Commencing on an ASHP Installation Process
Hi All
I've posted a general intro post in the introduction section, but the main reason for joining the forum was due to our commencing an ASHP quotation process, for which I can hopefully gain some insight from other forum members.
Our combi gas boiler is still working, but on its way out, so a ASHP seems a logical decision alongside our existing solar PV and battery system. To date, I've done several standard online quotes, all of which are landing in pretty much the same place (£6.5k-$7.5k, after the BUS grant). There's been one exception to this, which was Boxt quoting a fixed price of £4,599 after the grant, but with a downside that you have to pay the full amount upfront prior to any sort of survey taking place, which I'm very wary of.
Our property didn't have a current EPC, so we've paid Octopus (our existing energy supplier) the refundable £200 deposit for a combined EPC and heat pump survey, which was carried out last week. It was very detailed, taking 4 hours to complete, and we now have an updated quote from them for an 11kW Daikin heat pump with 9 radiator changes out of 13 in the house. The main complication from the survey was the conservatory at the back of the house which accounts for 1/3 of the total heat loss in the property. However, there are two large radiators in there which the calculations showed recovered 97% of this, meaning that the installation fell within scope for Octopus.
From an installation perspective, the surveyor seemed to think it was a fairly straightforward installation to carry out, as there are no planning permission or structural survey issues, and the heat pump can be situated on a gable wall, with pipework going straight up into the loft and across to an existing airing cupboard where the old water tank used to be situation prior to the combi boiler being installed in 2014. Consequently, I now have a much better base level of information to work from to be able to compare alternatives.
So far, I have arranged for an on-site visit from Aira this Friday (90 minutes, so less detailed than the Octopus survey). I've watched a few videos regarding them but, having read the thread on them on this site today I'm not sure I want the 'install and forget' kind of system that they provide, as I'd like to be able to tinker around with settings to optimise how the system works, but I'll see what they come up with.
I've read a couple of posts on here from people who've used Boxt, and will read up further on them. There's very little available on YouTube in the way of customer testimonies. If I can get myself comfortable that they're going to spec a reliable system and do a professional installation then their pricing is difficult to ignore, particularly as it's based on a Vaillant heat pump which seems to be well regarded generally, and is probably one I'd prefer to have than a Daikin unit. Their quote covers up to 6 radiator changes, so if 9 were required this would add £360 to the cost, based on email correspondence I've had with them. The big question mark currently is that the standard online quote has specced a 7kW heat pump, which I'm now concerned will be undersized based on the findings of the Octopus survey (which ruled out their own Cosy units as an option as there isn't one big enough currently). I'd love to get them to complete a survey to confirm their findings and pricing, but am holding off on this currently due to the capital outlay required (which I've been assured is refundable, less a £150 survey deduction, if I didn't go ahead).
I've had other standard quotes from E.ON and EDF, both of which I think are also speccing Vaillant systems, but at a higher cost than BOXT. I've not done anything to progress these further at this stage, but the pricing of both is very similar to Octopus.
We have a bit of time available before having to make a decision, as our eldest daughter is about to start her GCSE's, so I wouldn't want to commence a disruptive installation process while she's doing these, which means that the end of June is the earliest installation we'd be looking at.
If anyone has any particular insight they'd like to share, then I'd be grateful, particularly with regard to their experiences using BOXT, and also if anyone has any recommendations for other potential installers around the Leeds area that might also be worth considering within the process. We used a smaller, local installer for our PV and Battery installation and they've been fantastic both at setup, and in their aftersales service, where a couple of optimisers have had to be replaced under warranty. Consequently, even though the quotations to date have all been from 'big names' with the exception of Aira, I'm not averse to using an independent company based on word of mouth recommendation, provided that they are suitably certified. To date, it's been harder to identify any via the usual search processes, other than via using one of the advertised 'search sites' such as Greenmatch, who's TrustPilot profile seems to have many people complaining about spam calls after using them.
