Plate heat exchanger considerations
@jamespa I don't understand any point in an air test, if that fails, then the pipes are then broken, and the system cannot be refilled without digging up concrete and ruining finishes. Am I missing something?
Also, will the secondary circuit behind the PHE count towards the system volume of the primary circuit with the heat pump on it, or will we also need a volumizer? Why don't hot water circuits need minimum volumes?
Posted by: @scalextrix@jamespa I don't understand any point in an air test, if that fails, then the pipes are then broken, and the system cannot be refilled without digging up concrete and ruining finishes. Am I missing something?
If it blows open a joint or a pipe you are correct of course. Perhaps more likely it will detect an existing slow leak due eg to a pinhole in a solder joint or even a pipe and the leak will be detectable in the air pressure but not much water leaks out. Most likely it will detect nothing, but in principle the risk you identify does exist.
Posted by: @scalextrixAlso, will the secondary circuit behind the PHE count towards the system volume of the primary circuit with the heat pump on it, or will we also need a volumizer? Why don't hot water circuits need minimum volumes?
If the pump speeds are correctly matched and the PHE correctly plumbed then yes, but if, for example, the secondary pump is switched on and off by a thermostat (which some installers do) then no, because there is no guarantee that the secondary will be in circuit during defrost.
DHW circuits dont need min volumes because either (a) the heat pump switches to heating mode when doing defrost or (b) the dhw in the tank has sufficient energy which is transferred via the coil. I dont actually know which, or whether some heat pumps switch and others dont.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespathere is no guarantee that the secondary will be in circuit during defrost
Thanks, this is what I was thinking about, so as long as heat energy can transfer back through the PHE into the primary circuit during defrost, then that's fine. I suppose the secondary pump needs to run off of the same circuit as the primary pump so they are matched.
I suppose the other issue is cycling, and I can't quite get that straight in my head. Suppose as long as the PHE is doing it's job well, then the return flow temperature drop to the HP, will keep it running?
Posted by: @scalextrixI suppose the secondary pump needs to run off of the same circuit as the primary pump so they are matched.
They need to be switched on/off together. The pump rates may differ however. There is a bit of an science to setting up PHEs which I haven't fully understood yet; your installer should of course do this correctly but we all know what installers are like
Posted by: @scalextrixI suppose the other issue is cycling, and I can't quite get that straight in my head. Suppose as long as the PHE is doing it's job well, then the return flow temperature drop to the HP, will keep it running?
Depends on how the water pumps work. Some heat pumps leave the water pump running 24x7, others allow it to switch off and then switch it back on again from time to time to sample the current conditions. This is something again the installer needs to think about and understand properly. Unfortunately this is another reason to deprecate the use of PHEs (but I understand why you are proposing to have one).
Incidentally an acquaintance of mine is currently proposing to run his HP on a vented system without a PHE. Not sure what installers will make of that.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaIncidentally an acquaintance of mine is currently proposing to run his HP on a vented system without a PHE. Not sure what installers will make of that.
As far as I can tell my vented system would have a peak pressure of about 0.5 Bar, which technically does meet the absolute minimum pressure of the ASHP (also 0.5Bar) specifications, but you are then hoping the sensor is very accurate and if it isn't, fault codes and no heating I suppose.
I wish your acquaintance all the best!
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 24 Online
- 5,662 Members
Podcast Picks
Latest Posts
-
Powerwall 3 or Myenergi or something else?
Bit of background, 4 bed house 7.35kw heat loss, gas di...
By AdamK , 1 hour ago
-
RE: Does anyone have experience of a smart water meter?
Thanks, @technogeek. So far as I can make out, whilst...
By Majordennisbloodnok , 4 hours ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 6 hours ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 6 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 1 day ago
-
@bontwoody me too. I've contacted Heat Geek today, and ...
By Mars , 1 day ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 1 day ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 3 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 4 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 4 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 5 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 5 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 6 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 1 week ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 1 week ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 1 week ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 1 week ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 1 week ago