To add to the conversation, we've been using about 70-75kWh of electricity per 24 hours running on weather comp for our 18kW ASHP. House is lovely and warm, 21C in most areas. Compared to a winter a few years ago when we ran at 45C set point, we were doing 110kWh per day. Glad to see temperatures rising to double digits in a few days time, which will see our consumption drop well below 50kWh for 24 hours.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@iancalderbank - your second chart, zooming in on a single defrost cycle, is interesting, in that, apart from the RWT, and a slightly different but not by much time frame, the temps follow exactly the same pattern as seen in my zoom in on a single defrost chart. Interesting, in that two different installations with different brands of heat pumps do the same thing.
I wonder, does your heat pump sit in it's own microclimate? You have the same rise in OAT during the defrost as I do, which according to @derek-m's theory means that at other times the normally running heat pump is lowering the OAT. My own view, as you will know, is that this is normal behaviour that applies to many if not most heat pumps.
The failure of my system to reach the desired/design IAT in cold weather is I think largely another problem: the heat pump is simply under-specced for the loss/demand. Of course other factors affecting efficiency don't help, but the root cause is 11kW supplied will never meet a 12kW loss.
Midea 14kW (for now...) ASHP heating both building and DHW
@hughf Thanks 🙂 Im glad my self-install worked as I had hoped even though I used plastic piping for the new circuits.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody My self install seems to be working nicely too, despite me ignoring the manufacturers instructions and running it direct, open loop... I strapped the buffer sensor to the CH flow pipe after the 3 port 😀
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@hughf Makes you wonder doesnt it, if total amateurs like us can get it right how do so many installers manage to get it wrong 🤣 Dont mention the dreaded B word!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I think the answer is that we are "total amateurs" who really really gave a damn. read every document. watched loads of training and education video's. studied best practice. paid care and attention to absolutely everything. I wish there was a way to make use of this without actually becoming an installer!
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank we can argue with installers on Linkedin about how they're mostly incompetent 😀
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @cathoderay@iancalderbank - your second chart, zooming in on a single defrost cycle, is interesting, in that, apart from the RWT, and a slightly different but not by much time frame, the temps follow exactly the same pattern as seen in my zoom in on a single defrost chart. Interesting, in that two different installations with different brands of heat pumps do the same thing.
I wonder, does your heat pump sit in it's own microclimate? You have the same rise in OAT during the defrost as I do, which according to @derek-m's theory means that at other times the normally running heat pump is lowering the OAT. My own view, as you will know, is that this is normal behaviour that applies to many if not most heat pumps.
The failure of my system to reach the desired/design IAT in cold weather is I think largely another problem: the heat pump is simply under-specced for the loss/demand. Of course other factors affecting efficiency don't help, but the root cause is 11kW supplied will never meet a 12kW loss.
I always see a dip in the OAT as measured by the heat pumps own sensor whilst its running. I don't think there's a microclimate. There's simply a massive flow of air, that puts a bit of wind chill on the sensor , which is physically on a short wire on the upper back of the unit. If the wire was longer, I could site it well away from the unit . In that case I'd expect it not to vary with run state. But given this is what the manufacture gives us, and its the same, on 10000's of deployed units, I assume they must allow for this behaviour in their controls. In defrost mode, there's a large cloud of warm water vapour thats pushed into that same physical area. It briefly clouds up the window of the nearby utility room, so its no surprise it moves the OAT sensor higher for a few mins.
ref your heat loss - If you were able to run at a lower LWT, then IIRC the theory says they defrosts would be less frequent and thus effective output slightly better. Its also the case that often the capacity varies by LWT , its never the "nominal plated number" . So (speculating) you might perhaps get an extra 0.5kw out of it at 45C vs 55C. Suggest checking the data book to see if going through the emitter-side work to get yourself a lower LWT gains capacity.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
A sensor should not suffer from 'wind chill', since it is not a heat source.