My intention is to keep updating the thready throughout our ASHP journey, and to hopefully record a successful transition from gas to ASHP. I'm comfortable at this stage that the switch is the right one for us to make at this point in time, and I'm happy that we've made a sensible decision in paying for the Octopus survey as a reasonably priced method (with the option of a full refund) to get the level of insight beyond a standard online quote. The decision process from here is less obvious and, having discovered this forum, I've already gained a lot of additional insight from the posts and YouTube video content to make me think it will be a valuable point of resource.
Hi
I have just posted the below in response to your intro text.
-------------
In terms of getting quotes, be prepared to get a fair few to find a good installer who will do what you want and do ask lots of questions once you narrow it down. Key things to bear in mind are:
- System design matters more than choice of ASHP, but some ASHPs have more user friendly/flexible controls
- Don't accept any quotation with a buffer, low loss header or plate heat exchanger between ASHP and emitters (and do ask if its not clear from the quote). A 2 port volumiser is OK.
- If you have gas meter readings DO sense check the surveyed house loss against your gas consumption. Surveys can be wildly out and sizing does matter, gas meter readings can help avoid potentially expensive mistakes
- DO design for the lowest reasonable flow temperature. As a general guide 45C or less for radiators, 35C or less for UFH, unless space constraints mean that these are impractical
- Don't seek/allow the installation of third party add on controllers, room thermostats or smart devices like Hive etc. Heat pumps should generally be run 24*7 controlled by their native controller, all or most TRVs and thermostats set a couple of degrees above the desired temperature so they are acting as limiters not controllers. The exceptions to the advice against third party controller hardware are those designed specifically for heat pumps namely Homely or Adia. There is also Havenwise who do remote third party control again specifically for heat pumps.
Of course there are always some exceptions to the above, but they are rare and, if they apply to your case, there will be an identifiable reason which you may wish to test here.
-------------
My first observation is that 11kW is big and I note that 7kW is also quoted. Its important not to oversize (its also important not to undersize), you want to get as good a handle on this if you can and surveys can be a case of GIGO. As an extreme example I had two 3 hour surveys, both of which came out with 16kW, whereas my actual measured loss is 7kW! By way of getting a handle whats your floor area and house construction. Do you have smart meter readings, or indeed any information on gas consumption? 11kW Daikin is actually a larger one (14-16kW) downrated so not an ideal choice if your loss is in fact 11kW
I dont know anything about BOXT, others might, do check the questions above. If they want to put in any 4 port device between emitters and ASHP then look elsewhere, if they don't then as you say worth considering. The thing about heat pumps is that simple is best! You can find some reviews of some makes of heat pump (including Vaillant - written by me) here.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks for the replies to both forum posts.
I'm due to speak to the Octopus sales team tomorrow, so will ask for more info about the heat loss calculations, as I've only had the updated quote email from them which didn't provide huge detail. From what the surveyor was saying during the installation, I think the calculated heat loss was approaching 10kW so we're kind of in the gap between the two heat pump solutions they offer. Cosy (which I don't like the appearance of so am happy to avoid) is currently available in 6kW and 9kW sizes, and the Daikin is the bigger option. Interesting to read that it's a downsized bigger unit, as I believe that impacts the ability to which it can ramp down in warmer temperatures, making it less efficient.
The house is a 4-bed detached property, built in 1980, with 116m2 of floorspace. We've got cavity wall insulation which we believe is also in the conservatory too, but can't easily evidence this. I think I did enough to persuade the surveyor to reflect this in the EPC assessment. The ground floor is solid tile construction. One of the pre-reqs for an Octopus installation will be to remove the (unused, but still working) gas fire in the living room and cap the chimney (as they would then cap off and remove the gas meter as part of the installation process). I'd look to do the same, regardless of choice of installer as this is an obvious heat loss exposure area within the property.
Our gas supply is still on a dumb meter, but I'll be able to get consumption data going back for at least a couple of years, so I can do a bit of digging on that.
