Removing a Low Loss Header from Samsung Gen6 System
My system has a low loss header, which for effiency I’d like to remove. Currenlty averaging a daily COP of 3.5 to 3.8, which is good but I’d like it to be better. I have a 8k Samsung gen6, however all the installation information from Samsung or Joule says to use a header or buffer. My system map is this, its fairly simple one zone in two bedroom mid terrace.
Those of you with Samsung gen6 HP do you have a system without a header or buffer, my plan was to just remove it and connect up the flow and returns and see what happens. I just want to make sure I’m not doing something catastrophic before its done.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
Hi
I have a Samsung Gen6 (5kW) running without a LLH or buffer etc. I basically followed Glyn Hudson's tutorial on Youtube. It works fine for me. I guess you need to investigate why they decided to put one in in the first place.
Heatgeek states the reasons for doing it as "High flow rate requirement in the system, high resistance across the system/boiler pump is too small, or multiple heat sources for the property". the link is here https://www.heatgeek.com/low-loss-headers/.
I would imagine the middle one is most applicable to you, so you need to be looking at 28mm pipes to the heat pump itself and then look at the pipe configurations to the rads to make sure they they can carry the heat required at a reasonable flow.Here is a good explanation of that https://youtu.be/1FYv1RnVDrI.
Also check pump sizing. (BTW I dont think your pump supports PWM which is a shame as the heat pump can use it to adjust flow rate automatically, see here https://thegreeningofrosecottage.weebly.com/blog/alls-well-that-ends-well )
As long as your radiators are all open I cant imagine water volume would be an issue, but you could check just to be certain.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@ecobaker They work reasonably well on open zone, just make sure you always have the minimum flow rate.
Attached is a manual with the open zone programmer settings.
The Samsung DOES NOT support pulse width modulation pump control below 45 Deg Flow temperature, below 45 Deg C it maintains a fixed flow rate of 100%. Not great.
Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas
That isnt correct about the PWM Brendon. Here is my Samsung adjusting flow rate below 45C.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody @heacol I'm not sure my system supports modulation either way.
My pumps are UMP3 AUTO, with flow rate setting buttons on them, both currently set to max flow rate, so the heat pump cant modulate them. The secondary pump is permanently on and the primary pump switches on and off controlled by the heat pump. My flow rate round the system when heating is 26 lpm, appropriate for what Samsung recommends. I think my rate could be lower if I've done my maths right, around 16lpm. I could manually reduce the flow rates of the pumps and see what happens. I think my DeltaT is only about 2 degrees currently. Although I don't have very accurate monitoring.
The volume of my system is over 48 litres just in the radiators, so I am well with in minimum requirments for the 8kw pump.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@bontwoody That flow temperature is pretty close to 45 Deg C (43 deg C), it could be sensor drift that is causing the activation, it is clear that it is not activated at lower temperature. I have seen the official documentation, not publicly available. It is a great shame, as it has a detrimental effect on the performance of the refrigerant circuit. Possibly something to do with the finding that they become very unstable below 30 Deg C flow temperature.
I would be more concerned about the control strategy of the heating system, 45 Deg Flow temperature at 5+ ambient temperature? COP +- 3.5, pretty dismal. (unless you did this as a demonstration or hot water production)
Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas
In the middle of renovating an old stone cottage and both my wife and I like it hot inside so higher than desirable flow temperature at the moment. Should improve next winter now I have finished insulating and radiator upgrades to the new living room. Still beating gas though.
@Iancalderbank pointed me to the PWM control possibility and I think he has an 8kW Samsung model. Here is the pump modulation again at a lower flow temperature of about 41C. Perhaps Ian can add to the data available.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Remove the llh and the secondary pump, wire the pwm line of the primary pump up to the Samsung controller…. That’s pretty much all there is to it.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@bontwoody Maybe they have corrected it, I hope so.
Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas
@ecobaker ah damn…. Swap that out for a UPM GEO then….
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Yes, just make sure you have the correct flow rate at all times.Posted by: @hughfRemove the llh and the secondary pump, wire the pwm line of the primary pump up to the Samsung controller…. That’s pretty much all there is to it.
Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas
- 25 Forums
- 1,612 Topics
- 34.8 K Posts
- 61 Online
- 1,887 Members
Join Us!
Latest Posts
-
RE: In the middle of an ASHP installation - a few questions
Oh dear! How close is their behaviour to fraud? Over ...
By Judith , 10 mins ago
-
RE: Midea ASHP – how to set weather compensation
Many thanks @mphb and @cathoderay. Didn't expect so qui...
By iWolf , 25 mins ago
-
RE: British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
@jancold My day 1 of install over. It started at 7 wi...
By Lucia , 11 hours ago
-
RE: Undersized Vaillant ASHP and abandoned by installer
Ps to the above. The requirements on the heat pum...
By JamesPa , 11 hours ago
-
The greenhouse tomatoes have ,as usual, done well but t...
By Jancold , 11 hours ago
-
RE: Locational electricity pricing
@transparent Phew! ok have skim read despite hectic d...
By Lucia , 11 hours ago
-
RE: How to Solve Mould and Mildew Issues in Renovated Properties
The answer if you’re doing a major renovation is a MVHR...
By Judith , 11 hours ago
-
RE: Will heat pump heat hot water without increasing the temp in my home?
Do you have a reference for that directive @toodles ? ...
By Transparent , 13 hours ago
-
RE: Calculating inverter size to match battery size
I expect your Seplos kit came with some guidance as reg...
By Toodles , 15 hours ago
-
RE: Determining correct flow rate for a heat pump
It’s clear from what you say, above and what we have ex...
By SUNandAIR , 19 hours ago
-
'If you are not part of the problem there's good money ...
By AllyFish , 24 hours ago
-
RE: Suitability of 45C flow temp with existing pipework
I've ordered a cheap borescope online and I'm going to ...
By Alex_N , 2 days ago
-
RE: Ecodan - flow rates, sensors, settings
Hi @rhh2348 , coming late to this thread as our Ecodan ...
By SUNandAIR , 2 days ago
-
RE: Agile: average import cost vs other tariffs?
@tim441 Last year I ‘netted’ about £400 that way so I h...
By Toodles , 3 days ago
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
@irmartini I think that @editor might sympathise with t...
By Toodles , 3 days ago
-
RE: Heat pumps don't work: debunking myths & misconceptions
I applied for my G99 last November. Largely as a resul...
By IanMK13 , 3 days ago
-
Setback for Vaillant Arotherm Plus
Currently our Vaillant Arotherm Plus is set in fully We...
By JWilliams89 , 3 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Unfortunately @burtis James is right. MCS is the Gove...
By Transparent , 4 days ago
-
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
@simonh Im not sure how useful they are but Ive attache...
By bontwoody , 5 days ago
Latest Topics
-
Calculating inverter size to match battery size
By Homonid 1 day ago
-
Agile: average import cost vs other tariffs?
By Tim441 3 days ago
-
Suitability of 45C flow temp with existing pipework
By Alex_N 3 days ago
-
Setback for Vaillant Arotherm Plus
By JWilliams89 3 days ago
-
By Toodles 4 days ago
-
By Jeff 4 days ago
-
By dssr 5 days ago
-
Solar Edge Inverters, returns recycling policy
By AllyFish 6 days ago