my understanding from reading the manuals is that when water law is active - you cannot select "indoor" mode on that screen.
if indoor is active you are telling the heat pump to adjust it's temperature based on the indoor thermostat rather than the outdoor weather
*as far as i understand it!*
@simonh I think I know what’s happening. I have water law enabled but the room temperature is controlled via the Samsung controller which is acting as a limiter at 22C. When it was mild it was turning off the HP before it started cycling now it rarely turns off the heat pump at all as the WC is limiting the room temperature.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@simonh I stumbled across this which relevant
https://community.openenergymonitor.org/t/i-want-to-punch-my-samsung-controller-fsv-2091/27143
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @simonhmy understanding from reading the manuals is that when water law is active - you cannot select "indoor" mode on that screen.
if indoor is active you are telling the heat pump to adjust it's temperature based on the indoor thermostat rather than the outdoor weather
*as far as i understand it!*
There are 2 main display options on your wired remote controller. In both displays the current flow temperature and room temperature are shown on the right hand side. On the left hand side of the display is a setting that you can adjust with the up and down arrow.
- If you are using an external thermostat (FSV 2091/2092 = 1-4), then the adjustable setting is the Offset that you can apply to your water law settings (+/- 5C)
- If you are using the internal Samsung thermostat in the wired remote controller (FSV 2091/2092 = 0 (Not use)), then the adjustable setting is the desired room temperature.
In both cases, the flow temperature is controlled by your water law settings ie weather compensation is in operation. You could argue that using an external thermostat is more versatile as not only can you set the desired room temperature limit, but you can also change the target flow temperature without going into service mode by simply changing the offset value. Whatever you choose, weather compensation will be operating.
There is another option - in service mode --> Indoor Zone Option --> Standard Temperature --> Water Outlet. This allows you to set the desired flow temperature directly and in this case there is no weather compensation. This isn't used much.
@mike-h Thanks for that clear explanation Mike. Very useful.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@mike-h what I don't understand about this setback control is... How do I tell it when to operate the setback?
Or is Samsung basically saying that it's a manual thing for whenever you change it and then change it back?
But that would be ridiculous to do every night!
I have water law set up (auto), but when I try to schedule, the only options I have are dhw and holiday. Daily and weekly options aren't available...
Richdorm
@richdorm do you have an external thermostat, or not? In other words, which of the two modes @mike-h highlighted above are you running in?
We use a programmable room thermostat (first example in @mike-h post above), and simply knock back the desired room temp to 18C overnight, or we can programme it between set hours.
If you don't have an external thermostat, then I think you need to set a 'Weekly' schedule. Are you able to do this, or is 'Weekly' greyed out?
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @richdormOr is Samsung basically saying that it's a manual thing for whenever you change it and then change it back?
But that would be ridiculous to do every night!
Exactly that so far as I can tell from the manual and discussions with the Samsung rep at the installer show 2025 (I don't have a Samsung).
Samsung doesn't give an option to have a flow temperature setback or set forward unless you use an external controller. The only way to achieve setback or set forward using the Samsung controller is to operate it in temperature sensor control mode, which you can do as an overlay to WC. There is no way to do it if you want to do it on pure WC.
I challenged the rep at the last installer show about this, he was keen to show me the new flashy full colour UI, which still doesn't do this. His colleague then admitted that the flashy UI uses the same underlying logic and so hasn't expanded the capabilities to do this very useful thing. I confess that I told them at this point that their controller was one of the worst on the market of the major manufacturers, which they didn't entirely warm to (but didn't actually attempt to deny).
IMHO this limitation is rubbish. It's not unique to Samsung though. If you want to do this sort of thing with Samsung or other heat pumps that have this limitation, you need homely or to write your own script in HA or similar.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @richdorm@jamespa or havenwise perhaps?
Yes, and probably also Adia although the latter has a much greater scope
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@old_scientist so - I have a Hive thermostat, which I've currently got set to 25 (!) so that I could set up the water law without it interfering.
I guess having the hive means I've got an "external thermostat" then?
