Our Daikin ASHP
Hello,
I have been browsing for a few days and thought it best to register to say Hi and see if I can get a bit more specific advice. Lots of useful information already and hoping with more specific guidance I can that I will be able to pass forward to some of my friends with identical setups.
We are in a 2020 new build with a Daikin, gas boiler module and outdoor ASHP unit. The ASHP unit is an EVLQ05CAV3. Our DHW is from the gas boiler. We are in a three bed house with 9 radiators. The installer had the DHW set at 60°C, and the weather dependent curve set at; 55°C flow at -5°C and 35°C flow at 20°C.
I have adjusted this to set the DHW at 50°C (still slightly too hot) and the weather dependent curve to 50°C flow at -5°C and 30°C flow at 20°C. The lower limit is set at 30° for the flow temp when adjusting the curve. I see people referencing lower values than this however perhaps this is with UFH or different units?
I have the thermostat/controller in the hall set to 21°C from 07:30 till 22:30 and to 17°C overnight.
I'd be really grateful for some pointers as to how best adjust and happy to provide any further info you may need?
Thanks,
Adam
Is it a thermostat or the ASHP controller?
@adaml ok well thats the thermostat issue solved!
Do you know how much the unit the cycling? If you want to experiment I would suggest just lowering the values on the weather compensation and see what happens, try 1 or 2 degrees and leave it for the day. The other option you have is to keep the numbers the same, just change the ambient down/up.
As example I have rads and my setting is 45@-1 and 25@18 degrees - I had to tweak this morning as the back room was 20 degrees and my wife moaned at me. I think you'll just had to do some trial and error and see what works for you.
Also, whack your TRVs up to 5 everywhere
@batalto Thanks, that's great. I will put the TRV's to 5 and drop a couple of degrees on the curve and review.
It is strange that I can't bring the lower end of the curve down to below 30°C. I wonder what settings others with a Daikin are using due to this?
Any thoughts re running the system as it currently is with a reduced temp overnight vs running it 24/7 at say 21°C?
@adaml my lowest setting is 25. What you can do is just drop the temperature that it kicks in at 30 e.g. 30 at 15 degrees.
I am using mine 24/7 at 21 degrees, but my power at 00:30-04:30 is 5p/kw so its pretty advantageous for me to heat over that time. Do you have a smart meter? you could just do a test if there are two days of a similar temperature and what the impact is. Ultimately, you are going to have to put the heat you lose back into the house
@batalto Thanks for all your help so far!
Okay I understand I can drop the other value, that makes sense, I just didn't know if the value was absolute as in 30°C is the lowest?
I can see why it is in your interest to keep it on 24/7. I am trying to work out is it more expensive to make up the degrees heat lost between 22:30 and when the temp goes back up to 21°C at 07:30 or to maintain a constant temp? No smart meter unfortunately but can get a pen and paper out and give it a shot.
I would be keen to hear from any other Daikin users as well with rads? Also anyone any data for the 24/7 vs dropping the temp overnight? @Kev-M sorry for pulling you in but I noticed in your thread which is full of useful info that you may have looked at this - any advice would be really appreciated?
@kev-m Thank you!
I will have a look at my heat loss overnight as well, this will of course be heavily influenced by the outside temp. I am curious to get some data on it and see if a conclusion can be reached as the consensus seems to vary. @derek-m Please let me know if you have any pointers? I am happy to give it a shot if a couple of days of similar weather are due in the near future.
Would others be able to share their weather dependent curve or to what is extent is it just trial and error? I've adjusted the DHW to 45°C and the weather dependent curve to 45°C flow at -1°C and 30°C flow at 15°C to see how things go. All TRV's are now at 5 also.
Thanks for all your help so far!
Posted by: @kev-mI think @derek-m has done some more modelling on this. Just to clarify; I'm looking at switching it off, not down, at night. That's significantly diffferent. I'll post some results/thoughts on my thread.
Hi Adam,
I would suggest that you have a read through the manual, and see if there are parameters set, that limit the maximum and minimum water flow temperature that the ASHP can produce, if the minimum value is set too high it may be preventing you from lowering the weather compensation curve setting. If you have the Daikin indoor controller unit, it may be possible that this may automatically vary the water flow temperature for maximum efficiency, the manual should give more details on this.
I have attached a copy of the spreadsheet that I produced for Ecodan owners, whilst not for the Daikin it will still provide you with some idea of how the required water flow temperature varies with changes in ambient air temperature.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 342 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Advice on reading thermal images
@editor Hi Mars, this thread has been dormant for a whi...
By colinc , 10 minutes ago
-
RE: Heat Pump Training vs. Real-World Installation
@judith I looked at the control challenge of balancin...
By Lucia , 21 minutes ago
-
RE: Grant Aerona circulation/system pump staying on
@mikefl thank you, I've changed 4200 to 2 and now the m...
By damonc , 2 hours ago
-
RE: Solar panels on side of house to heat water
The original strategy behind the production of bi-facia...
By Transparent , 2 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@batpred I've had a bit of time to look into this to...
By Bash , 3 hours ago
-
RE: Flow rate discrepancy between ASHP and manifold
Air release valves dont always work! You are gonna ha...
By JamesPa , 3 hours ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
Fair enough. I recommend quizzing him to get your mone...
By JamesPa , 4 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@simonwig Thanks for the bump. Not sure why I didn't se...
By HCas , 7 hours ago
-
RE: Are Water Companies Delivering Bricks?!
...which in turn reminds me of a Thelwell cartoon I onc...
By Majordennisbloodnok , 7 hours ago
-
RE: Our journey through Octopus tariffs 2020-2025
I mentioned above "2025 move to Intelligent Go meant ...
By Tim441 , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — thank you, that is useful information you hav...
By cathodeRay , 10 hours ago
-
RE: Electricity price predictions
My apologies. I should've written "The number and dep...
By Transparent , 11 hours ago
-
RE: Help…my NIBE heat pump has faulted again!
If it happens only when it gets cold then it maybe that...
By JamesPa , 11 hours ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
Has anyone got past this screen to set up the integrati...
By AlanW1212 , 12 hours ago
-
RE: Diagnostic Data Needed for Repeatedly Failing Tesla Powerwall 3 System
You seem to be on the right track... Installers are rec...
By Batpred , 20 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
there's a detect cycle setting (4200) on the old grant ...
By damonc , 22 hours ago
-
RE: Commencing on an ASHP Installation Process
@sheriff-fatman It's also worth highlighting that th...
By Lucia , 24 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
. It does but, unless there has been a firmware updat...
By JamesPa , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
Yesterday it was chilly and the cosy6 had a Cop of 4.3 ...
By AgentGeorge , 1 day ago