Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
How to balance a post buffer tank circulation pump?
Hi, has anybody managed to balance the circulating pump in the ASHP with the post buffer tank circulating pump, and if so how did you manage it. Thanks
@potatoman - follow what @ashp-bobba is describing to @netdonkey over on this other topic.
He's addressing a very similar issue!
Save energy... recycle electrons!
@potatoman, to balance a buffer system effectively, both flow rates and flow temperatures on the primary and secondary sides must align perfectly.
Modern air source heat pumps modulate their flow temperature based on the controller’s set point, and many also adjust flow rates to maintain a specific Delta T (temperature difference) on the primary side of the buffer. However, the secondary side is less straightforward.
The secondary pump may regulate flow using pressure control methods, but it cannot directly maintain Delta T due to factors like zone valves or TRVs adjusting flow dynamically. This means the flow to individual emitters isn’t always consistent, which can affect balancing.
Emitters are sized for specific mean flow and return temperatures, and changes in flow rate can shift the Delta T, altering radiator output. Without precise control or measurement of both flow and temperature on the secondary side, true balancing isn’t achievable.
While buffers aren’t inherently bad, they’re often less effective with modern inverter-driven compressors, which perform best in direct systems. Buffers work better with fixed-compressor units, where control is based on return temperatures rather than flow temperatures.
For your specific question, balancing would require synchronising both pumps through careful calibration and possibly additional controls or sensors on the secondary side. However, this level of precision is rarely implemented in standard installations.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@potatoman This post https://renewableheatinghub.co.uk/forums/postid/38331 may also help you.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
- 26 Forums
- 2,694 Topics
- 63.2 K Posts
- 629 Online
- 7,105 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: What is possible with FIT, SEG, Hate Pumps and Batteries?
On the right tariff, there is no reason a well installe...
By Old_Scientist , 1 hour ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
So... after 2 frustrating years, with a COP of 2, for a...
By bubuontheweb , 2 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
It's worth also remembering (as @transparent partly cov...
By Majordennisbloodnok , 19 hours ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
Not so sure. When I read Octopus' article, they seemed ...
By Majordennisbloodnok , 20 hours ago
-
@transparent I would imagine that DW’s inverters are no...
By Toodles , 21 hours ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
@judith Standard UK style plastic frame double glazing ...
By EtchedPixels , 22 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@bobflux That's the stuff. The installer recommended tw...
By tomasmcguinness , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@chandykris Indeed, the elevated temperature does atten...
By Toodles , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Anyone able to share the name of a competent independen...
By Papahuhu , 2 days ago
-
I applaud you for this initiative; however, I can see a...
By L8Again , 3 days ago
-
RE: Nook batteries from Octopus
Both of octopus' new batteries are Fox ESS units re-bad...
By sonosppp , 3 days ago
-
The drawing is fine and perfectly understandable except...
By bobflux , 3 days ago
-
RE: Design Of Cascade System Replacing Undersized ASHP
How does the installer propose to control it? Do Clivet...
By alincork , 3 days ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Can you post pics of the cassette and heat pum...
By alincork , 4 days ago
-
RE: Finally got everything up and running (well, almost)
Hi Guys I'm new to the forum but have been u...
By JandP , 4 days ago