needed a quick shower as I was in a rush and had to go out. So I put on forced mode for DWH and turned on the immersion heater, which I normally have turned off, to turn on after 15 mins. When I had enough hot water I turned off forced mode but forget to turn off the immersion in the field settings.
So my sudden drop in COP has been down to my immersion firing up and helping heat my hot water for the last few weeks 😭
Turned it off and I got 4.1 cop for DHW today
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker May I ask a question of you please. I too have a recent install of a gen 6, one of the 16kw units. As it’s warm, only been running DHW cycles and trying to get my head round how it can be tweaked to run optimally.
With my legionella cycle off, and a hot water set point of 45C I’m getting a COP around 3.6. But it’s not behaving as I’d expect, mine seems to ramp up the circulation pump inverter to 100% and ramps up the heat pump power input to about 6kW and then ramp it down again, it finishes the cycle in less than 20mins (a 250L tanks) and uses approx 1.5 kWh. I was expecting it to behave less bruitishly, tickling up the flow temp slowly to get better efficiency.
Does yours go flat out too please?
thanks
-
Samsung problems
1 week ago
-
Nibe F2040 periodic warm water increase fails
4 months ago
-
Samsung E911 intermittent issue
8 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
10 months ago
-
Heat Pump, DHW, UFH and Radiator Install
10 months ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 44 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
You are too young, 50s-60s expression (or earlier?) whi...
By JamesPa , 34 minutes ago
-
RE: Heat Pump Damage on install - useable or dealbreaker?
Definitely that one, more important than the fins proba...
By JamesPa , 39 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson - looks like good work, and thanks for posting ...
By cathodeRay , 59 minutes ago
-
RE: Electricity price predictions
@diverted-energy sounds like good tariff for you. Octop...
By JulianC , 12 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 14 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 15 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 15 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 17 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 18 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 19 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 20 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago