Poor COP with an Ecodan
Hi Guys,
I'm hoping you may be able to help. I'm getting (I think) poor COP. In November so far I'm getting a cop 2.39, with heating being a cop of 2.71 and DWH being 1.65. My heating is weather compensation with a flow rate which doesn't go higher then 30c at -2 outside and the DWH is set at 45c with it heating back up when it drops by 12c. All rads are fully open upstairs and downstairs we have underfloor heating. Thermostats are set at 23c with room temperature of around 21c downstairs and upstairs of around 20-19c. I've attached pics of my readings and the model.
It does sound a bit low. My DHW COP is exactly 2 for November. I run my DHW at what is normally the warmest time, 2pm.
Where in the country are you?
Do you have a buffer, low loss header or similar on your system?
Is your heating on all the time or do you have it on and off?
Can you access Melcloud to see what the flow temperatures are doing over time?
The Ecodan measures of consumed and delivered energy are notoriously inaccurate though, especially at low usage. Your usage is very low - do you have a small or very well insulated house?
Hi Kev,
I'm in Wales.
I'm not sure, how would I find out what I have regarding the buffer ect.
The last two days I have and the cop has got worse.
No, I don't have access to the melcloud. How do I get access to that?
I have a 3 bedroom/2 and half bedroom house and it's well Insulated. It's a new build, built this year.
Sorry, I know I haven't been much help there
@adam_colwell Hi Adam. The COP numbers do sound very low given the flow temperatures you are talking about and the insulation values of your house. Do your bills corroborate the COP readings you are reading?
Where abouts in Wales are you? Mark
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Hi Mark,
Yeah my electricity bill does,in total yesterday i used 15kwh , 9kwh of that is heating and water.
I'm in Mid Wales near Aberystwyth.
@adam_colwell I have a 5kW Samsung, but used to have the same Mitsubishi ASHP as you and I was doing quite a bit better in terms of COP.
9kW for heating and water doesnt sound that bad, I used 9.9 kWh yesterday and 13.5 the day before. I do use an immersion for my hot water but it averages about 3kWh a day. Given you are warm and your usage isnt that high, perhaps the COP given by the monitoring system isnt correct?
My house is old and much leakier than yours but my heating COP is 3.6 for the past two days. How long do you run your heat pump for in a day? I probably do so for about 12 hours.
If your COP is really that low, I think I would start by looking for areas where Im leaking heat such as pipe insulation outside and in the loft. You can view my heat pump stats via the link below. My blog is also linked so you can have a look at my setup.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody am the moment, I'm running my heating 24/7, well the thermostats are calling for heat 24/7. The heating is going from working to standby around 4 times an hour.
@adam_colwell So you are running your heating for twice as long as me with a similar energy usage? It doesnt feel to me like your reporting system is accurate. I have an openenergy monitor system so Im confident my reported COP is accurate. Ball park I would guess you are actually getting a very good COP. You didnt say how big your house was, mine is a two bed bungalow, so if your is larger that would again suggest you are doing a lot better than you think 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody it's a three bed semi detached house. Hopefully it is just reporting it wrong. I'll look at getting the Melcloud app, because by what people are saying, hopefully that is accurate
@adam_colwell I dont have experience with Melcloud but if you can run to putting a heat meter in your circuit it will give you accurate figures. Im pretty confident now that your heat pump is working well 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@adam_colwell I have an Ecodan they don’t modulate down well. If you are running flow temps that low it will be cycling on and off and that will be why your COP is low. I have an 8.5 kw unit and I have figured out over the past few years that it can’t run lower than 32C without cycling on and off several times an hour.
You could try pushing your WC curve up a few degrees and see if it cycles less and see if that improves your COP
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 52 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 23 minutes ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@heat-pump-newbie as I suspected. I measure/monitor my ...
By Old_Scientist , 15 hours ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 19 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 2 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 2 days ago
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 3 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 3 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 3 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 4 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 5 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 5 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 5 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 7 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 7 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 1 week ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 1 week ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 1 week ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 1 week ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 1 week ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 2 weeks ago