New to Heat Pumps
Hi
Hi Mirnes,
Welcome to the forum.
Thank you for the detailed description of your system, which highlights one of the main problems that people encounter with heat pump based systems, 'how should it be set up for best operation'.
As you have correctly stated, your system has two water pumps, one (pump 1) inside your heat pump system which pushes the water into the buffer tank, and one (pump 2) after the buffer tank which pushes the water around the radiators. Because the buffer tank is just an insulated vessel, with flow and return pipework connected to the heat pump at one side, and flow and return pipework connected to the radiators via pump 2 on the other side. So, what would appear to be happening in your situation, is that even when the room is up to temperature and pump 2 is switched off, if your heat pump is still operating, and pump 1 is running, there is sufficient water flow from pump 1 to push the warm water through the buffer tank and around your radiators. During milder weather conditions, this water flow can be sufficient to cause the indoor temperatures to continue to increase above the desired setpoint.
The easiest solution to your problem would be to have your system rewired, so that the thermostat not only switches pump 2 on and off, but at the same time starts and stops your heat pump.
For improved efficiency, it would probably be better to configure your system for weather compensation. I can give you more details about how to set up your system if you can provide a full list of all the equipment and controls. The manufacturers name and type/model number of each piece of equipment would be adequate.
Posted by: @derek-mThe easiest solution to your problem would be to have your system rewired, so that the thermostat not only switches pump 2 on and off, but at the same time starts and stops your heat pump.
Thank You for your quick reply, I was really hoping to get this kind of answer. I myself also find this the most logical, and just needed this kind of assurance, 'case next week the company who installed the heat pump will address my complaints, and they are as well interested to my claims regarding radiators still getting warm water even external pump is OFF 🙂 so it's good to have the opinion and confirmation of others to better argument my case.
After I rewire my system to this way, I will test for a few weeks, and also wait for the October electricity bill and post back the results
tnx again
Hi,
Hi Mirnes,
I appreciate that English is not your first language, and my Bosnian is non-existent, so if there is anything that you don't fully understand please let me know and I will try to explain in a better way.
Thank you for your detailed description of how your system is operating.
Since your original post in October, there has been a great deal of discussion on the forum about the most efficient way to control a heat pump system. It has been decided that in most cases, the most efficient way to control a heat pump is to use weather compensation.
Let me first of all explain how weather compensation works and then how it can be set on your system.
Inside the outdoor ASHP unit is a temperature sensor, which measures the outside air temperature. This sensor feeds a signal to the indoor controller to tell it how cold or how warm it is outside. As you are no doubt aware, the colder the outside air temperature, the more heat energy that is required to maintain the desired indoor temperature. So if the outside air temperature is say 10C, to keep the indoor temperature at 21C may require a water flow temperature of say 32C. If the outside air temperature falls to 0C, then it may now require a water flow temperature of 42C to keep the indoor temperature at 21C. What is the minimum outside air temperature that you normally get in Winter? This will give you some idea of the settings for the lower end of the weather compensation curve.
By correctly setting the parameters for the weather compensation within the indoor controller, it is possible for your system to automatically vary the water flow temperature, to the correct value required to maintain the indoor temperature at approximately the correct level. By keeping the water flow temperature at the minimum required to meet the heat demand, you should find that your heat pump operates in the most efficient manner and keeps your energy consumption to a minimum.
I am not that familiar with the Midea ASHP controller, so if you would like to contact Batalto (who I believe has a Midea ASHP) on the forum, he will hopefully be able to guide you through the process of setting up your weather compensation.
If you need any further help then please get in touch.
@batalto, can you help in any way?
Call and ye shall be heard.
If its anything like mine - big IF - then you first unlock the controller and go to
- MENU
- FOR SERVICEMAN - CODE 234
- HEAT MODE SETTING
- 3.8 Is your max flow temperature
- 3.9 if you min flow temperature
- 3.10 is the lowest temperature at which you will have maximum flow e.g. -5 degrees
- 3.11 is the maximum temperature at which you'll get the lowest flow temperature
If you have the M-Therm model (like I do) this is the manual -
Password is: midea2020
Page 87 has the explanation on all the settings.
Also on YouTube you can view videos by Freedom Heat Pumps - https://www.youtube.com/c/SamsungEHSHeatpumps
They have a number on the Midea unit (that I have anyway) and they explain lots of things about its set up, fault codes etc.
Thank you all for your kind responses...I always have the goal to keep my writing short, but I doubt it...but maybe this essay will help someone in the future 🙂 But I will end this with basic YES or NO questions.
First @batalto thank you for joining the thread and the input you gave. On my unit I only have options from 3.1 to 3.7, they are all set and I know what they mean. The other options are not there or are configured somewhere else.
My unit is a M-Thermal Split (Indoor: SMK-160/CD30GN1-B Outdoor: MHA-V16W/D2N1) The wired controller looks like in the picture attached.
I have the manual and found where to enable preset temperatures for weather compensation, like the "weather temp set" option and the settings to enable and set the "climate related curves" (in heat mode there are 8 curves for LOW temp and 8 curves for HIGH temp). Currently the option to use the weather temp set for heat mode is OFF, and I adjust the water flow temperature (mainly it's on 40C) manually on the unit, and quite frankly will keep it that way for now, because I am always home and it's kind of confusing, so I will elaborate to see If I am reading it right 🙂
I can set the water flow manually up to 55C , T1S Range in FOR SERVICEMAN>HEAT MODE SETTINGS is set to LOW, so 55C is max (stated in the manual, while on HIGH = 60C is max). The tech guys set it to LOW because I don't use the heat pump for sanitary water and they said that most heat pumps anyway achieve up to 55C, and that there is no need for 60C or HIGH setting.
