New Build - Grant Aerona3 10kW - Questions and observations
@ggw I think you've nailed the issue. Very odd.
I think you may have a faulty outdoor temperature sensor probe, if the unit is under warranty this will be covered by Grant. You've enough evidence based on your own monitoring to ask them to come out and replace it. Fault when running only may be vibration caused, so it might be OK when the unit is not running, but goes doo-lally when it is. Just because it's not open circuit doesn't mean it's not faulty, a poor connection onto the PCB or in the thermistor unit itself could mean vibration causes incorrect readings.
I have the exact same 10kW Aerona and the outdoor air sensor is pretty accurate. It can be slightly affected by heat from the coil when it defrosts during which time the fan stops for a while, other than that it's been within 1degC or so of where it should be. As the outdoor temperature goes above 17degC the unit starts to cycle on and off for long periods, as the heat load for a typical 21degC set point falls below the unit minimum unit turn down of about 25%. Above 20degC outdoor air temperature heating is disabled regardless of the indoor thermostat setting or demand.
In addition to the suggestions by AllyFish, another reason could be electrical pickup from a nearby power cable, that is only live when the heat pump is running. Whenever possible, all cables should be kept separated from each other, and in particular that would apply to power and signal cables.
Do you know what flow in l/m your unit is showing? @allyfish
How do i check this? is it a parameter on controller? i've not seen it in manual. Tho, with the bewildering amount of parameters, that wouldn't be a surprise.
Posted by: @ggw
Both Good shouts - ill make sure to tell Grant that if they ever commit to coming to look/fix. Noise affecting resistance would be a new one for myself. never considered vibration either.
BT is sometimes right, It's good to talk...
It is possibly electrical interference on the cable rather than affecting the thermistor. The controller will be measuring the OAT by passing an electrical current down one core of the cable, through the thermistor, and back to the controller via a second core. An electrical interference entering the controller could affect its reading.
I presume that you have measured the air temperature, near the sensor, with the heat pump operating, to be certain it is not a true reading?
@ggw This is a requirement of the Grant pump - Section 9.13 of the Installation Manual: "A flow regulator is supplied with the heat pump. This must be fitted in the return pipe to the heat pump."
If it's not present then speak to the installer/builder.
There's no parameter on the Grant controller which shows the flow, so looking at that is the only way to find out (outside of adding your own flow meter).
Grant Aerona 3 10kW
SITREP #2
Learning experience - that's what his first winter has been... The future, maybe - the present... If willing
Temperature Sensor issue is still unresolved - Grant have talked a good game on phone - still no one is yet to turn up to fix (1 month) - they offered to post a replacement sensor - I declined, worried that if I install and something fails, bad job for the warranty. So they grudging said they would organise someone.. still waiting
Fixed temperature has worked well above freezing. 33Deg LWT is lovely and warm, even when 4Deg OT.
Our recent 0Deg weather has stressed the 10kW unit, cannot get to 33Deg, best I've seen it is 29Deg - then defrost - then 29deg - rinse and repeat. Double the electrical cost for less heat - oh the joys. Found reducing the zones down (heat only living room and bedrooms) has been effective in both getting heat into the property and slowing the defrost rate to closer to 60mins. That is my decision, and other parts of the house are *much* cooler.
Another issue - DHW
I have 3rd party controls on my S-Plan PDHW setup. For CH, works great. For DHW, the timings to get to 50Deg vary depending on the outside temp. Normal so far...
If I set the DHW time to 90min run, the unit will heat up to 50Deg - stop - but is keeping the pump running. So taking heat away from the Tank. I've had several days with no HW. I understand how this is happening, but how to correct? I need the pump to stop when it reaches set point. ? If using the 3 way valve, it will changeover to CH but as I am 3rd party setup, the unit doesn't talk to valves.
Need to get the engineering hat on - might try and Jerry rig the connections for the 3 way valve on the unit to provide an interlock
Thoughts welcome..
- 26 Forums
- 2,283 Topics
- 51.1 K Posts
- 228 Online
- 5,944 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
I've been following this thread since it began, and it'...
By MikeFl , 2 minutes ago
-
RE: Maximising Home Automation: Integrating Octopus Energy & More
Ah, this is a bit of a mess. The interface from the sm...
By JamesPa , 8 minutes ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
That's an interesting use of the phrase 'site-specific ...
By Transparent , 19 minutes ago
-
RE: Faulty Clivet heat pump out of the box
@steveimpey as a short term "fix" have you tried turnin...
By Sune , 50 minutes ago
-
I was thinking something similar to the OP half way thr...
By RadWhisperer , 56 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@technogeek Couldn’t agree more! Years back, we were wi...
By Toodles , 1 hour ago
-
RE: Help me keep the faith with my air source heat pump installation
The double panel radiators I’ve seen have a bleed screw...
By AgentGeorge , 2 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@nickhorne Unfortunately not. We take the "normal" IOG ...
By HCas , 13 hours ago
-
RE: Mixture of copper and plastic CH pipework. Will it be ok, or need changing?
In principle yes. Some heat pumps (I think including D...
By JamesPa , 14 hours ago
-
RE: New Fogstar 15.5kWh upright solution
For the common benefit, a quick update on this. Fogs...
By Batpred , 14 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Some of the circuits in my home are not protected by RC...
By Batpred , 14 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Aqara sells some inexpensive hubs (usb dongle size) tha...
By Batpred , 16 hours ago
-
RE: Extend the colder range of the weather compensation curve?
@thebinman In answer to this and personal...
By TechnoGeek , 16 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard That's probably fine, provided as you say...
By GrahamF , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
16Kw AIROSD Manufacturer: Foshan Model: QBKFXFC-...
By Polar bear , 1 day ago
-
Just a suggestion but upload your images to an AI agent...
By RadWhisperer , 1 day ago
-
RE: Daikin Wireless Thermostat
The switch from WDC to LWT i.e. pure WC is fairly strai...
By RadWhisperer , 1 day ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Thank you for your continuous research, and posts. As y...
By ectoplasmosis , 1 day ago
-
RE: Trying to understand my Nibe F1245
@barry-sharp, is this something you could help with?
By Mars , 1 day ago