Our Daikin ASHP
Hello,
I have been browsing for a few days and thought it best to register to say Hi and see if I can get a bit more specific advice. Lots of useful information already and hoping with more specific guidance I can that I will be able to pass forward to some of my friends with identical setups.
We are in a 2020 new build with a Daikin, gas boiler module and outdoor ASHP unit. The ASHP unit is an EVLQ05CAV3. Our DHW is from the gas boiler. We are in a three bed house with 9 radiators. The installer had the DHW set at 60°C, and the weather dependent curve set at; 55°C flow at -5°C and 35°C flow at 20°C.
I have adjusted this to set the DHW at 50°C (still slightly too hot) and the weather dependent curve to 50°C flow at -5°C and 30°C flow at 20°C. The lower limit is set at 30° for the flow temp when adjusting the curve. I see people referencing lower values than this however perhaps this is with UFH or different units?
I have the thermostat/controller in the hall set to 21°C from 07:30 till 22:30 and to 17°C overnight.
I'd be really grateful for some pointers as to how best adjust and happy to provide any further info you may need?
Thanks,
Adam
Is it a thermostat or the ASHP controller?
@adaml ok well thats the thermostat issue solved!
Do you know how much the unit the cycling? If you want to experiment I would suggest just lowering the values on the weather compensation and see what happens, try 1 or 2 degrees and leave it for the day. The other option you have is to keep the numbers the same, just change the ambient down/up.
As example I have rads and my setting is 45@-1 and 25@18 degrees - I had to tweak this morning as the back room was 20 degrees and my wife moaned at me. I think you'll just had to do some trial and error and see what works for you.
Also, whack your TRVs up to 5 everywhere
@batalto Thanks, that's great. I will put the TRV's to 5 and drop a couple of degrees on the curve and review.
It is strange that I can't bring the lower end of the curve down to below 30°C. I wonder what settings others with a Daikin are using due to this?
Any thoughts re running the system as it currently is with a reduced temp overnight vs running it 24/7 at say 21°C?
@adaml my lowest setting is 25. What you can do is just drop the temperature that it kicks in at 30 e.g. 30 at 15 degrees.
I am using mine 24/7 at 21 degrees, but my power at 00:30-04:30 is 5p/kw so its pretty advantageous for me to heat over that time. Do you have a smart meter? you could just do a test if there are two days of a similar temperature and what the impact is. Ultimately, you are going to have to put the heat you lose back into the house
@batalto Thanks for all your help so far!
Okay I understand I can drop the other value, that makes sense, I just didn't know if the value was absolute as in 30°C is the lowest?
I can see why it is in your interest to keep it on 24/7. I am trying to work out is it more expensive to make up the degrees heat lost between 22:30 and when the temp goes back up to 21°C at 07:30 or to maintain a constant temp? No smart meter unfortunately but can get a pen and paper out and give it a shot.
I would be keen to hear from any other Daikin users as well with rads? Also anyone any data for the 24/7 vs dropping the temp overnight? @Kev-M sorry for pulling you in but I noticed in your thread which is full of useful info that you may have looked at this - any advice would be really appreciated?
@kev-m Thank you!
I will have a look at my heat loss overnight as well, this will of course be heavily influenced by the outside temp. I am curious to get some data on it and see if a conclusion can be reached as the consensus seems to vary. @derek-m Please let me know if you have any pointers? I am happy to give it a shot if a couple of days of similar weather are due in the near future.
Would others be able to share their weather dependent curve or to what is extent is it just trial and error? I've adjusted the DHW to 45°C and the weather dependent curve to 45°C flow at -1°C and 30°C flow at 15°C to see how things go. All TRV's are now at 5 also.
Thanks for all your help so far!
Posted by: @kev-mI think @derek-m has done some more modelling on this. Just to clarify; I'm looking at switching it off, not down, at night. That's significantly diffferent. I'll post some results/thoughts on my thread.
Hi Adam,
I would suggest that you have a read through the manual, and see if there are parameters set, that limit the maximum and minimum water flow temperature that the ASHP can produce, if the minimum value is set too high it may be preventing you from lowering the weather compensation curve setting. If you have the Daikin indoor controller unit, it may be possible that this may automatically vary the water flow temperature for maximum efficiency, the manual should give more details on this.
I have attached a copy of the spreadsheet that I produced for Ecodan owners, whilst not for the Daikin it will still provide you with some idea of how the required water flow temperature varies with changes in ambient air temperature.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 263 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 29 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 40 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 3 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 19 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 24 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago