Removing a Low Loss Header from Samsung Gen6 System

28 Posts
5 Users
0 Reactions
1,512 Views
(@ecobaker)
Estimable Member Member
358 kWhs
Joined: 7 months ago
Posts: 39
Topic starter  

My system has a low loss header, which for effiency I’d like to remove. Currenlty averaging a daily COP of 3.5 to 3.8, which is good but I’d like it to be better. I have a 8k Samsung gen6, however all the installation information from Samsung or Joule says to use a header or buffer. My system map is this, its fairly simple one zone in two bedroom mid terrace.

Screenshot 2024 03 27 at 20.26.11

Those of you with Samsung gen6 HP do you have a system without a header or buffer, my plan was to just remove it and connect up the flow and returns and see what happens. I just want to make sure I’m not doing something catastrophic before its done.

Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
Quote
Topic Tags
(@bontwoody)
Noble Member Contributor
3779 kWhs
Joined: 3 years ago
Posts: 546
 

Hi

I have a Samsung Gen6 (5kW) running without a LLH or buffer etc. I basically followed Glyn Hudson's tutorial on Youtube. It works fine for me. I guess you need to investigate why they decided to put one in in the first place.

Heatgeek states the reasons for doing it as "High flow rate requirement in the system, high resistance across the system/boiler pump is too small, or multiple heat sources for the property". the link is here https://www.heatgeek.com/low-loss-headers/.

I would imagine the middle one is most applicable to you, so you need to be looking at 28mm pipes to the heat pump itself and then look at the pipe configurations to the rads to make sure they they can carry the heat required at a reasonable flow.Here is a good explanation of that https://youtu.be/1FYv1RnVDrI.

Also check pump sizing. (BTW I dont think your pump supports PWM which is a shame as the heat pump can use it to adjust flow rate automatically, see here https://thegreeningofrosecottage.weebly.com/blog/alls-well-that-ends-well )

As long as your radiators are all open I cant imagine water volume would be an issue, but you could check just to be certain.

 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@heacol)
Noble Member Contributor
2128 kWhs
Expert
Joined: 3 years ago
Posts: 351
 

@ecobaker They work reasonably well on open zone, just make sure you always have the minimum flow rate.

Attached is a manual with the open zone programmer settings.

The Samsung DOES NOT support pulse width modulation pump control below 45 Deg Flow temperature, below 45 Deg C it maintains a fixed flow rate of 100%. Not great.

 

This post was modified 6 months ago by Brendon Uys

Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas


   
ReplyQuote
(@bontwoody)
Noble Member Contributor
3779 kWhs
Joined: 3 years ago
Posts: 546
 

@heacol @ecobaker

That isnt correct about the PWM Brendon. Here is my Samsung adjusting flow rate below 45C.

PWM

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@ecobaker)
Estimable Member Member
358 kWhs
Joined: 7 months ago
Posts: 39
Topic starter  

@bontwoody @heacol I'm not sure my system supports modulation either way. 

My pumps are UMP3 AUTO, with flow rate setting buttons on them, both currently set to max flow rate, so the heat pump cant modulate them. The secondary pump is permanently on and the primary pump switches on and off controlled by the heat pump. My flow rate round the system when heating is 26 lpm, appropriate for what Samsung recommends. I think my rate could be lower if I've done my maths right, around 16lpm. I could manually reduce the flow rates of the pumps and see what happens. I think my DeltaT is only about 2 degrees currently. Although I don't have very accurate monitoring. 

The volume of my system is over 48 litres just in the radiators, so I am well with in minimum requirments for the 8kw pump. 

Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
ReplyQuote
(@heacol)
Noble Member Contributor
2128 kWhs
Expert
Joined: 3 years ago
Posts: 351
 

@bontwoody That flow temperature is pretty close to 45 Deg C (43 deg C), it could be sensor drift that is causing the activation, it is clear that it is not activated at lower temperature. I have seen the official documentation, not publicly available. It is a great shame, as it has a detrimental effect on the performance of the refrigerant circuit. Possibly something to do with the finding that they become very unstable below 30 Deg C flow temperature.

I would be more concerned about the control strategy of the heating system, 45 Deg Flow temperature at 5+ ambient temperature? COP +- 3.5, pretty dismal. (unless you did this as a demonstration or hot water production)

This post was modified 6 months ago by Brendon Uys

Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas


   
ReplyQuote



(@bontwoody)
Noble Member Contributor
3779 kWhs
Joined: 3 years ago
Posts: 546
 

@heacol @ecobaker

PWM2

In the middle of renovating an old stone cottage and both my wife and I like it hot inside so higher than desirable flow temperature at the moment. Should improve next winter now I have finished insulating and radiator upgrades to the new living room. Still beating gas though.

@Iancalderbank pointed me to the PWM control possibility and I think he has an 8kW Samsung model. Here is the pump modulation again at a lower flow temperature of about 41C. Perhaps Ian can add to the data available.

 

 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@hughf)
Noble Member Member
2999 kWhs
Joined: 2 years ago
Posts: 489
 

Remove the llh and the secondary pump, wire the pwm line of the primary pump up to the Samsung controller…. That’s pretty much all there is to it.

 

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@ecobaker)
Estimable Member Member
358 kWhs
Joined: 7 months ago
Posts: 39
Topic starter  

@hughf The pump dosen't have a pwm line as its an Auto model

Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
ReplyQuote
(@heacol)
Noble Member Contributor
2128 kWhs
Expert
Joined: 3 years ago
Posts: 351
 

@bontwoody Maybe they have corrected it, I hope so.

Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas


   
ReplyQuote
(@hughf)
Noble Member Member
2999 kWhs
Joined: 2 years ago
Posts: 489
 

@ecobaker ah damn…. Swap that out for a UPM GEO then….

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@heacol)
Noble Member Contributor
2128 kWhs
Expert
Joined: 3 years ago
Posts: 351
 

Posted by: @hughf

Remove the llh and the secondary pump, wire the pwm line of the primary pump up to the Samsung controller…. That’s pretty much all there is to it.

 

Yes, just make sure you have the correct flow rate at all times.

 

Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas


   