New Samsung 12KW Heat Pump Help
Posted by: @bontwoodyThe seem to think that the situation is the same as the Vaillant one
FWIW, the Vaillant app gives the energy efficiency (=COP) as (total heat generated including heat pump energy used)/ energy used. See this screenshot. However, the numbers don't quite add up.
Posted by: @bontwoodyUsing the adjusted calculation for the Samsung alters its COP to 4.76. Much closer to mine.
@bontwoody I think the fact that your Samsung displays generated energy as less than OEM generated energy whereas mine is the reverse may just demonstrate the inaccuracy of how Samsung measures flow rate and delta T. It uses external temperature probes whereas the heat meter uses pockets and paired probes.
I monitored what Samsung was displaying as delta T and flow rate through ESPHome and it correlated well with its displayed heat output of around 4kW. After an hour of stable heat output, generated energy had increased by 4kWh. So I am pretty sure that generated energy includes electrical input energy and is different to the Vaillant. It is noteworthy that the latter calls it environmental yield.
@mike-h Im not sure I follow you Mike. I can see that external temperature probes may differ from internal, especially if there is a long pipe run.
My interest in the correct formula is academic really, but there seem to be people on both sides of the fence.(see @technogeek here https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/new-heat-pump-owner-questions)
I think the argument about whether its called environmental yield or something else might be a translation one from the Korean.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@mike-h Im not sure I follow you Mike. I can see that external temperature probes may differ from internal, especially if there is a long pipe run.
@bontwoody Sorry for the lack of explanation. I was taking my comment from Glyn Hudson's recent observation on the OEM forum - "I found the onboard Samsung flow and return temperature sensors are quite inaccurate, if you do a mass flow rate calculation to calculate heat delivered it could be significantly inaccurate because of the inaccurate onboard sensors. My Samsung is 20% out. Heat meters use matched pairs of temperature sensors in wet pockets, which have maximum 2% error."
I was concerned that users with poor COPs might be falsely reassured that all was OK if they added electricity usage to generation before dividing by usage. Of course, if the Samsung consistently underestimates generation, then the poor COP might be completely false and using the G+EU/EU formula might be closer to reality. But if it overestimates it as often as it underestimates it then using the correct formula might be more important. At the end of the day, if you are happy with your electricity consumption then that is what matters.
@mike-h Yes, totally agree about false reassurance Mike. I was thinking that an error would always be in the same direction but I guess that doesnt have to be the case.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 22 Forums
- 2,084 Topics
- 46 K Posts
- 28 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@cathoderay thanks I have just figured it out. You need...
By benson , 2 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 7 hours ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 18 hours ago
-
RE: Vaillant AroTherm Plus 7kW
@jamespa I have a hydronic baseboard heater in the kitc...
By Scalextrix , 24 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 1 day ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 2 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 2 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 3 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 4 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 5 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 5 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 5 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 5 days ago