So once I've set up my water law (which I've more or less done) then I could schedule the hive to be (say) 2C cooler at night than the desired 19C - which would have the effect of limiting the pump. Is this correct? Most people say "don't use a hive!"
Posted by: @richdormSo once I've set up my water law (which I've more or less done) then I could schedule the hive to be (say) 2C cooler at night than the desired 19C - which would have the effect of limiting the pump. Is this correct? Most people say "don't use a hive!"
Not really in the way you describe
The effect at best would be to switch it off altogether until the house cools. It wont limit it by reducing FT, which is what you really want to do. However I think Hive may do 'pulse width modulation' on its output, a crude way to control on on/off boilers 'proportionately'. If it does this (several smart thermostats do) then its a real no-no for heat pumps. You would need to check this before even considering using Hive this way. Its possible that this function can be disabled but you would need to check with Hive or someone who is an expert in Hive.
The Hive guy at InstallerShow definitely told me that they had looked at making Hive properly suitable for heat pumps but had not pursued it because there was no standard interface. I take that as an admission that currently it isn't!
Samsung has an on/off schedule function inbuilt I believe; use this if you want to switch the heat pump off for a period and leave the Hive doing nothing!
Unfortunately this is where the crudeness of Samsung's controls bites a bit. That said, although my Vaillant is cleverer in this respect, I still dont bother with a nightime setback, I just have the bedrooms at a slightly lower temp permanently.
PS There is something here about what Hive does. The 'time proportional' element is the one which may be problematic, depending on how its actually implemented, which I doubt is publicly documented.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Rodents! A word of warning for heat pump owners
1 week ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
3 weeks ago
-
Running my new Nibe ASHP efficiently
4 weeks ago
-
Weather compensation- why you should use it
1 month ago
-
Where has Watson gone?
1 month ago
- 27 Forums
- 2,475 Topics
- 56.9 K Posts
- 240 Online
- 6,165 Members
Join Us!
Worth Watching
Latest Posts
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Hi, Nothing yet. I've asked customer to measure flow...
By errmm , 5 hours ago
-
RE: High Temp Heat Pumps for fast warm-up of house
I don't know exactly how long it takes to heat up (and ...
By JamesPa , 6 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
OK. What Im seeing looks fairly normal TBH: 1 start ...
By JamesPa , 7 hours ago
-
RE: Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@editor thanks for the tips which I will try before cal...
By DavidB , 8 hours ago
-
RE: Daikin 6kw setup with Dixell controller
@jamespa Many thanks for your reply, a very detailed an...
By CraigH , 8 hours ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Despite reservations, I found some time to respond to t...
By Rusty , 8 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@crankplus, nope, still not, and I've followed up with ...
By Mars , 8 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge Probably, but temperature change at -10 ha...
By AndrewJ , 9 hours ago
-
RE: External wall insulation - your experience
To be clear, my experience was very positive. The journ...
By Batpred , 11 hours ago
-
@foxesfan Re: ‘Servicing’ as @editor has covered in his...
By Toodles , 11 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson No idea why mine doesn’t work, all I see on ...
By Papahuhu , 12 hours ago
-
RE: Battery sizing - How low can you go!
It seems I am seeing something similar to what you do, ...
By Batpred , 13 hours ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
Don’t know if this is relevant to this thread, but my A...
By Gruff2001 , 14 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
@majordennisbloodnok While getting Home Assistant runni...
By Steelbadger , 1 day ago
-
RE: MCS - BS EN 12831-1:2017 – Heat Loss Survey
Since May 2025 it no longer a requirement in England to...
By JamesPa , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handel @jancold Manufacturer: Daikin Model: E...
By Jancold , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@harriworld it was roughly 3am for an hour as that’s ...
By L2jad , 1 day ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
I have been wondering that myself. The fact is that, ...
By JamesPa , 1 day ago
-
RE: Filtering Tap Water – Share Your Setup for Cleaner, Better-Tasting Water
I remember when I was in my early 20s I was introduced ...
By Majordennisbloodnok , 1 day ago
-
RE: Setback savings - fact or fiction?
But if it is recorded an an integer, which it seems it ...
By cathodeRay , 2 days ago