Pipe Work Question?
I'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
I think the 22mm plastic pipe might be a bit small for 8kw. 22mm copper is considered ok for 5kW I think. This link gives more detail. https://www.heatgeek.com/does-my-pipework-need-upgrading-for-a-heat-pump-with-cheat-sheet/
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
The issue with the 22mm plastic piping in your loft could potentially impact the efficiency of your heat pump system, especially if it differs from the rest of your installation in terms of diameter. We have this issue where the previous owners “narrowed” the pipework when they extended the heating to the north end of the house, creating a bottleneck which I think is the major issue that the rads at the far end of the house struggle.
Did your installers run all the pipework for your system - copper and the 3.5m run in the loft?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Yes so the pipe work from the HP that runs externally to the loft is copper, then the pipe work runs length of loft to the other end where the DHW tank is, that section inside the loft is plastic. I need to measure accurately to check diameters, but im fairly certain that it’s the same as the copper pipes.
Thinking about it now, all l the pipe work externally from the HP is insulated, I’ve assumed it copper, but don’t know for sure, I might have to check that.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
There is a good video explaining the pipe sizing issue here
https://renewableheatinghub.co.uk/forums/postid/29119
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @ecobakerI'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
That's too tight IMO, we would use 28mm copper, or 32mm MLCP
Technical Manager & Professional Installer: Ultimate Renewables
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 25 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
@carlo the 16kw rating refers to output.. afaik? So w...
By Tim441 , 9 hours ago
-
Anyone still weathering it out with Agile?
Being curious, I have continued to monitor the daily ra...
By Toodles , 15 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 19 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 2 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 2 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 4 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 4 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 4 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 4 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 5 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 5 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 5 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 6 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago