To add to the conversation, we've been using about 70-75kWh of electricity per 24 hours running on weather comp for our 18kW ASHP. House is lovely and warm, 21C in most areas. Compared to a winter a few years ago when we ran at 45C set point, we were doing 110kWh per day. Glad to see temperatures rising to double digits in a few days time, which will see our consumption drop well below 50kWh for 24 hours.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@iancalderbank - your second chart, zooming in on a single defrost cycle, is interesting, in that, apart from the RWT, and a slightly different but not by much time frame, the temps follow exactly the same pattern as seen in my zoom in on a single defrost chart. Interesting, in that two different installations with different brands of heat pumps do the same thing.
I wonder, does your heat pump sit in it's own microclimate? You have the same rise in OAT during the defrost as I do, which according to @derek-m's theory means that at other times the normally running heat pump is lowering the OAT. My own view, as you will know, is that this is normal behaviour that applies to many if not most heat pumps.
The failure of my system to reach the desired/design IAT in cold weather is I think largely another problem: the heat pump is simply under-specced for the loss/demand. Of course other factors affecting efficiency don't help, but the root cause is 11kW supplied will never meet a 12kW loss.
Midea 14kW (for now...) ASHP heating both building and DHW
@hughf Thanks 🙂 Im glad my self-install worked as I had hoped even though I used plastic piping for the new circuits.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody My self install seems to be working nicely too, despite me ignoring the manufacturers instructions and running it direct, open loop... I strapped the buffer sensor to the CH flow pipe after the 3 port 😀
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@hughf Makes you wonder doesnt it, if total amateurs like us can get it right how do so many installers manage to get it wrong 🤣 Dont mention the dreaded B word!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I think the answer is that we are "total amateurs" who really really gave a damn. read every document. watched loads of training and education video's. studied best practice. paid care and attention to absolutely everything. I wish there was a way to make use of this without actually becoming an installer!
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank we can argue with installers on Linkedin about how they're mostly incompetent 😀
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @cathoderay@iancalderbank - your second chart, zooming in on a single defrost cycle, is interesting, in that, apart from the RWT, and a slightly different but not by much time frame, the temps follow exactly the same pattern as seen in my zoom in on a single defrost chart. Interesting, in that two different installations with different brands of heat pumps do the same thing.
I wonder, does your heat pump sit in it's own microclimate? You have the same rise in OAT during the defrost as I do, which according to @derek-m's theory means that at other times the normally running heat pump is lowering the OAT. My own view, as you will know, is that this is normal behaviour that applies to many if not most heat pumps.
The failure of my system to reach the desired/design IAT in cold weather is I think largely another problem: the heat pump is simply under-specced for the loss/demand. Of course other factors affecting efficiency don't help, but the root cause is 11kW supplied will never meet a 12kW loss.
I always see a dip in the OAT as measured by the heat pumps own sensor whilst its running. I don't think there's a microclimate. There's simply a massive flow of air, that puts a bit of wind chill on the sensor , which is physically on a short wire on the upper back of the unit. If the wire was longer, I could site it well away from the unit . In that case I'd expect it not to vary with run state. But given this is what the manufacture gives us, and its the same, on 10000's of deployed units, I assume they must allow for this behaviour in their controls. In defrost mode, there's a large cloud of warm water vapour thats pushed into that same physical area. It briefly clouds up the window of the nearby utility room, so its no surprise it moves the OAT sensor higher for a few mins.
ref your heat loss - If you were able to run at a lower LWT, then IIRC the theory says they defrosts would be less frequent and thus effective output slightly better. Its also the case that often the capacity varies by LWT , its never the "nominal plated number" . So (speculating) you might perhaps get an extra 0.5kw out of it at 45C vs 55C. Suggest checking the data book to see if going through the emitter-side work to get yourself a lower LWT gains capacity.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
A sensor should not suffer from 'wind chill', since it is not a heat source.
@derek-m maybe thats not the right technical term. I'm just telling you what it does. If you stand by the heat pump its a LOT colder when its running. I had to do some minor property maintenance the other day in the full blast. 7 layers on and still numb in 5 mins, had to give up. Ok so the sensor isn't directly in the blast - its on the upper back . but it doesn't surprise me it drops a bit at all. Not sure how many people actually graph this level of detail from a sensor that is physically on the unit.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @hughf@iancalderbank we can argue with installers on Linkedin about how they're mostly incompetent 😀
thinking about the installers (and related roles) that I follow , who discuss this subject area on Linkedin, they are largely the good ones I think. Its the ones not discussing how best to make these systems work, just "banging them in" that are the issue.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Yep mine is near 2 degrees colder when it's running according to reading on my unit. Noticed it few times.
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 35 Online
- 3,353 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent That’s the current concern.
By Toodles , 2 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Being with Octopus, I’m paid 15p for any exported kWh, ...
By AgentGeorge , 4 hours ago
-
RE: 5 Star Service from Havenwise
Oh good! I was wondering when/if you might pick them ...
By Transparent , 20 hours ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
update - my old installer insisted on a heat loss of 11...
By MatWin , 22 hours ago
-
I agree it's not very helpful. Generally, the max heat ...
By Old_Scientist , 23 hours ago
-
RE: Commencing on an ASHP Installation Process
I think therein lies the problem. Ratio of quotes to i...
By JamesPa , 2 days ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
Hive and most other smart thermostats don't play well w...
By JamesPa , 2 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Thanks for the input. I've been running various experim...
By Grahamh-uk , 2 days ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet Hi, this sounds great is you are getting 5...
By ASHP-BOBBA , 2 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 3 days ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 3 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 4 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 5 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 5 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 5 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 5 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 6 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 7 days ago