The manual points out when it's like this on LOW, and if I enable the weather temp set option for heat mode, I can select the curves from 1 to 8 for LOW temperature, it states in the graphic table that for the LOW temperature curve, 38C waterflow temp is the maximum for curve 1 at -20C outdoor temperature, for zero degrees outdoor temp, water flow would be 35. So this means when the unit works like this, and it's zero degrees outside, automatically the unit will get waterflow temperature only up to 35C if I select curve 1 (curves 2 to 8 of course have lower waterflow).
I doubt that 35C waterflow at 0C outdoor temperature will keep me warm when selecting the highest curve 1 🙂 So I am guessing I would have to change in FOR SERVICEMAN>HEAT MODE SETTINGS and set to HIGH, by doing this when I enable "weather temp set" I get the option to choose the climate related curves from 1 to 8 for HIGH temperature, and the graph in the manual shows that maximum water flow temperature than would be 55C for curve 1. I would go with curve 5 (picture attached of graph)
So questions:
1. Enabling weather temp set/weather compensation basically adjusts the water flow temperature for me, instead of me adjusting it manually from time to time
? (I know it's a YES, just to confirm)
2. If I would go with weather compensation and enable "weather temp set" and select my preferred curve, am I assuming the above right? That I first have to change in FOR SERVICEMAN>HEAT MODE SETTINGS and set to HIGH, and after doing this I can select a curve listed for HIGH temperature?
3. This question relates to my previous posts regarding ON/OFF intervals of the unit. Now that my room thermostat turns everything ON/OFF depending on given room temperature, should I be concerned if sometimes the unit turns OFF just after 10-15-20 minutes of work because it achieved room temperature and the RT sends a signal to turn it OFF, or vice versa it turns ON after 10-15-20 minutes of being OFF because room temperature drops. Sometimes I notice the unit starts and works for like 10-15 minutes and STOPS because my wife is making dinner and the room temperature rises half a degree duo to the oven, or we have guests who smoke and we open a window...the room temp drops and the RT starts the unit again after being OFF just for a couple of minutes. It's more a need to understand if these shorter ON/OFF cycles are bad for the unit, a friend told me not to concern myself with this...to just set my desired room temperature on the RT and let it be 🙂
4. A mix question involving Qs 2 and 3 🙂 If I enable weather temp set/compensation, this option has nothing to do with my room thermostat? Meaning, enabling weather compensation will only automatically dictate water flow temperature on the unit based on outside temperatures , and my room thermostat will act like it does now...like Derek M said, be the switch for turning ON/OFF the heat pump based on what room temperature i set on RT?
Attached:
- heat pump wired controller
- from manual regarding heat mode settings (LOW or HIGH)
- from manual regarding LOW/HIGH curves
I can't comment with any authority on the Midea ASHP or controller. However, it sounds like the answer to 4. is yes. That's how my ASHP was set up by the installers. It worked OK. However, it does result in the thermostat turning the ASHP off and on. Some opinion says that it will be more expensive to run this way. From what I have read, as long as the turning on and off is not consistently more than 3-4 time an hour, itwon't harm the unit. Is there a sensitivity setting on your room thermostat will stop it reacting to small variations in room temperature?
Hi Mirnes,
Were you able to download and access the manual sent by Batalto, and is the manual similar to your manual?
From what I can see in Batalto's manual, you can either select one of the weather compensation curves from the high temperature list shown, or it may be possible to create your own weather compensation curve which is a closer match to your requirements.
Obviously, the ambient air temperature rises above 20C in the Summer, but what is the coldest temperature in the Winter where you live?
@Kev M
ON/OFF cycles aren't more than 2-3 times per hour, so glad to hear that that even 3-4 times isn't harmful to the ASHP.
Posted by: @kev-m
As for this, my RT is a non programmable Salus RT-310RF, it only has the two DIP switches on the back, one for CHP (cycles per hour, 6CHP or 9CHP, it's on 6) and the other one is the TIP switch which is in deed in charge for the sensitivity/change of degrees in the room temperature (Span +/- 0.25C or +/- 0.5C), but it's already set +/- 0.5C temperature change. Setting it to Span +/- 0.25C would only result in more frequent on/off cycles.
Posted by: @derek-mWere you able to download and access the manual sent by Batalto, and is the manual similar to your manual?
Yes, I was able to DL it, went through it a bit...some things are the same like with most ASHP, but the manuals aren't that similar. In my manual, I also can only select just one of the 8 weather comp. curves, but first I think I have to select HIGH (because now T1S Range is set to LOW) in serviceman > heat mode settings to be able to choose one of eight curves for HIGH tempareture "weather temp set / climate related curves" option . It's my question 2, maybe Batalto could clarify about that?
Why Buffer Tanks & Low-Loss Headers Can Sabotage Your Heat Pump's Efficiency
5 days ago
British Gas Heat Pump Installation Complaint
4 months ago
Heating Turned Off but Radiators Still Warm
4 months ago
Samsung Heat pump with Yonos Pico circulating pump running all the time
4 months ago
Samsung 5kW R32 Monobloc Gen 6 ASHP
5 months ago
- 446 Online
By trebor12345 , 3 minutes ago
By L8Again , 5 minutes ago
By cathodeRay , 39 minutes ago
By Batpred , 1 hour ago
By cathodeRay , 1 hour ago
By AndrewJ , 2 hours ago
By benson , 3 hours ago
By Batpred , 7 hours ago
By GC61 , 9 hours ago
By JamesPa , 23 hours ago
By DavidB , 1 day ago
By Slartibartfast , 1 day ago