I suppose my main doubts about BOXT are that they are primarily gas boiler installers, albeit one of the bigger names doing this (they sponsor Leeds United, but I won't let that cloud my judgement!) Finding information on their heat pump installations is difficult as the searches primarily throw up gas boiler testimonies. It's the reason that I haven't sought a quote from British Gas at this stage. On the plus side, they offer the full 7 year Vaillant warranty, which I believe requires that their installers have done additional training with Vaillant. From what I can see, there's no obvious indication that they're including a buffer in their quote too, which appears to be a positive sign based on reading various posts on here. The full payment up front is an annoyance, but not necessarily a deal-breaker with them and the difference in price quoted by them will mean they'll remain under serious consideration, but will probably be the final option I use in terms of committing to a survey while I collate comparative data from other companies. It feels like using them will be something of a leap of faith, so I'll spend more time doing due diligence on them.
@sheriff-fatman, given you're based in Yorkshire, I have three excellent installers I can recommend that are not in the mass volume game. Let me know if you'd like me to connect you with them.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@sheriff-fatman, given you're based in Yorkshire, I have three excellent installers I can recommend that are not in the mass volume game. Let me know if you'd like me to connect you with them.
Thanks. I'd be happy with this as a way to explore further options.
Posted by: @sheriff-fatmanThe house is a 4-bed detached property, built in 1980, with 116m2 of floorspace.
Is 116 sqm both floors, or just the footprint? If the former then 11kW sounds possibly a bit high to me. Your conservatory may be dominating however and older double glazing isn't necessarily too good. I replaced the glass in mine (but not the frames) with low e argon filled, it made a noticeable difference!
For comparison my house is 200sq m (sum of both floors) 1930s build. Originally solid 9" wall; most but not all walls now upgraded with internal wall insulation. Double glazing and 300mm loft insulation. Uninsulated floors (either concrete or suspended) throughout. 7kW verified by measurement both of the gas and the ASHP.
There is a tendency for surveys to overestimate ventilation loss. 2-3ACH per hour is typically assumed for older houses but there is at least some evidence that 0.5-1ACH is more likely unless there are obvious draughts. Also some surveyors will ignore any fabric upgrades that they cant see. There is room for debate how much oversizing matters and it quite possibly varies from manufacturer to manufacturer (or even model to model). There are good reasons why it might matter but smart control algorithms can go some way to addressing this, hence the possibility it varies from manufacturer to manufacturer. There is some, extremely limited, evidence (no more than a suggestion really) that both Daikin (M series) and Vaillant deal well with oversizing, albeit by very different control means. This doesn't mean that others don't.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa The 116m2 is the total floor area as per the EPC, so I assume its the total usable area. It will be interesting to see what the other surveys come up with in terms of their own calculations.
I also should have mentioned previously that we have 15mm pipework throughout, so no complications arising from microbore, which was another reason why the surveyor viewed it as a fairly simple installation, from a technical perspective.
The conservatory was obviously a challenge for him to consider. I think it has a heat loss of close 3-4kW in isolation. Within a couple of minutes of entering the property he said that it might have to be excluded from heating to meet their criteria, but the subsequent calculations and assessment of the radiators meant this wasn't necessary, although I think he's planning to add a 3rd radiator in there due to the lower temperature flow with a heat pump. Ironically, it's a room that we spend more time of the year trying to keep cool rather than warm, but he's done the assessment based on it being a regularly habitable room, which is the appropriate usage for it.
Whether or not this is a factor in the sizing of the heat pump, I'm not sure. It was potentially more of a factor into whether or not the job would fit within Octopus' installation criteria or was a job that they ultimately turned down after doing the survey. I guess we passed that test, but perhaps were somewhere close to the cusp in that regard.
Posted by: @sheriff-fatmanThe 116m2 is the total floor area as per the EPC, so I assume its the total usable area. It will be interesting to see what the other surveys come up with in terms of their own calculations.
11kW does sound way over in that case! As you say it will be interesting to see what others come up with, maybe try to get a copy of the calculations and dig out your gas consumption. You would be well advised if possible to avoid getting a 10-12kW model if a 7kW one will do.
Posted by: @sheriff-fatmanThe conservatory was obviously a challenge for him to consider. I think it has a heat loss of close 3-4kW in isolation.
I can see why he is thinking of fitting another radiator! Finding a radiator even to do 1.5kW at say 45C is a challenge!
Posted by: @sheriff-fatmanIronically, it's a room that we spend more time of the year trying to keep cool rather than warm
Bear in mind that most heat pumps can cool as well as heat, but for cooling you need fan radiators or underfloor heating at least in the rooms you want to cool. It adds another level of complexity to the purchase decision and strictly speaking requires planning consent. That said the only feasible enforcement action, so far as I can see, is to tell you not to use it for cooling!.
Some heat pumps, including Daikin and Vaillant have cooling disabled. In the case of Vaillant you can buy a 'coding plug' (AKA a 4K resistor) for either £500 (with the correct part number) or £5 (same part, different part number) which enables it, I don't know about Daikin. Lots more to consider if you go down this route, the likes of Octopus wont support it and converting it probably invalidates the guarantee.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I've done some calculations based on our gas usage, for which I have 'dumb meter' data within Octopus going back to October 2022, when we switched to them. Applying the m3 conversion on the latest bill, the total Gas kWh usage in 2023 was 14,100kWh, split roughly as 11,100 heating, 3,000 hot water. In 2024 the figure is higher, being 17,800kWh in total, with a higher hot water estimate of 4,500kWh, which feels a bit on the high side (I've assumed that the quarter from 1st July to 1st October is all hot water, with no heating being used in those months, which is an over-simplification). The increased usage might be a factor of both a colder overall year in 2024 (solar generation was well down compared to 2023) and the gas boiler inefficiencies that are prompting the decision to replace it.
By comparison, the EPC carried out last week estimates 11,200kWh and 2,300kWh respectively, so is quite close to the 2023 usage.
Not sure how this equates overall to an estimate of heat pump size. A google search suggested dividing the total usage by 2900, which gives an answer of 5-6kW, depending on which figures are used, but I'm not sure how good a calculation this is. If anything like, then it suggests the 7kW Vaillant unit auto-quoted by BOXT might actually do the job, albeit this is without the benefit of any survey done by them.
Crudely dividing by somewhere between 2000 and 2900 gives an estimate dependant on assumptions/who you believe. My total gas consumption for a 7kW house was 18-20MWh/yr.
For my money, assuming you heat the house to a sensible temperature most of the time, this puts to bed 10-12kW and puts it firmly in the 5-7kW bracket. Even that's quite a lot for 110sqm but the conservatory sounds like it may be close to uninsulated.
It would be good if you could rationalise this back to the fabric calculations, I found I could by assuming ACH = 0.5. More than one installer has said publicly that 0.5-1 is more realistic than 2-3 typically assumed by MCS.
Please note I'm just a homeowner with a physics/engineering background who has spent two years studying this stuff for 'fun'/to inform their own installation. I am not an expert, so you will need to form your own judgement (that's the disclaimer!).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPlease note I'm just a homeowner with a physics/engineering background who has spent two years studying this stuff for 'fun'/to inform their own installation. I am not an expert, so you will need to form your own judgement (that's the disclaimer!).
I did wonder where all the detailed knowledge came from, and had assumed you were involved in installation in some form or another. Caveat duly noted!!
Posted by: @sheriff-fatmanPosted by: @jamespaPlease note I'm just a homeowner with a physics/engineering background who has spent two years studying this stuff for 'fun'/to inform their own installation. I am not an expert, so you will need to form your own judgement (that's the disclaimer!).
I did wonder where all the detailed knowledge came from, and had assumed you were involved in installation in some form or another. Caveat duly noted!!
Lots of reading and questioning which the background makes easier. I started when I first thought about getting a heat pump for myself and it became a bit of an obsession.
For me the process of getting a heat pump took two years, due largely to planning issues (long story), giving me plenty of time to understand the technical side. I like to think this is, at least in part, why my installation was straightforward and gave good performance from day 1.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 16 Online
- 3,312 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@damon thank you for posting. Would you care to tell ...
By JamesPa , 5 hours ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 7 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Well my switch from eon is tomorrow/Monday so I’ll soon...
By Westkent , 11 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 15 hours ago
-
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@johnmo I have been looking at the daily Agile rates fo...
By Toodles , 18 hours ago
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 19 hours ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 1 day ago
-
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 3 days ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 3 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 4 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 4 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 4 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 4 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 5 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 5 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 5 days ago