Hi there,

I have big difficulties in understanding the on/off behaviour of my new Samsung HT Quiet 12 kW Water Pump.
Some days ago I observed the behaviour for 1 hour and saw that the compressor is turned on for about 5 minutes, then it stopped heating, but the water pump continued for about 2 minutes before turned off for about 7 minutes. I guess that  was because item #2093 was set to the last option. All in all the pump made 4 on/off-cycles per hour. That felt quite much, therefore I called a technician to look for the settings.
But unfortunately now it is even worse. He made some changes (I don't know exactly what he changed - but #2093 is still at the last option!), and now after 5 minutes of the compressor turned on, the water pump continues for about 1,5 minutes and then turnes off for only 2 minutes. I don't understand, what that thing does ...
Unfortunatly I also don't understand most other posts hier, because there are so many abbreviations used ... (I'm not native english, and I'm very new in understanding, how such a system works - so I need somebody who is patient in explaining to me 😉 )
I think it would be better, if the compressor runs for longer intervals on low level and when it has to turn off, it should stay turned off for longer intervals. Maybe there is a possibility to reduce the maximum turn-on-numbers per hour? or allow, that the water temp falls for more degree under the set water temp before heating up again? What settings are possible to reduce the number of on/offs?

The only thing I changed since installation is the heating curve (the two items for the outdoor temperature and the corresponding items for the water temperature). I have control by indoor temperature activated with a limit to 22,5 C. When this room temperature is reached, the system stops further heating (that works fine!)

Thank you for your support!
Petra



   
Quote
(@guthrie)
Estimable Member Member
Joined: 2 years ago
Posts: 73
 

This sounds like what I noticed in our heat pump a few weeks ago.  The Honeywell room thermostat was set to have a 'cycle rate' of 5 times per hour.  I.e. if the temperature was too low it would come on, but only for 5 or 6 minutes, then off for the same, then on again until after much struggling the room temperature reached the desired one. 

So if you have the instructions for the room thermostat, what does it say about 'cycle rate' or similar?



   
ReplyQuote
(@iancalderbank)
Noble Member Contributor
Joined: 3 years ago
Posts: 643
 

its important to differentiate between, is it cycling because a thermostat has told it to turn off? Or is it cycling because the actual LWT is at or above the target LWT, and/or the RWT has got too high (so, delta T has got too low for the HP to be happy with it) and so the HP's internal control logic decides to "not add heat to the system" for a bit, to allow the circulating WT to drop? That second option is not the same as saying the house isn't calling for heat.

3rd party stats may cycle between on and off state too quickly for a HP. The samsung controller will not. @petra I deduce you are probably using the samsung controller?

2091 on the last option what I have always seen recommended (by people who genuinely do this for a living, I don't I'm an enthusiastic amateur) for a 3rd party stat install. 2093 is the exact equivalent if using the wired controller. That option allows the HP to do the back-off that I mentioned. the 3+7 min cycling is normal when the HP is backing off from adding heat.

However, what this can tell you about your system if its happening a lot / continuously, is that you may have an imbalance between emitter output and heat input, because the HP has to keep on stopping adding heat. If you have balance between input and output (which is what you are always aiming for), you will not see this backoff, or at least not see it much. In my system (full system performance link accessible in my sig) it can take an hour to stabilise (I am in my first winter so still tuning the WC numbers), here's this morning with some annotations:

image

so , if this is happening all the time may be worth working out what the heat output of your emitters is at the temperatures you are using, and does that match what the HP is putting in? Have the  emitters balanced (at the flow level, i.e. radiator lockshield valve adjustment), do they all get sufficient water flow so they all contribute? Do any get turned off by TRV's or similar, reducing available emitter output capacity ? also your system design can influence this: is it a single loop, or is there a buffer tank or low loss header splitting the system into primary and secondary? The latter two can make it harder to get the heat that the HP puts in to the buffer/LLH, back out again to the emitters : there has to be a flow-rate balance between the two sides of the system.

@petra how are you monitoring your system, you must have something that is telling you compressor is on or not? Do you have a way of collecting heat throughput data, a heat meter or similar?


My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
👍
3
ReplyQuote
(@petra)
Active Member Member
Joined: 2 years ago
Posts: 3
Topic starter  

@guthrie The room thermostat is integrated in Samsungs wired remote controller which is placed in my living room. There I cannot find any parameter which sounds like controlling the number of cycles per hour.



   
ReplyQuote
(@petra)
Active Member Member
Joined: 2 years ago
Posts: 3
Topic starter  

@iancalderbank Thank you for your answer. May I just ask at the beginning about the abbreviations you use? LWT and RWT?