@derek-m maybe thats not the right technical term. I'm just telling you what it does. If you stand by the heat pump its a LOT colder when its running. I had to do some minor property maintenance the other day in the full blast. 7 layers on and still numb in 5 mins, had to give up. Ok so the sensor isn't directly in the blast - its on the upper back . but it doesn't surprise me it drops a bit at all. Not sure how many people actually graph this level of detail from a sensor that is physically on the unit.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @hughf@iancalderbank we can argue with installers on Linkedin about how they're mostly incompetent 😀
thinking about the installers (and related roles) that I follow , who discuss this subject area on Linkedin, they are largely the good ones I think. Its the ones not discussing how best to make these systems work, just "banging them in" that are the issue.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Yep mine is near 2 degrees colder when it's running according to reading on my unit. Noticed it few times.
- 21 Forums
- 1,865 Topics
- 40.7 K Posts
- 79 Online
- 2,184 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Rob is here to help!
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
Latest Posts
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
Hi @stuartornum, would you be willing to share your WC ...
By Grantmethestrength , 2 hours ago
-
Octopus intelligent Go, IOG. maximising slots
Agile user for most of last year but now moved to IOG. ...
By Tim441 , 2 hours ago
-
RE: Agile: average import cost vs other tariffs?
@toodles Partial answer to my own question!EV is 100% f...
By Tim441 , 3 hours ago
-
RE: Not a good January? My heat pump used 840 KWh of electricity
@carpenterstation can you tell us a bit more? Locatio...
By Tim441 , 4 hours ago
-
RE: New Mitsubishi system, several concerns but just a newbie…..
Got home from work today. Same scenario. Nothing callin...
By Carpenterstation , 5 hours ago
-
RE: Grant Aerona3 with Octopus Cosy tariff
We have a Grant Aerona3 as well. We are not on Octopus ...
By davidm06 , 5 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
@jamespa Perfectly possible re the pipes from the Buffe...
By Alfapat , 5 hours ago
-
RE: New Project! ASHP, Solar PV + Battery, MVHR!
@nickmorgan We have a Sunamp Thermino eP210; this may b...
By Toodles , 5 hours ago
-
RE: Air source heat pump roll call
User name: ASHP-AeronaASHP model: Grant Aerona3 13kW HP...
By ASHP-Aerona , 6 hours ago
-
RE: ASHP & Radiator Sizing - Measuring Heat Loss
That's correct. You probably will need to measure flow...
By JamesPa , 6 hours ago
-
RE: Tesla Powerwall charge level.
@gary that’s what I am hoping - whatever he said he is ...
By andy_e , 7 hours ago
-
RE: Do thick walls make for warm houses?
@transparent understood, thanks very much. I'll create ...
By nickmorgan , 8 hours ago
-
-
You can only get 4kw out of the inverter, regardless of...
By Uk_pete_2000 , 9 hours ago
-
RE: Looking for some advice – no viable installer/system – I'm stuck
Wow, thats a lot of gas - you said 120 sq m is that the...
By JamesPa , 10 hours ago
-
RE: 4 port buffer tank connections
In the coming weeks, I’ll be scheduling another session...
By Mars , 12 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@grantmethestrength, thanks so much for the feedback. I...
By Mars , 14 hours ago
-
RE: Is there a problem with SolarEdge monitoring?
@johnr thanks. After not being able to login for at lea...
By Mars , 14 hours ago
-
RE: Is the Grant controller a thermostat?
@davidm06 no doubt you're right, the house is newish an...
By damonc , 1 day ago
Latest Topics
-
Octopus intelligent Go, IOG. maximising slots
By Tim441 2 hours ago
-
Grant Aerona3 with Octopus Cosy tariff
By ASHP-Aerona 6 hours ago
-
New Project! ASHP, Solar PV + Battery, MVHR!
By nickmorgan 7 hours ago
-
By Curlykatie 9 hours ago
-
ASHP & Radiator Sizing - Measuring Heat Loss
By IanMK13 1 day ago
-
By DavidAlgarve 2 days ago
-
Octopus design temperatures confusion
By AndrewJ 2 days ago
-
Is there a problem with SolarEdge monitoring?
By Mars 2 days ago