New Samsung 12KW Heat Pump Help
Posted by: @bontwoodyThe seem to think that the situation is the same as the Vaillant one
FWIW, the Vaillant app gives the energy efficiency (=COP) as (total heat generated including heat pump energy used)/ energy used. See this screenshot. However, the numbers don't quite add up.
Posted by: @bontwoodyUsing the adjusted calculation for the Samsung alters its COP to 4.76. Much closer to mine.
@bontwoody I think the fact that your Samsung displays generated energy as less than OEM generated energy whereas mine is the reverse may just demonstrate the inaccuracy of how Samsung measures flow rate and delta T. It uses external temperature probes whereas the heat meter uses pockets and paired probes.
I monitored what Samsung was displaying as delta T and flow rate through ESPHome and it correlated well with its displayed heat output of around 4kW. After an hour of stable heat output, generated energy had increased by 4kWh. So I am pretty sure that generated energy includes electrical input energy and is different to the Vaillant. It is noteworthy that the latter calls it environmental yield.
@mike-h Im not sure I follow you Mike. I can see that external temperature probes may differ from internal, especially if there is a long pipe run.
My interest in the correct formula is academic really, but there seem to be people on both sides of the fence.(see @technogeek here https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/new-heat-pump-owner-questions)
I think the argument about whether its called environmental yield or something else might be a translation one from the Korean.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@mike-h Im not sure I follow you Mike. I can see that external temperature probes may differ from internal, especially if there is a long pipe run.
@bontwoody Sorry for the lack of explanation. I was taking my comment from Glyn Hudson's recent observation on the OEM forum - "I found the onboard Samsung flow and return temperature sensors are quite inaccurate, if you do a mass flow rate calculation to calculate heat delivered it could be significantly inaccurate because of the inaccurate onboard sensors. My Samsung is 20% out. Heat meters use matched pairs of temperature sensors in wet pockets, which have maximum 2% error."
I was concerned that users with poor COPs might be falsely reassured that all was OK if they added electricity usage to generation before dividing by usage. Of course, if the Samsung consistently underestimates generation, then the poor COP might be completely false and using the G+EU/EU formula might be closer to reality. But if it overestimates it as often as it underestimates it then using the correct formula might be more important. At the end of the day, if you are happy with your electricity consumption then that is what matters.
@mike-h Yes, totally agree about false reassurance Mike. I was thinking that an error would always be in the same direction but I guess that doesnt have to be the case.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 248 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Advice on internal circulation pump noise
Welcome and I am sorry you are having this problem. &...
By JamesPa , 5 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@harrisonc mine has level 3 MID monitoring and you can ...
By swwils , 7 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@alastair, in short, no, increasing emitter capacity wo...
By Mars , 8 hours ago
-
RE: Setback savings - fact or fiction?
Hi @cathoderay - this is a good discussion! I feel like...
By RobS , 8 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona happy to help as much as I can if you decide t...
By bontwoody , 9 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
I'll be honest, I love that idea! I'll start working on...
By Mars , 9 hours ago
-
RE: Configuring third party dongle for Ecodan local control
@majordennisbloodnok I think the HPDHD diagnosis may be...
By Sheriff Fatman , 10 hours ago
-
RE: External pipework insulation
I don't think we can tell from a photo whether your exi...
By Transparent , 11 hours ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
@majordennisbloodnok That’s correct. I can’t find anywh...
By weoleyric , 17 hours ago
-
RE: A Smarter Smart Controller from Homely?
@papahuhu I hope you get a swift resolution. Regards, T...
By Toodles , 2 days ago
-
RE: Poll for Time of Use, tariffs, technology
That’s fine by me too Major, I feel it is a sad reflect...
By Toodles , 2 days ago
-
Bingo. Sometimes a judiciously placed size 10 bovver bo...
By Majordennisbloodnok , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW heat pump with low COP
@ciocoiu-alexandru I can't provide the same level of di...
By Sheriff Fatman , 2 days ago
-
The three technical issues I'm considering are: BMS...
By Transparent , 2 days ago
-
RE: LiFePO4 lithium battery fires and explosions
@transparent Your post may fit better in th...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@jamespawhite, if you could be bothered, you could also...
By Mars , 2 days ago
-
RE: Commencing on an ASHP Installation Process
I've got a bit of time to draft something today, so the...
By Sheriff Fatman , 2 days ago
-
RE: Help with heat pump sizing
@amin I dont think materially relative to t...
By JamesPa , 3 days ago