Your first question: yes, I am using the Samsung wired remote for controlling the HP.
This 3+7 cycle that I also read of in the user guide isn't followed by the HP (although option 4 is selected in item 2093.

The delta T you mention, is it item 4052 (under "inverter pump")? And what exactly does it mean? And how does it influence the on/off-cylce?

What I observed until  now:  I've chosen the option of controlling temperature by the room thermostate. If the room temperature isn's reached, the HP turnes on. And it stays on until the water temp is reached according to the water-temp-law. So it doesn't turn off before water-law is reached, also if room temp is already reached. And on the other hand it turnes off with water-law also if room-temp is still to low.  Is it meant that way?

I turned on all radiators yesterday (also the one in the basement which is normally turned off), and it really got better after a while. I can show you my power usage curve (that's the only thing I can control over time ... my "normal" power need is about 300 W, so everything that is about 1000 W or higher is due to the HP turning ON. The peaks at about 8:30 AM and 15:30 PM is something else (washing machine), the peak at 11 AM is the hot water which I turn on every day at that time (hoping that my PV is working good at that time of day).

image

The plateau in the afternoon was very interesting to observe: the water temp increased VERY slowly, so the water-law temp was only reached after several hours. Normally it lasts only about 15-20 Minutes to rais the water temp from about 33 to 40 celsius. So I have no idea, what caused the WP to work that way but I was really happy about that 🙂
Unfortunatly after that, during the night, the "old" behaviour returned:

image

Is there a parameter in the Samsung controller that influences the number of cycles per hour? Or that influences the time, the water-law-temp is reached? I reduced the delta T parameter to 3 (from default 5) 2 days ago without really knowing, what it does and if it helps reducing cycles ...

Just do understand my initial problem: here's a graph a few days ago (HP was turned off during night at that time) ...

image

And regarding your further questions: no buffer tank, one single loop (I think), and "low loss header" I don't know what that means (and therefore don't know, if it was installed)
Monitoring the system I do via looking at my power usage via PV App - and by switching through status info screens in the Samsung wired remote. Unfortunatly I have no other monitoring tools available.



   
ReplyQuote
(@mike-h)
Reputable Member Member
Joined: 4 years ago
Posts: 197
 

@petra LWT is Leaving Water Temperature, that is the temperature of the water leaving the heat pump and going to the radiators. RWT is Returning Water Temperature, that is the temperature of the water returning from the radiators back to the heat pump. The difference between the two temperatures is called Delta T. This usually varies between 3 and 6. The amount of heat energy that the heat pump produces is proportional to the flow rate and Delta T. However, you cannot control Delta T on the Samsung. Changing Setting 4052 doesn’t do anything in my experience. 

The heat pump runs continuously until either the room temperature limit that you have set on the controller is reached or the LWT rises above what the Water Law says it should be. For example if the Water Law setting suggests that the LWT should be 34, then the heat pump will try and maintain the LWT at 34. If it rises to say 36, then it switches off. The reason why the LWT exceeds the target of 34 is usually because the radiators are no longer getting rid of the heat energy produced by the heat pump. When there is an imbalance like that the RWT rises first. This means Delta T and the heat energy being produced fall, but LWT initially stays the same. There is a limit to how low the heat pump’s heat energy can go. When that point is reached the LWT ends up rising above its target temperature and the compressor stops. With some makes, it stays off for 20 minutes, but the Samsung seems to restart after 4-5 minutes. The 2093 setting suggests that after the compressor stops because of the high LWT , the pump will run for 3 minutes and then be off for 7 minutes. In practice, the pump runs for 3 minutes and switches off, but restarts 2-4 minutes later as the LWT has now fallen below the target of 34 and the compressor wants to start again. 

The best way to stop this behaviour is to make sure that all your radiators are open, particularly when the outside air temperature is higher and the heat requirement of the house is lower. When it gets really cold outside, you should find that the heat loss from your home is more than the minimum output from the heat pump. Therefore the target LWT is maintained and doesn’t rise and therefore doesn’t switch the heat pump off. The only thing that then switches it off is if the room temperature target is reached.

The other solution to prevent cycling when the outside temperature is higher, is to make the target LWT quite a bit higher than really necessary, so that your home heats up quite quickly and switches the heat pump off when the target room temperature is reached. Then the heat pump will remain off until the house slowly cools down below the target temperature. This means that the heat pump is still cycling on and off, but much less frequently. Doing it in this way may not be the most efficient or economic way of doing it but maybe worth trying.

