Real world advice on ASHP installation - 2 18kW ASHP's recommended
Hi,
I would really appreciate the advice, if anyone has the time or inclination to humour an extreme novice in renewable energy.
We're about to undergo a full reno of a late 70's property, which is just shy of 300sqm in the South West.
As part of the works we're very seriously considering switching from gas to ASHP and have appointed a recommended engineer to design the system (and ultimately use an experienced installer too). The system would be for both heating and water.
My concern is less of whether we are considering enough capacity (from the looks of it, two 18kW units is on the very large side) but more of real world running costs.
The reno works will include insulating the ground floor and installation of a slab with wet UFH, replacement of all windows, doors and garage doors (currently visible air gaps through all, so extremely leaky) and upgradings the rads upstairs and UFh to the bathrooms. We're not installing cavity wall insulation as the property is prone to driving rain, so there is too much concern about water ingress, damp and cold spots.
I don't have the heat loss calcs to hand, (I have asked for them so hopefully I will receive in a few days), but recall 20kW as the output of his calcs.
Am I crazy for considering ASHP, is this far too little information for anyone to begin to pass judgment on? Any advice would be greatly appreciated.
Thanks,
J
Welcome to the forums @mrj. In very quick reply (because I'm heading out the door) the 2x18kW units seems to be on the overkill end of the spectrum. We are currently heating an area exceeding 300sqm in our property with just a single 18kW heat pump, and it's proving more than sufficient. Prior to installation, we sought several quotes, and almost every installer recommended a unit in the 16-18kW range. Interestingly, there was one exception who suggested two 16kW Ecodans. His decision to text us the quote rather than providing a more formal proposal was quite telling.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Blown bonded eps beads in that cavity, that’s definitely something you should do.
are you active on buildhub?
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@editor Thanks for the welcome!
I'm slightly paraphrasing, along with potential for failing memory, but the way it was explained to me was that the the stated output on the ASHP's was not the actual output. From each 18kW ASHP you could expect c.12kW to give a total of 24kW. Whilst the heat loss calcs for the house are c.20kW, he likes to add a buffer hence the over spec.
If in actual fact all of the above is nonsense, then I have one of two scenarios. First I have completely misunderstood what he was saying (distinct possibility). Second is that he has completely over spec'd the system and two 12 kW or a 16kW and a 4kW would be absolutely sufficient..? If it's the latter then my level of confidence has dipped somewhat
@hughf I'm not active on buildhub.
In truth I'm somewhat put off by the stat that 1.5m brits with retrofit cavity wall insulation are unhappy with the result. I appreciate that this covers the full spectrum of unhappiness, but thats 25% of all retrofit cavity wall jobs. I'm just not happy with that type of risk.
@mrj Hi James, I would definitely advocate some wall insulation to keep running costs lower, what about insulated plasterboards internally, your pocket will thank you later 🙂
alternatively if you can run to it, external wall insulation!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I had initially thought insulated plasterboard could be a good solution, albeit my architect dissuaded me from this. I think it might be something I need to look at in a little more detail.
EWI was the suggested route. However this would require planning and detract from the exterior (it's a limestone exterior with cavity to masonry).
I guess what I'm trying to understand is my worst case scenario. If I didn't insulate the walls, would I be left with an inadequate system that ends up costing a fortune in energy bills?
@mrj obviously do all youi can on insulation. others have said that well. 2x 18 sounds enormous even for 300m2. especially if you are making a serious effort on insulation. couple of things to be aware of
- if the actual capacity is significantly below the "nominal plated number" that is a warning flag. Study in detail the capacity tables of any proposed unit. What you DONT want is one of the ones where the capacity goes down as the air temps gets cooler and the emitter water temp gets hotter (which is what you need when it gets colder). Some brands do not have this as an issue.
- with two units you will need a buffer tank. which brings its own complications in terms of trying to control and modulate between two units at full power vs one unit at low power (in mild weather). there's one other regular poster on here, @dunlorn, with a two unit system, and I think he finds it hard to control.
- consider the low modulation point (mild weather) of the system as well. what can it turn down to?
I'm in a 1973 property which is 210m2, no deep retrofit just the crappy 20mm cavity insulation it was built with, I need 9kw at -6C (as proven by this weeks weather), I have a 16kw, which is more than I need. I'd have thought that 1x16 (making sure its one that maintains capacity all the way down the temp chart) would be enough for you.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@mrj Its difficult to say without an in depth heat loss survey. You could do one of these yourself as there is free software out there or if not some companies will charge you up front for one if you ask for a quote.
What reasons did you architect give for not liking insulated plasterboard? A less effective method I have tried is insulated lime render for a wet stone wall. It seems to be dealing with the moisture fine so far but its not cheap at £20 a small bag. Its called cornerstone if you wanted to have a look. Also you could go down a timber frame route and use either kingspan like boards, mineral wool or real wool if moisture is an issue.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Hello @mrj. @iancalderbank is correct. I've 2 x 12kW Samsung units operating as 'master' and 'slave' which aren't particularly efficient and the system as a whole doesn't see a great deal of benefit from the second unit.
I'd avoid having two units combine in a buffer tank, it makes secondary side flow matching a challenge and I end up losing 2-4.5°C across the buffer. If you really do need two units then I'd give some thought to dedicating them to separate heating zones, or upstairs and downstairs say and controlling them independently.
Incidentally, my 12kW Samsung doesn't deliver that once you factor in regular defrost cycles. In cold and damp conditions mine can be entering a defrost cycle every 30-40mins. They only last 5 minutes but their effects are felt for longer and the heat pump can struggle to reach set point LWTs above 42° before the whole cycle starts again. My observations of generated output tell me I'm only achieving around 9kW in these circumstances.
I don't want to get LWTs too high (it's too costly) but if - in practice - you are limited to a peak of 42° or so then you need to make sure your secondary side (emitters) are designed on this basis.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
Hi @iancalderbank @dunlorn, the units are Daikin altherma H HT, which from what I can see are a good quality pump.
Vague recollection of the BUS scheme feeding in to the overall spec, but in truth I need to have a more in depth conversation with the consultant. On initial presentation and conversation my knowledge was as close to zero as you can get. I guess slowly building up so let's see if I can't push him on an explanation.
There could be an element of simply trying to understand why a home with heat loss calcs of 20kW requires 36kW of ASHP's, and that's what I need to get to the bottom of.
If I'm at 20kW heat loss, then it looks like I need two. As @dunlorn noted then maybe one to run the UFH on the GF and the hot water tank and the second the rads upstairs.
@bontwoody It was a concern regarding damp. More that we would need to do a lot more work on understanding how all the different elements interact with each other which adds additional risk to the design. We're looking at a mortar slurry wash, albeit there are planning restrictions over what I can do so it can't be of the same thickness of a render as that would apparently take away from the character of the area. At least according to the planners. Unfortunately everything I do has to received planning approval. Yay
- 22 Forums
- 2,051 Topics
- 44.7 K Posts
- 56 Online
- 3,278 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Yes, the "zoning with ASHP" topic again...
@johnmo Thanks, Johnmo — fair points as always. I ...
By HarryRea , 2 minutes ago
-
RE: How to disable radiator heating in LG HM161MR
If your lowest flow is set to 20 degs, if room temp is ...
By Johnmo , 11 minutes ago
-
RE: Warm weather and heat pumps.
Ours is still on - stat sits at 23 all year round and i...
By HughF , 3 hours ago
-
RE: Renewables & Heat Pumps in the News
If you want to read a huge amount of speculation, fabri...
By Judith , 13 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris hi. Whilst I understand your logic, the FiT is ...
By JulianC , 14 hours ago
-
Thanks it doesn’t provide anymore info just says UD-0
By Gary , 15 hours ago
-
IVT Greenline high pressure switch and electrical cassette errors
I have an IVT Greenline HT Plus C heat pump that is con...
By tdudgeon , 17 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
Not sure if you have the defrost cycle and what happens...
By Johnmo , 18 hours ago
-
A buffer is a legacy issue, they were never used on gas...
By Johnmo , 19 hours ago
-
RE: Hydronic plinth heaters and ASHPs
Thanks. I suspected I was overthinking that part. ...
By benson , 20 hours ago
-
RE: Help optimising my system!
@wh0am3ye you’re absolutely right that what you’re seei...
By Mars , 1 day ago
-
RE: Additional Battery v Wind Turbine v Ripple
There was a call today for Ripple investors and amongst...
By Judith , 2 days ago
-
-
RE: Commencing on an ASHP Installation Process
I think you may very well be right and of course A2A ca...
By JamesPa , 2 days ago
-
-
RE: Agile: average import cost vs other tariffs?
@old_scientist We are with SSEN and our G99 application...
By Toodles , 4 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15, @heacol cover your area… I’d strongly recom...
By Mars , 4 days ago
-
RE: Potentially more choice including air to air heat pump grants
@jeff Such documents are far too wordy for my ‘daily re...
By Toodles , 5 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@grahaml I cannot agree that it is a small percentage o...
By benson , 5 days ago