[Solved] Samsung Gen 6 ASHP Outdoor Unit Supplied With Wiring Issue!!
Hi, Ive just installed my new ASHP but on start up kept getting E458 errors which is a fan malfunction. I took the top off the outdoor unit and the issue was pretty obvious
Does anyone know or can look if the fan plug should fit in here (6 pin socket on the left), its fits nicely.
If anyone is interested the unit came from The Heat Pump Warehouse but has a Joule sticker on it.
Thanks Mark
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Problem now solved, for anyone with the same problem, I managed to take the plastic top off the circuit board and saw the lettering CNP 901 by the socket I thought was correct with the description BLDC-FAN. all working now. Crazy that they shipped it without connecting the fan. Ill let you know their response when I get it
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,289 Topics
- 51.4 K Posts
- 271 Online
- 5,949 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
Really good episode thanks for that. Uplifting as well...
By JamesPa , 57 seconds ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Very sound reasons imho. My current feel, albeit based...
By JamesPa , 1 hour ago
-
RE: Electricity price predictions
In general, in order for the market to work and drive p...
By Batpred , 2 hours ago
-
That's not always the case.Let's see what they say once...
By Transparent , 3 hours ago
-
-
RE: BUS grant voucher expires before install date
@bornagain That is what our installer is pr...
By Bash , 5 hours ago
-
@sheriff-fatman Interesting because I am considering so...
By DavidAlgarve , 6 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
I'm not so sure. New gas boiler £10...
By Bash , 7 hours ago
-
RE: DHW heat loss through pumps.
I have a recirculation pump that we had fitted when the...
By Marzipan71 , 7 hours ago
-
RE: Renewables & Heat Pumps in the News
I thought an aircon doubling as a heat pump could do ou...
By Batpred , 9 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Just wanted to share some info for anyone facing challe...
By Batpred , 10 hours ago
-
Daikin Altherma HT Temperature Sensor Question - Caution: Mentions AI...
Hi All - first post for a while, hope you are all well,...
By Marzipan71 , 11 hours ago
-
RE: Do Heat Pumps need to start up at Full Power?
@steelbadger We have an LLH with secondary pump; the se...
By Toodles , 14 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
And the saga continues… So today a Senior Grant Engin...
By Crimson , 1 day ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa Yes, the OAT sensor is situated on the back pa...
By Toodles , 1 day ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
Just to clarify, returning water from UFH is colder tha...
By lukewarmbath , 1 day ago
-
RE: 10kw heat pump run in 24*7 data?
A different heat pump (Midea 14kW) but a stark reminder...
By cathodeRay , 1 day ago
-
RE: Confusion over Octopus Tariffs
That's sounds great. I have no ASHP, but 15kwh storage....
By Batpred , 1 day ago