My Mitsubishi ASHP has used 1078kWh from 25 November to 31 December – Help please
Posted by: @harriupAt the bottom of page 6 it states the water flow rate range is 10.0 to 24.8 l/m. Similar to mine, though I have also seen the tank installation manual be a bit more specific that the flow rate should be 24l/m. Not sure what to make of that difference. There is discussion in other threads about altering the flow rate to manage the difference between flow and return temperatures to 5°C, but if the manifold temps of 28 and 21 are typical then you have a slightly too large difference, which is to be expected if the flow rate is lower than it is meant to be.
Hi @Harriup
i thought I ought to add some comments on this for Sarah to consider.
Theres a good reason why there is a flow rate range quoted, and probably other reasons too.
It was generally believed in an earlier thread (Keystone COP) that Ecodan does not have an internal pump to regulate deltaT so there are 2 things that can control it. 1. Adjusting the flow rate via the circulation pump of the primary flow and primary return and 2. The internal modulating electronics which cannot regulate the circulating pump. In other words the ecodan operates at a constant flow rate depending on the chosen set pump speed.
A flow rate must therefore be measured on the return primary pipe since that is precisely en-route back to the heat pump and will give a near accurate measurement of flow through the heat exchanger. (I would say it’s essential to check this before any adjustment of flow rate)
another thing to point out is that a 28 to 21 differential is only 7c which is quite common when the hp is still settling down. I’ve noticed it fluctuates all the time between 3c and 8c and when it starts up it can be more.
So a flow rate of 13LPM is within the acceptable band of the ecodan 8.5 provided it is being measured in the correct place in the circuit. But if the temperature difference never settles close to 5c then a slightly faster pump speed will lower the temperature difference. However there are other issues such as balancing flow rates between the primary loop and other heating circuits so this kind of adjustment really needs to be done by a professional.
Hope this helps
@sunandair hi - yes that does help and again makes sense that it's set by the gauge on the pump itself - i.e. that is the maximum it will flow. I've had a manic week this week - but I need to look at the manifold on a regular basis for the living area to see what the return is. The thermostat is set to 18 for the living area - but rarely gets to that, unless there is solar gain - for the past two days it is still 17 degrees at 18:00 - when it was 16 degrees at 09:00. In all honesty this could be what I have to live with and it doesn't feel cold. The other 2 zones always get up to their set temp - although their set temps are 16 (bathroom area) and 17(bedroom area). Everything generally is SO MUCH BETTER since I first found this forum 🙂
- 26 Forums
- 2,118 Topics
- 46.6 K Posts
- 32 Online
- 4,523 Members
Join Us!
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
So in summary it was a decision between pragmatism and ...
By JamesPa , 49 minutes ago
-
RE: Double or Triple Glazed Windows?
As I have reported elsewhere, we replaced all our glass...
By downfield , 4 hours ago
-
How to waste energy (and time) playing with AI.
A friend of mine who subscribes to an AI service was ex...
By Toodles , 5 hours ago
-
FRV valves - can you mix and match
Great video again this week @editor, I am very interest...
By Grantmethestrength , 6 hours ago
-
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@topher you’re more than welcome to, yes. I’ll send you...
By Mars , 1 day ago
-
RE: Fitting new shower valve ..........
I’ve never taken a chance when fiddling and changing ou...
By Mars , 1 day ago
-
You should contact the council and report the unsatisfa...
By JamesPa , 1 day ago
-
RE: Benefits of an extra horizontal loop for GSHP
I would deffo install an additional slinky run, especia...
By Transparent , 2 days ago
-
RE: Say hello and introduce yourself
@editor fab - thanks Mars, and keep up the great work o...
By normpang , 2 days ago
-
RE: Compressor and Evaporator Stratification
@trebor12345 So I think the 1st zigzag section shows so...
By ASHP-BOBBA , 2 days ago
-
RE: Is this just haze or something more?
@majordennisbloodnok I was giving a talk to primary sch...
By Toodles , 2 days ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
We had our Tesla Powerwall 3 (and Gateway) installed ea...
By Old_Scientist , 2 days ago
-
Indeed. With a battery its presumably the battery con...
By JamesPa , 3 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
To update an ESP device using ESPHome in Home Assistant...
By Grantmethestrength , 3 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 6 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 6 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 7 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 1 week ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 1 week ago