 

 



   
👍
1
ReplyQuote



(@iancalderbank)
Noble Member Contributor
Joined: 3 years ago
Posts: 643
 

Posted by: @petra

The plateau in the afternoon was very interesting to observe: the water temp increased VERY slowly, so the water-law temp was only reached after several hours. Normally it lasts only about 15-20 Minutes to rais the water temp from about 33 to 40 celsius. So I have no idea, what caused the WP to work that way but I was really happy about that 🙂

Unfortunately after that, during the night, the "old" behaviour returned:

Is there a parameter in the Samsung controller that influences the number of cycles per hour? Or that influences the time, the water-law-temp is reached? I reduced the delta T parameter to 3 (from default 5) 2 days ago without really knowing, what it does and if it helps reducing cycles ...

Just do understand my initial problem: here's a graph a few days ago (HP was turned off during night at that time) ...

And regarding your further questions: no buffer tank, one single loop (I think), and "low loss header" I don't know what that means (and therefore don't know, if it was installed)
Monitoring the system I do via looking at my power usage via PV App - and by switching through status info screens in the Samsung wired remote. Unfortunatly I have no other monitoring tools available.

very likely what made it better was that you turned on that extra radiator. it is amazing to see the improvement in stability that comes from adding extra emitters / getting the emitters properly balanced so they all carry a fair share of the load. I am still working on this weekly in my own system. There's no parameter for cycles/hour. I suggest you don't focus on solving that directly  - focus on getting your system setup so that its stable, then the cycling will just sort itself out.

if you don't know if you have an LLH...  Whether you have one or not will actually make a really big difference to how your system is operating. I would suggest at this point you draw a logical diagram of your system. Lines for pipes, boxes for components (valves, pumps etc). There are some good examples on this forum from other members. then post it.

depending on how keen your are , and how much of a DIY'er / technical person you are (or not), there are various ways to setup more detailed monitoring, so that you know exactly what your heat pump is doing.  where do you sit on that spectrum?

 


My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
ReplyQuote
(@guthrie)
Estimable Member Member
Joined: 2 years ago
Posts: 73
 

@petra Ah,that sounds like a more sensible way to set things up than my system.



   
ReplyQuote
(@misiak)
New Member Member
Joined: 2 years ago
Posts: 4
 

Hi @petra

Have you managed to resolve this issue at the end ? I have exactly the same problem with my 8KW HT Quiet pump. Basically it's the same pump only crimpled in the software. Issue is that it can't work lower than 1.0KW of power so minimal power output is around 4KW. I didn't know this before and I wouldn't never buy it probably. But what is worse is this CRAZY cycling behavior. It's hardly believe that someone can implement this logic. For me it works up to 2C where it can keep with my heat looses and desired indoor temperature. But once there is over 5C outside it start cycling like crazy. 7 minutes on / 3 minutes off. I would assume when stupid pump logic find out this is too short (my indoor temperature didn't fall down a bit!) then it should keep the pump off for longer time. Oh my... what is this. So I have a few questions for you.

1. Do you have PWM pump connected to the system?

2. Do you user "water law" or "inddoor" temperature regulation. I had water law so I switched to indoor but seem this is completely ignored. I set temp 23C. 23C is reached and it will shut off the mump. OK, but why for the sake of god it will start it after 4 minutes again while the indoor temp is still the same ????? This I can't understand. This must be some software error or what, I don't have and explanation for that. 

Really hope you were able to fix it so probably you can give me some hints ? Thanks!



   
ReplyQuote
(@misiak)
New Member Member
Joined: 2 years ago
Posts: 4
 

@mike-h Hi Mike, I have the same problem with this pump. The problem is that it can cover heat losses at 0C (4KW) but once there is +5C outside my heat losses are only around 3 so the cycling is inevitable. My only issue is that this cycle is very short 7/3 minutes. This is crazy. I still ask myself who programmed this ? 

I had regulation by water law but didn't understand how this works exactly since I did not have room temperature fully under control. It has cycled every few minutes at 5C so can imagine what it will do when there is +10 or +15 ?? Nevertheless, I've switched to indoor temperature regulation and hoped, it will solve the issue with short cycling and the heat pump will wait until the target room temp falls under certain level. But NO. It has reached the temp, shut down and guess what, it started again like stupid after 4 minutes despite the fact the indoor temperature didn't drop a bit! I would expect some hysteresis here.

Please help me to understand what I'm doing wrong here.

I was wondering to gave up completely at this "remote controller" and simply connect my own thermostat to the terminals which send the signal to heat when I want it and shut down that damn unit when I don't want to heat. I would set it up only if outdoor temp is above 5C. Bellow it would "follow" Samsung logic. Do you think this could work ? There is not way I can stand cycling every 5 minutes or so. This is insane.



   