How to balance a post buffer tank circulation pump?
Hi, has anybody managed to balance the circulating pump in the ASHP with the post buffer tank circulating pump, and if so how did you manage it. Thanks
@potatoman - follow what @ashp-bobba is describing to @netdonkey over on this other topic.
He's addressing a very similar issue!
Save energy... recycle electrons!
@potatoman, to balance a buffer system effectively, both flow rates and flow temperatures on the primary and secondary sides must align perfectly.
Modern air source heat pumps modulate their flow temperature based on the controller’s set point, and many also adjust flow rates to maintain a specific Delta T (temperature difference) on the primary side of the buffer. However, the secondary side is less straightforward.
The secondary pump may regulate flow using pressure control methods, but it cannot directly maintain Delta T due to factors like zone valves or TRVs adjusting flow dynamically. This means the flow to individual emitters isn’t always consistent, which can affect balancing.
Emitters are sized for specific mean flow and return temperatures, and changes in flow rate can shift the Delta T, altering radiator output. Without precise control or measurement of both flow and temperature on the secondary side, true balancing isn’t achievable.
While buffers aren’t inherently bad, they’re often less effective with modern inverter-driven compressors, which perform best in direct systems. Buffers work better with fixed-compressor units, where control is based on return temperatures rather than flow temperatures.
For your specific question, balancing would require synchronising both pumps through careful calibration and possibly additional controls or sensors on the secondary side. However, this level of precision is rarely implemented in standard installations.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@potatoman This post https://renewableheatinghub.co.uk/forums/postid/38331 may also help you.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 36 Online
- 5,744 Members
Podcast Picks
Latest Posts
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 2 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 19 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 21 hours ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 22 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 1 day ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 1 day ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 5 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 6 days ago