New Daikin 11kW Altherma 3M install - is it working as it should?

3 Posts
2 Users
0 Reactions
41 Views
(@synthbuilder)
New Member Member
Joined: 4 weeks ago
Posts: 1
Topic starter  
I had the system installed by Octopus in October last year and the recent cold snap here in the UK has made me slightly regret the move to a heat pump from an oil boiler. My house is a standard sized three bed detached bungalow built in 1974 in a relatively exposed position 650ft above sea level in Cumbria, UK. It had cavity wall insulation added about 15 years ago, and roof insulation is to current specifications. Octopus calculated the heat loss to be around 10kW at -3.7C.
 
The system is based around a Daikin Altherma 3M 11kW with 180l Daikin water cylinder. There were five radiator changes made within the house.
 
COP for space heating only: October (3.74), November (2.77), December (3.12), January (2.09).
COP for DHW only: October (1.84), November (1.58), December (1.83), January (1.31).
COP overall: October (3.44), November (2.65), December (3.01), January (2.04).
 
The January figures were taken up to the 10th January 2026. 
 
My two point heat curve is now set at 50C at -8C, 30C at 15C. I altered the curve in November to lower the LWT as the pump was switching on and off a lot which may account for the slight better COP in December. Early in January I discovered that the back up heater was kicking in at 0C and I have since changed the equilibrium temperature to -7C. I have also switched off the 'increase under 0C' mode which was also on by default.
 
My heating schedule was 24/7 at 21C with set back to 19C at night. However, during the recent cold weather (just below freezing) it was costing me in excess of 20GBP per day. I have since made the set back temperature much lower to effectively turn the pump off at night and during the Octopus Cosy tariff's 4pm to 7pm peak. This has kept the daily cost to around 15GBP per day.
 
I have a 14 panel solar system with 6.2kWh battery. I am charging the battery twice a day during Cosy's two 3 hour cheap periods.

This topic was modified 5 hours ago by Synthbuilder

   
Quote
Toodles
(@toodles)
Illustrious Member Contributor
Joined: 3 years ago
Posts: 2431
 

Perhaps you obtain a higher solar yield than we do with our 8.1 kWp array (21 panels in 4 separate locations on 3 roofs and in back garden but neither optimally orientated nor free of some shading) but at present, our best yield for a day in January has been 6 kWh.

Now as to the Daikin heat pump, we have an 8 kW Daikin EDLA08 monobloc without an internal heater and the system is controlled by a Homely smart controller - thus direct comparison is meaningless - nevertheless, for what it is worth, here are a few details.

December COP was 3.6 and so far January has been 2.6; we are enjoying a 24/7 comfort level of 22.5 deg. C throughout the 4 bedroomed semi detached 1930’s house with cavity wall insulation. under-floor Q-Bot insulation on ground floor (though not under the kitchen as this is solid floor) loft insulation is 300 mm. plus some boarding with old fibre glass insulation of ~ 100 mm. There are also Celotex type panels next to the roofing felt.

We are on OE’s Cosy, use 27 kWh’s of Powerwall storage and only use grid power during the 8 cheapest hours to recharge the battery. Our DHW is separate due to not having space for the MCS requirement of a mega size tank for 4 bedrooms! (We use a Sunamp Thermino for this job which can be grid or solar charged.)

Our total electricity charge for December (we do not have gas at all) was £161.82 including all those added charges to subsidise gas etc. (1,013.96 kWh.) The solar energy exported provided 32pence.! The rest of the 101.4 kWh we produced was used rather than being exported.

You have been going through some of the most expensive part of the year for heating as the minus temperatures really do ratchet up consumption on heat pumps - come March, the consumption should be much lower but I think I would be asking why the internal heater is set to come on so soon as this will be running at a COP of 1 and not helping your savings at all!

If there is anything else you wish to ask about, just say please. Regards, Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
ReplyQuote
Toodles
(@toodles)
Illustrious Member Contributor
Joined: 3 years ago
Posts: 2431
 

I forgot to mention: Octopus measured our heat loss at 6.5 kWh though I don’t have any written details of the other parameters as this was just what the engineers told me at the time of survey and we didn’t have them carry out the installation in the end (very long story there!).

We live in the SE of England, on the side of a hill at 60 metres ASL. with the prevailing westerly wind hitting us square on. The house is 97 sq. metres according to the EPC we had carried out for Octopus (C 72), we have since replaced the aging double glazing throughout with triple glazing and other factors including solar, battery and heat pump hadn’t taken place at time of the assessment. Regards, Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   