Samsung ASHP scheduling help
@broadsman the #2093 setting should be "Room Temp. only ON / OFF" for the Gen 6 controller.
Please make sure #2091 and #2092 are set to "not use" and any external third party thermostats are disconnected.
I did get an error myself but it looked like a flow interruption if I remember correctly. I think it is caused by the change in mode, I just pressed OK and it cleared then everything was running ok. The error for me was "Indoor (200000) / E121" for your info.
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
@mike-h I do have the 12Kw Samsung Gen 6 model.
Just to clarify, if you go to the Zone screen you should have the target room or water temp on the left and "Water Outlet" and "Indoor" temperatures on the right. These indicate the actual temperatures the system is seeing
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
@mike-h my pump does switch off when the room temp goes 0.5C above my target temp but this only happens with solar gain or my hand is near the controller too long. Most of the time it appears to keep the room at the target temp of 20.5C and the pump running continuously.
Here is my firmware version info
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
Posted by: @mike-hI wonder if your ability to keep room temperature at +/- 0.3C is because you have got your water law settings perfectly set rather than feedback from the controller.
I did a little experiment last night and changed my water law setting to a flat 37C (WL-1) to verify if the controller configured as the thermostat still used this water law or calculated its own water temperatures based on the outside temperatures. It appears that the controller still uses the water law set in WL-1 in my case. The pump continuously runs due to the On /Off only setting in #2093 but the water outlet temperature basically stabilised at 37C for an outside temperature of 6.5C (should be around 44Cish).
In my case @mike-h your assumption is correct and my water law is set about right and is still being used.
This is not the behaviour implied in the video I posted in an earlier posting which indicates the pump "looks at the outside temperature and decides the required temperature to set your radiators to to achieve the indoor temperature set point. When the temperature is reached the pump is reduced to maintain the internal temperature set point" (not verbatim). The radiator temperature seems to still be based on the water law settings for the Gen 6 not some implied clever internal feature.
Apologies for misleading anyone 🙂
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
- 26 Forums
- 2,122 Topics
- 46.6 K Posts
- 93 Online
- 4,529 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: 300 Liter Tank - Do I have to heat it all?
There’s no second hand market for DHW tanks (I was told...
By Judith , 2 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 10 hours ago
-
You may well be right, @jamespa.
By Majordennisbloodnok , 15 hours ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 16 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 18 hours ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 19 hours ago
-
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@davidalgarve It should just be recovered by both servi...
By dgclimatecontrol , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
Aggregators have been recognised for many years, and it...
By Transparent , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Great news I edited my previous post (probably af...
By JamesPa , 2 days ago
-
RE: Double or Triple Glazed Windows?
@toodles Glad to hear things are progressing well for y...
By TRBob , 2 days ago
-
How to waste energy (and time) playing with AI.
A friend of mine who subscribes to an AI service was ex...
By Toodles , 3 days ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@topher you’re more than welcome to, yes. I’ll send you...
By Mars , 3 days ago
-
RE: Fitting new shower valve ..........
I’ve never taken a chance when fiddling and changing ou...
By Mars , 3 days ago
-
You should contact the council and report the unsatisfa...
By JamesPa , 4 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
I would deffo install an additional slinky run, especia...
By Transparent , 4 days ago
-
RE: Say hello and introduce yourself
@editor fab - thanks Mars, and keep up the great work o...
By normpang , 4 days ago
-
RE: Compressor and Evaporator Stratification
@trebor12345 So I think the 1st zigzag section shows so...
By ASHP-BOBBA , 5 days ago