Posted by: @burtisDon't know if you have a idea.
My circulation pump next to the buffer is set to max in theory 3.5m³/H
The heat pump is pushing 0.5m³/H
So in theory to balance them better I should drop the pump output??
On the face of it, perhaps, but we do want the pump to take all the heat the heat pump is delivering. But 'set to max' is a bit opaque to say the least. It could be 'set to max' but have a bung in the outlet => flow rate 0m^3/h! In other words, circuit resistance matters.
I have the same problem. compounded by Grudfos jargon. The only pump 'readout' is via traffic light LEDs and I am currently on CC£ sorry CC3 which is Constant Curve Max which is supposed to be constant speed but I have no idea what the actual flow rate is.
I haven't thought of a better way to estimate secondary flow. Maybe other have some ideas that don't involve expensive complicated and intrusive third party solutions?
Midea 14kW (for now...) ASHP heating both building and DHW
Yeah fair buddy mine is on constant 3 basically as high as it can go.
Will leave it for now
I've a similar challenge to yourselves - no fancy monitoring over and above what my Samsung controller is telling me. However, I do have a few cheap temperature sensors and by using these to measure secondary flow and return temps, along with knowledge of how many kW are being generated, I can make an approx estimate using the equation below. Note this assumes the figure for heat energy generated (measured at the heat pump) is the same as the heat energy transmitted to the secondary side, which is pretty reasonable if you're in stable conditions.
Generated Energy (kW) = Flow Rate (litres/sec) x Specific Heat Capacity (4.18 for water, around 3.9 for glycol, depending on concentration) x Temp Difference (°C between flow and return).
It's a little approximate because my temp measurements aren't exactly accurate to 0.1°C but, do this a few times when your system is stable, and you'll have a half decent estimate . Try it at different pump settings and you'll be able to plot your own characteristic system curve!
I try to make my secondary flow as near as possible to the primary flow, or slightly lower. This minimises turbulence (and losses) in the buffer tank and means I see only a small temperature drop from primary inlet to secondary outlet.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
Another update with no fruit
Still absolutely no communication from MCS or NAPIT since 5th of December.
Called NAPIT a while ago and they said they will get back to me within their time frame of 5 to 10 days 😢
Looks like MCS are launching their new website and processes in January so that may be a cause of slow down and I guess being near Christmas.
This is going to take a loooooong time it seems to get anywhere.
Installers have again said they don't want to do any work including the service, fitting/filling up anti freeze and sorting the basic installation problems out.
@burtis it's unbelievable how appalling and frustrating this process is.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Another day of flow errors, oh what joy....
Still no reply either
Will start the process of contacting everyone again tomorrow...
@burtis - can I check if you are reading other topics here where ASHP owners are delving into issues and identifying the causes of problems?
The feedback from @cathoderay on his Midea unit is particularly insightful.
He is going far deeper into the technology that others would ever expect to do.
There's a massive difference between the information supplied by manufacturers to the likes of MCS and DESNZ,
and what end-users are actually experiencing.
Until the 'official bodies' realise that they need to involve the general public in their analysis, we will continue to see new regulations and policy developed which fails to address the issues.
@editor please take note, I've stated that very deliberately!
Save energy... recycle electrons!
Yeah I have a browsed a few things here and there buddy.
Hard to keep up with a lot of it as I also browse Facebook groups as well as working 50 hours weeks 😅
I have found if I get a error I can clean the filter even though it's clean every time and dump the water out that in that section of pipe. Re fill it and it kicks back into life.
I will look into what you mentioned later regarding the other posts in more detail.
Cheers buddy
NAPIT have reopened the case and it's being reviewed again.
Thanks to MCS saying that their Audit is not a justified case for the issues that I have.
Just a waiting game again now
Posted by: @transparentUnfortunately @burtis James is right.
MCS is the Government's preferred vehicle to deliver the domestic initiatives they wish to promote (solar panels, battery storage, Boiler Upgrade Scream etc).
Apart from fees paid to it by those it accredits as installers, it also receives significant income from HMG itself.When it comes to the issue of Heat Pumps, MCS made its case to Government that the accredited installers should self-certify their work in the same manner that electricians do.
MCS considers itself as worthy an organisation as the National Inspection Council for Electrical Installation Contracting (NICEIC), ELECSA or Electrical Contractors Association (ECA).
But the evidence doesn't bear that out.
Whilst we enjoy high professional standards in respect of the electrical portions of heat-pump installation, contractors don't even appear to understand the relevant Building Regulations requirements.The people who should be complaining about this are the Local Planning Authorities.
They have responsibility for enforcing Building Regulations, and can be held to account (legally) if they allow work in their area which doesn't comply.
MCS has made an arrangement which goes above their heads - a conflict with the existing legislation.That's why I write here on the Forum that consumers with failed installations should be communicating with their local LPA Councillor.
It is they who have the mandate to ensure that Building Regulations are enforced.And if that fails, then your next recourse is to your MP.
Government shouldn't have granted permission to MCS that they can stray into Planning legislation.
Yes, I've done a lot of research into this.
So you can copy whatever you need from my posts here on the Forum in order to inform Councillors and MPs what the problem is.
at the bottom of our installers invoice it said we were liable for confirming LPA standard/guidelines met etc. Thankfully we were all ok with ours
16 days again so far running trouble free no flow errors.
No updates from NAPIT about anything.
I have signed up the the Energy Sure program though as it is behaving itself again.
A *free* Homely to monitor the system in better detail may help future diagnosis but also it just looks like a better system than what Midea provide.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 70 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 53 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 59 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 3 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 4 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 15 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 18 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 19 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 22 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 23 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 24 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 4 hours ago
-
SolarPV tables / online calculator
By MichelleC 11 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 23 hours ago
-
By Toodles 2 days ago