No heat in radiators since heat pump failure
I have an Ecodan system that was working fine for the last 4 years until it failed in the cold spell back in December and promptly froze. After defrosting I had a company come out and repair which seemed to go fine and it heats water no problem but only get heat in about the bottom 2 inch's of all the radiators. They have been out and checked the system and say it is working fine !! All statistics and traces from Mitsubishi say it is working fine. Last recommendation from them was to replace the pump which I have done with the one they recommended and still no improvements. Getting to the end of my tether with them. Does anybody have any suggestions on what the problem could be and how to resolve? All rads have been bleed and all full
Weird that the pump is working (as per the latest team to visit) but you're not getting heat to the rads @tony-clarke. My first thought was distribution pump, but that's been replaced. Have you checked your expansion vessel? Is that pressurised and maintaining pressure?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Presume you've bled the radiators? Air might have got into the system during the service?
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
If the heat pump is producing warm water, then I would suggest tracing along the pipework from where it enters your home, measuring the pipework temperature to see where the warm water is going. Ensure any manual valves located on the way are fully open and any actuated valves are functioning correctly.
Has the system been drained down and refilled? If so you may possibly have an airlock somewhere, try opening the filling valve to increase the heating system pressure slightly then bleed the radiators again.
@tony-clarke , Derek’s reply prompted me to remember something that occurred to us a couple of years ago. Our heat pump was working fine, rads were hot, but the UFH stopped working.
We followed the pipework out of the heat pump to the UFH circuit and when we hit the Honeywell valve the water getting to it was hot, but the pipes after the valve were cold. As it turned out, the motor in the valve has died - we replaced it, and everything worked again.
So follow the pipes and see where that leads. Hopefully it’s something simple like a faulty valve.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Radiators that are only getting warm at the bottom only sounds like they are full of air. Easy to check that one. Has the Ecodan got either a manual flow gauge or automatic flow measurement? With all manual valves open, radiator TRVs open and zones calling for heat, easy to check if you have correct flow.
Pumps can cavitate if they are working against closed valves, when that happens their flow drastically reduces and air bubbles will be generated in the system as the pump suction tries to pull water that simply isn't there because something is stopping the flow, but the cause is usually quite obvious. Check all circuit isolation and service valves are open.
Hope it gets resolved soon!
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 38 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 19 minutes ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 1 hour ago
-
RE: Ecodan & MelCloud scheduling
I think the Melcloud timer disclaimer window says it al...
By Majordennisbloodnok , 2 hours ago
-
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 22 hours ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 2 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 3 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 3 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 4 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 5 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 6 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 6 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 7 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 1 week ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 1 week ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 1 week ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 1 week ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 1 week ago