I am most grateful to both Derek M and JamesPa for their advice, and I would just like to confirm how the tank is used as a volumiser, only in the return line.
I should confirm that at present, the pipe from ASHP to the buffer tank is connected to the top left tank connection via the 3 way valve which alternatively feeds the DHW tank.
Is the following correct?
The ASHP pipe after the 3 way valve, (which is currently connected to the tank), should be replaced by one that connects the 3 way valve to the CH pipework at the point where secondary pump discharge is now connected.
The top left tank connection (currently ASHP flow) and the top right (currently radiator flow) to be plugged, whilst the bottom left (ASHP return) and bottom right (Radiator return) are to remain as installed.
The secondary pump appears to be connected to the mains feed (running whenever the heat pump power is on), but will any electrical changes be required in the Ecodan?
You would be most welcome and 3 bedrooms available. I would consider it good value!
Posted by: @davidalgarveThe ASHP pipe after the 3 way valve, (which is currently connected to the tank), should be replaced by one that connects the 3 way valve to the CH pipework at the point where secondary pump discharge is now connected.
Correct
Posted by: @davidalgarveThe top left tank connection (currently ASHP flow) and the top right (currently radiator flow) to be plugged, whilst the bottom left (ASHP return) and bottom right (Radiator return) are to remain as installed.
It would be better to connect the radiator return to top right, leave the ASHP return bottom left, then plug the remaining two ports. This ensures that the volume in the tank is engaged by forcing water to flow top to bottom through the tank.
With 15 radiators its quite probable that you don't actually need the volumizer, but since you have it...
Posted by: @davidalgarveThe secondary pump appears to be connected to the mains feed (running whenever the heat pump power is on), but will any electrical changes be required in the Ecodan?
If its currently running constantly (indicating that the Ecodan doesn't control it in any way) then probably not, but without going through all the system settings I couldn't be sure.
Posted by: @davidalgarveYou would be most welcome and 3 bedrooms available. I would consider it good value!
Thank you for the very kind offer, but it was my feeble attempt at a joke. If my wife and I were to visit Portugal in the not too distant future, which we are not planning to do, we could maybe get together for a meal, and bore the ladies with tales of heat pump disasters.
After discovering yesterday that all buffer tanks would appear to not be created equal, I would add to the excellent advice supplied by James, that you should check for arrows on the buffer tank indicating direction of flow. With reference to the photo bellow, the return pipe from the radiators would need to be moved from the bottom left connection and connected at the top right connection. The present bottom right connection remains the same, and the two now open connections would need to be plugged.
With regard to the electrics for the secondary water pump, the manual shows that the power for the water pumps is switched on and off via relay contacts within the control unit. It should therefore only be necessary to disconnect at the local power supply feeding to pump.
Thanks Derek M for the further update. I have approached the contractor that installed the DHW system (including the 3 way valve) and he will make the changes as confirmed by JamesPa and I believe that this complies with your description above regarding the radiator return.
One last point: The towns water supply is connected to the buffer tank via a pressure regulator and is always on (currently set to about 1.9 Bar). Is the connection at that point acceptable or must I move it?
I am attaching a photo and the connection referred to is middle front.
Posted by: @derek-mPosted by: @davidalgarveThanks Derek M for the further update. I have approached the contractor that installed the DHW system (including the 3 way valve) and he will make the changes as confirmed by JamesPa and I believe that this complies with your description above regarding the radiator return.
One last point: The towns water supply is connected to the buffer tank via a pressure regulator and is always on (currently set to about 1.9 Bar). Is the connection at that point acceptable or must I move it?
I am attaching a photo and the connection referred to is middle front.
-- Attachment is not available --
I can't think of any reason why the mains water connection would need to be moved.
Agree, although in the UK, at least according to my understanding, this would have to be demountable via double check valves etc (assuming its effectively the 'filling loop'
Thanks JamesPa - have only just picked this up.
I have the contractor visiting who is primarily a solar installer but he added the DHW system and I have a lot of respect for him, although he has some fixed ideas.
I have started to explain the perceived benefits of taking the buffer tank out of circulation, but it occurred to me that I am uncertain how I will decide on the speed of the built in Ecodan pump.
What method will I use to evaluate the performance at the available speeds?
By "taking the buffer tank out of circulation" I mean removing the secondary pump and using the buffer tank just as a volumiser
@davidalgarve If the heat pump is capable of modulating the pump speed (via a pwm cable) I would let it do so.
Otherwise you will have to look in the installation manual unless someone here is familiar with the specifics of ecodan. Or just set it at the middle speed, and see if you get a DT flow-return of roughly 5C at the design OAT (or in proportion to Room temp - outside temp at higher OAts unless the heat pump modulates the water pump speed), with all emitter valves open. Its not particularly critical ASFAIK so long as its sufficient.
Posted by: @davidalgarveThanks JamesPa - have only just picked this up.
I have the contractor visiting who is primarily a solar installer but he added the DHW system and I have a lot of respect for him, although he has some fixed ideas.
I have started to explain the perceived benefits of taking the buffer tank out of circulation, but it occurred to me that I am uncertain how I will decide on the speed of the built in Ecodan pump.
What method will I use to evaluate the performance at the available speeds?
I agree with James. I think that I am correct in saying that the water pump speed on the Ecodan can be varied from 1 to 5, so probably start with the pump set at 3 and see what DT you get. You may find that you need the pump speed lower in Summer and higher in Winter.
- 25 Forums
- 1,442 Topics
- 30.2 K Posts
- 21 Online
- 1,225 Members
Join Us!
Latest Posts
-
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Yes, it is one of those two who first alerted me to the...
By IvanOpinion , 11 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
The fact that the MCB is rated 16A tells us what we nee...
By Transparent , 12 hours ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
Thanks, @editor. Ideally it’d be someone who would li...
By Majordennisbloodnok , 14 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Unless adequately controlled it could devour your bank ...
By Derek M , 14 hours ago
-
RE: Effect of buffer tank or volumiser on heat pump system
I think that you will find that the best location for a...
By Derek M , 14 hours ago
-
RE: ASHP Commissioning: What Questions Should I Ask the Installer?
@derek-m thanks - will look out for the point regarding...
By Declan90 , 1 day ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor @kenbone Thanks, I would be very interested ...
By Elton , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
This is all a bit too frequentist for my liking. The pr...
By scrchngwsl , 1 day ago
-
Relax with 4K drone footage of lawn mowing to a smooth Motown tune
Sending out some chilled weekend vibes to everyone. Lis...
By Mars , 2 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
The starting point of that discussion on Camelot-Forum ...
By Transparent , 2 days ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 2 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 3 days ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 3 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 3 days ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 3 days ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 4 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 4 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 4 days ago
Heat Pump Humour
Latest Topics
-
By David999 10 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 6 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 7 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago