Should I make my radiators smaller?
A deliberately provocative title, forgive me.
The question is really about how important it is to have equally sized radiators in each room, in relation to specific room heat loss.
I had a heat loss calculation done, and with my current radiatiors at a design temperature of 50C flow and -3 OT, some are clearly undersized, the worst being -47%. Okay that needs upgrading, no brainer.
But how much to upgrade it, just to 100% the heat loss of that room, or to match the most oversized radiator in any other room?
What if thats not possible, and room A is sized with 100% of power output to heat loss, and room B is sized to 158% of power output to heat loss; I assume room B is going to get much too hot?
The modern advice is not to have TRVs and to go as "open circuit" as possible, so how do we mitigate the oversized radiator in room B? Should we make it smaller? What % of size deviation can be handled without adding flow restrictions and controls?
Everyone seems to say bigger radiators are better, but should that advice come with the caveat that sizing needs to be equal throught the heating zone?
TIA
Bonus question; if you open up all the radiators in a reasonably balanced system, and let the heating come to equielibreum with OT, and measure the temperature within each room; is that a better way to calculate heat loss? Is there a method for that?
Posted by: @scalextrixWhat if thats not possible, and room A is sized with 100% of power output to heat loss, and room B is sized to 158% of power output to heat loss; I assume room B is going to get much too hot?
The modern advice is not to have TRVs and to go as "open circuit" as possible, so how do we mitigate the oversized radiator in room B? Should we make it smaller? What % of size deviation can be handled without adding flow restrictions and controls?
The deviations can be handled by
a) the lockshield valve. this restricts the flow rate through the rad in question which increases the deltaT for that rad which reduces the average temperature and hence the output.
b) the fact that rooms tend to share heat anyway because the thermal separation is poor.
I had mismatches of 150% plus, no problem
Posted by: @scalextrixBonus question; if you open up all the radiators in a reasonably balanced system, and let the heating come to equielibreum with OT, and measure the temperature within each room; is that a better way to calculate heat loss?
No, you wont leave it like that for long enough to overcome all the other variations that mother nature throws at us.
Posted by: @scalextrixIs there a method for that?
yes, (a) measure it over several weeks monitoring individual radiators and the heat pump, Adia Thermal make the kit to do this or (b) plot your gas/oil usage vs average OAT for several months or preferably a whole season, estimate the efficiency of your boiler, and work from there (gives you whole house only).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the reply, so really in this case we have to reduce the flow to the radiator to achieve it.
In my specific case the oversize radiators are upstairs which isn't really the best from a heat sharing perspective, but I get your point.
Posted by: @scalextrix@jamespa thanks for the reply, so really in this case we have to reduce the flow to the radiator to achieve it.
In my specific case the oversize radiators are upstairs which isn't really the best from a heat sharing perspective, but I get your point.
Mine are also upstairs because I upgraded them before I realised how much the heat pump industry overestimates house losses. Still not a problem although the lack of 'valve authority' with the very old LSVs on a couple of the rads in question makes for a slightly tricky, but not impossible, adjustment . Of course that is my house, yours may be different. The 'excess' upstairs capacity helped my installer to be happy to leave the bathroom well under-provided for, thus I could retain my exiting towel rail rather than replace it.
That said if you can make the downstairs ones bigger go for it. Lower flow temperature = lower cost and greater comfort, as you clearly know!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,113 Topics
- 46.4 K Posts
- 79 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 hours ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 6 hours ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 18 hours ago
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 2 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 3 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 3 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 3 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 5 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 5 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 6 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 6 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 6 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 6 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 6 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 1 week ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago