Need ASHP advice for old (1882) stable development in SW Scotland - where do I begin?
@heacol I find that faintly patronising Brendon when you have no idea what my scop is.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Brendon, I'm trying to work out how I access your experience, you are three and a half hours from me by car, do you go that far?
@alan22 So given you have a 100mm kingspan envelope to the building, just using the very simplest estimator from heat geek.
I would imagine you wont be far from 20-30 W/m2. Multiply that by 100m2 and you get a heat loss of about 2-3 kW. Its very basic and I would advise that you might use some of the other methods to double check but if its -3C outside and your electric fan heater can heat your stable then you have verified that it isnt more than 3kW. My old stone cottage is about the same floorspace and runs nicely on a 5kW Samsung so I doubt that its far out. All heat loss estimates are less than perfect (thats why they are estimates!) but having experimental proof of the heat loss is gold dust. Keep up with the experimentation 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@heacol SCOP only needs to be 2.8 to beat gas - and that's what it's all about... not costing more than a gas boiler.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@hughf Its also not that difficult to get SCOPs of greater than 5 in a well insulated new build with free radiator choice and low flow temperatures. (Ive done it) The challenge is trying to get a good SCOP in an old retrofit whilst not busting the bank and causing mayhem.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody indeed, although I would question the viability of having radiators that don't feel warm to the touch, from a homeowner acceptance perspective. That would leave you running at around 37 degrees...
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@hughf I guess you just have to think of them as under floor heating on the wall! 😉
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@hughf I guess you just have to think of them as under floor heating on the wall! 😉
good luck convincing anyone that their radiators will never be warm to the touch... That's why I stick with 38.5 as the hot end of my WC curve - it's just easier that way. Also, my fan coils switch off below 37 ish degrees, flow temperature switch inside.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @bontwoody@alan22 So given you have a 100mm kingspan envelope to the building, just using the very simplest estimator from heat geek.
-- Attachment is not available --
I would imagine you wont be far from 20-30 W/m2. Multiply that by 100m2 and you get a heat loss of about 2-3 kW. Its very basic and I would advise that you might use some of the other methods to double check but if its -3C outside and your electric fan heater can heat your stable then you have verified that it isnt more than 3kW. My old stone cottage is about the same floorspace and runs nicely on a 5kW Samsung so I doubt that its far out. All heat loss estimates are less than perfect (thats why they are estimates!) but having experimental proof of the heat loss is gold dust. Keep up with the experimentation 🙂
The electric heater experiment failed miserably, the thermometer didn't move in 2 hours, it's a small heater and the ceiling is 4m in a 15x5m room, in two hours the heat didn't reach the other end! it was just a silly non scientific experiment but it gives me a feel for KW's maybe, essentially the space being big needs a few hours to heat up, my hope is that an ASHP keeping a low temperature then maintains it, looking on the bright side I think an ASHP is the perfect way to heat it, I think I'm going to need very, very big radiators.
Posted by: @hughfPosted by: @bontwoody@hughf I guess you just have to think of them as under floor heating on the wall! 😉
good luck convincing anyone that their radiators will never be warm to the touch... That's why I stick with 38.5 as the hot end of my WC curve - it's just easier that way. Also, my fan coils switch off below 37 ish degrees, flow temperature switch inside.
It's a fair point, I'm used to coming in from work and lighting a multi fuel burner and feeling skin burn, the idea of tepid radiators is not exactly appealing but.....I have a friend with underfloor heating, when you go into his house it;s the same temperature all the time, never gets hot exactly but it never feels particularly cold, it's a different sort of environment, one I'm only starting to understand, how you turn that up a bit when it's cold though...
@bontwoody it is easy to get SPF's above 5 in ANY house, including old draughty solid stone buildings, I have hundreds to prove it. Get the design and operation right, and it will work. Get it wrong, like most, and it will not. Simple.
If you follow the manufacturer's recommendations, you are 99% guaranteed to get it wrong.
Technical Director Ultimate Renewables Director at Heacol & Head of Domestic Heat Pump Design Net Zero British Gas
- 21 Forums
- 1,818 Topics
- 39.1 K Posts
- 74 Online
- 2,131 Members
Join Us!
Latest Posts
-
-
RE: Is it crucial to get flow temperatures with heat pumps right?
@toodles By the way, have you balanced the system with ...
By Alfapat , 10 minutes ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I thought that they brought in CfD to stop this merry g...
By Abernyte , 43 minutes ago
-
I live in Yorkshire so am in the northern area for mete...
By MikeF , 1 hour ago
-
RE: Running my new Nibe ASHP efficiently
thank you everyone for your insightful replies @toodl...
By jamieheatpumpnew , 2 hours ago
-
RE: ASHP and how it should run and potential kw consumption?
Damn really wasn't expecting those figures, but agree t...
By jeegnesh , 2 hours ago
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
Understood. You suggest (I think) that your data sho...
By JamesPa , 3 hours ago
-
Maybe best not to sound too clever, it might upset him....
By JamesPa , 3 hours ago
-
RE: Best temperature wave form for best economy and efficiency .
Hi @ivanhoew , no worries. This is such a well-informin...
By s_gatorator , 4 hours ago
-
RE: ASHP for small garage and workshop
@transparent I spent a King’s ransom on grid chargeable...
By Toodles , 4 hours ago
-
RE: How do the settings on my Gen 5 Samsung ASHP sound?
@jamespa Some even sit under the DHW tank rather as tho...
By Toodles , 4 hours ago
-
RE: Solar thermal with combi boiler
Can you explain a bit more about the context in which y...
By Transparent , 9 hours ago
-
RE: Can you work an ASHP too hard?
As someone with an over-sized HP and the lower level of...
By HarriUp , 19 hours ago
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
Quite possibly. As I mentioned above the 'ideal' produ...
By JamesPa , 21 hours ago
-
RE: Say hello and introduce yourself
Thank you Transparent ...much appreciated 😊 ...
By ivanhoew , 23 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
Greg Jackson in the Times again just yesterday promotin...
By IanMK13 , 1 day ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Yeah we have a 40l buffer too. Problem is the App doesn...
By MikeH , 1 day ago
-
RE: Mitsubishi Ecodan 8.5kW Monobloc (FTC5) Defrost Mode
@gary no set backs. Yes see others in various forums ha...
By AlsoCold123456 , 1 day ago
-
Looking for homeowner to join our podcast as a guest
We’re looking for a homeowner to join us on the Homeown...
By Mars , 1 day ago
Latest Topics
-
By MikeF 1 hour ago
-
Running my new Nibe ASHP efficiently
By jamieheatpumpnew 8 hours ago
-
How do the settings on my Gen 5 Samsung ASHP sound?
By cyrusir 10 hours ago
-
Best temperature wave form for best economy and efficiency .
By ivanhoew 23 hours ago
-
By Potatoman 1 day ago
-
By DavidAlgarve 2 days ago
-
ASHP for small garage and workshop
By BobTSkutter 2 days ago
-
By ChandyKris 3 days ago
-
Nibe heatpump comms error when freezing
By Toody 4 days ago