@iancalderbank I agree. Just bear in mind that the BUS requires MCS and MCS requires that the whole system has been designed and installed under the same contract. My personal conclusion is that BUS costs me too much (because of the imposed restrictions) so I currently plan not to bother with this grant.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I agree with you about BUS adding cost to install contracts. which is one reason why I did what I did. (see my write up).
But, if the householder has previously upgraded a bunch of radiators, and just so happens to have been forward looking enough to make them large enough that they would pass the MCS design criteria, then , as and when they want to go for a BUS/MCS heat pump install, there's nothing to worry about surely - their MCS installer isn't going to say "I didn't design those radiators so I'm going to replace them with some new ones that are the same size" ?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank "But, if the householder has previously upgraded a bunch of radiators, and just so happens to have been forward looking enough to make them large enough that they would pass the MCS design criteria, then , as and when they want to go for a BUS/MCS heat pump install, there's nothing to worry about surely - their MCS installer isn't going to say "I didn't design those radiators so I'm going to replace them with some new ones that are the same size" ?
Hopefully yes. But if they fail to take into account insulation upgrades or extensions with a more modern construction, despite the fact that you tell them about them, then no.
I have had two full 2.5hr surveys done, one of which I paid for one of which was free. In both cases their final calcs were based on solid walls throughout, despite the fact that I told them where the walls had internal insulation or were, in fact, made of lightweight block. So in my experience the most likely answer is 'no'
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - off subject I know but how did you modify your post? I can't see a way to edit a post (though I'm sure there must be a way)
Ideal HP290 10kw heat pump, 2.99kw PV, Powerwall 2, Zappi charger, EV. Midlands location hybrid house part 1911, part 1970, part 2020s.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I’m pleased to say that the intended installer of my heat pump has fully refunded me. They kept me informed of the progress of the refund and we agreed the process which has taken less than two weeks so all credit to them (no pun intended). Not sure of my next steps though.
Ideal HP290 10kw heat pump, 2.99kw PV, Powerwall 2, Zappi charger, EV. Midlands location hybrid house part 1911, part 1970, part 2020s.
Sounds like a descent "installer".!
Unfortunately, I was threatened with a bill for £14000 covering the installation of a Samsung Heat Pump.
I was refused Scottish government payback "because my incompetent "installer" was STRUCK OFF by the NIC Regulator!
To protect me from an incompetent installer I was to be landed with a £14 bill!
Fortunately the Scottish Government stepped in early December asking EST Scotland to repay the initial down-payment.
Full marks to the Scottish Government and EST Scotland.......................no marks to the MCS,NIC and RECC "Charitable Regulators".
YES!, your friendly Regulator , MCS,NIC and RECC , will , when on the defensive , reluctantly admit to being a Charity!
This "Charitable" status was imposed to provide "Light Touch Regulation" !!
ian
Horrendous is the only way I can describe my experience having a Daikin heat pump installed under the Eco4 grant. Forgive my ignorance on technicalities but I'm learning fast! It's 8 months on and I sit here with it all turned off as I await a Daikin installer to fix all the issues as it seems my installer hasn't got a clue and has just given up. They were here for 3 days last week correcting the miriad of problems still left by the Eco4 installer changing pipes and trying to sort wiring problems. Issues from the outset and when I had the funding inspection he failed the system. They had to move tank to loft and rewire something. Still issues, not least waking me at 3am 2 weeks later with horrendous noise in loft and another electrical issue and a leak into the floor where a radiator had to be moved. By then it was summer but it was clear some issues with the water. They sent the Daikin registered company out to check it all, but huge issues to be put right so back they came. Then summer over and no heat! At this point clearly installer had given up so I rang Daikin and handed over to the Daikin company again 2 weeks ago. It's still not right and even they are baffled so awaiting someone from head office to come out, in the mean time left me with it running at huge cost trying to at least get me warm but had set it at 50c as the main set point but left me with no control over anything so not on room thermostat. Cost aside, which was frightening I was absolutely boiling and with days to wait for the return visit and someone from Daikin head office to come and sort wiring I looked up how to turn the main set point down (she had mentioned it over the phone) to 45 cost a bit less but still far too hot, turned it down to 40 next day and house way too hot still so lord knows what is going on. Still costing me way too much I tried the weather compensation curve but after several tweeks no heat and no clue what they have set it to I gave up and turned everything off 3 days ago as it was the weekend and no hope of the cavalry coming and the job they thought would take 2 days max has taken 2 weeks trying to find the issue. Frankly now scared it will never be right and I won't be able to afford to have any heat at all.
@joti Oh Joti! This is very bad indeed. May I suggest you go into the settings on the MMI and set to LWT and set that down to say 35 (or a little lower if still roasting) you can set the slope to -3. Then set the lower limit to 25 (it probably won’t go lower than this anyway) and the right hand point to your intended room temperature (perhaps 20?). Now set the MMI controls for Weather Compensation and allow the system to do its’ reset and syncronise. Have you a thermostat? That should improve matters until the cavalry return; you can refine it later. Regards, Toodles. (I have a Daikin EDLA0E3)
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles Thanks I will give that a go and see what happens. I do have a thermostat but can't use it as they set it to LWT only to see what happened with it set to 50 I presume, I don't think they were expecting me to cook. But as I'm still not sure what the problems are reluctant to change anything else. Thankfully got a bit of sun today as my conservatory gets warm all by it's self pretty quickly. I could write a book on my installation cock ups!
@joti you say you are "cooking" with an LWT of 50, in fact in your previous point you mentioned "cooking" with an LWT of 40. So just to give you a small piece of positive feedback: that does at least imply that your system is capable of heating your house, and also implies it should be able to do so with an LWT of less than 40. In which case, you should be able to arrive at a system that is efficient to run. mid 30's will give you really good efficiency - once the system is setup right. I suggest you post as much possible info as you can about your system . it's usually worth starting a new thread for the discussion of a specific system - then all manner of helpful people will try and help you work out what to do.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Will do. Indeed it does anyone who says it can't heat a house eh! I also noted that it went from 23 to 19 degrees overnight after having turned it off completely at midnight. I thought that seemed pretty good considering 1950's house and currently no loft insulation (another story).
-
Is this ASHP install OK?
3 weeks ago
-
My Journey to Finding the Best Heat Pump for My Home in France
6 months ago
-
What is the most important factor for you when choosing a heat pump brand?
1 year ago
-
Mid terrace - ASHP Install location
1 year ago
-
Any installer recommendations for Samsung ASHP?
1 year ago
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 25 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@heat-pump-newbie as I suspected. I measure/monitor my ...
By Old_Scientist , 4 hours ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 7 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 1 day ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 1 day ago
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 2 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 2 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 3 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 4 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 4 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 6 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 6 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 7 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 7 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 1 week ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 1 week ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 1 week ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago