Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

My horrific Samsung heat pump installation and experience

946 Posts
28 Users
125 Reactions
412.9 K Views
(@iantelescope)
Reputable Member Contributor
Joined: 4 years ago
Posts: 418
Topic starter  

@derek-m 

Hi Derek,

1: The Sharky is installed across the beginning of the Radiator circuit , the purpose being to  measure the losses by comparing the Power , Energy output from the Samsung with the Power , Energy at the start of the Radiator circuit.

2: Yes, the DT across the primary of the Heat Exchanger ,PHE is approximately 2C to 3C and the flow rate in the region of 16 to 17 lpm.

3: The term Flow Water Difference Temperature is the difference between the Flow and return Temperature sensors on the Sharky , i.e on the Radiator pipe circuit..

4:  I was advised , by the French Samsung Engineer that the energy losses were caused by the "excessive flow rate in the primary of the Heat Exchanger" . His "solution" was to reduce , or control, the flow rate in the primary ports of the Heat Exchanger. 

5: The "Short Cycling " has been apparent from the start of the "installation" with my "installer" spending days trying, unsuccessfully , in reducing  the, then  ( August 2022), 8 minute period Short cycling.

6: I was advised " that if I reduced the flow rate in the primary ports of the Heat Exchanger that the Delta_T would increase.

7: I used the unused Pulse Width Modulation , PWM motor ports to limit the flow rate in both the primary and secondary circuits.

8: I have reduced the primary ports of Heat Exchanger to flow  rate of 16 lpm.

9: Being very sceptical about my own, or the "experts" advice, I test the results both with and without flow rate reducing in the primary .

10: The Delta_T across the primary Heat Exchanger does slightly increase but at the cost of increased instability.

11: As usual I have followed the advice of the "experts" at Samsung, Samsung-Dallium , Samsung-France ,the NIC , my "installer"  with increasing scepticism.

12: My , probably mistaken, understanding of my flow rate problem

The thermal power in a hot water pipe is given by :

            Thermal Power ,kW  =  Specific_Heat_of_Water X Flow Rate X Delta_T Across the primary ports of the Heat Exchanger

 Given that the  power is fixed, controlled by the Samsung inverter :

             Flow_Rate X Delta_T = constant

 As the French Samsung engineer pointed out 

             a decreased flow rate will increase Delta_T.

13: I have reduced my flow rate using the Motor Pulse Width Modulation ports set to the 50% to 70% values given in the Samsung manual for the Pulse Width Rate Control.

Please , Derek, don't be offended by my obvious inexperience.

I have, with increased scepticism , tried to follow the advice of the "experts".



   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 6 years ago
Posts: 4425
 

@iantelescope

Could you please provide the model number of your heat pump so that I can ensure I have the correct manual. Also the make and model of the PHE if possible.

Do you know the concentration of anti-freeze in the primary circuit?



   
ReplyQuote
(@iantelescope)
Reputable Member Contributor
Joined: 4 years ago
Posts: 418
Topic starter  

@derek-m 

Hi Derek,

Please find all the serial number , Field parameters et al in the attached Samsung-Controls.pdf ......

The options I have selected, and used ,  are shown with an asterisk.

I have tested most of the Field settings in my pursuit of a solution avoiding moving the Buffer tank to the other side of the motor, with the attendant risk of further increasing the losses and decreasing the effective REAL-COP.

 

The user manual is given by:

Air to Water Heat Pump

User manual

Control kit MIM-E03CN / MIM-E03EN

Warning! , the manual was probably, originally  , written in Korean being translated "automatically" by a computer.

A newer version was produced where the changes to the flow rate PWM are better discussed:

Samsung PWM Installation 1
PWM theory 2

Notes

1) The water motors  may be controlled in either of two options , case 1 & case 2:

       a)  Case 1 Using On-OFF motor switching. this was the method used by the French Samsung Engineer.

       b) Case 2 , Using a continuous Pulse width modulation,PWM  signal from the Samsung Control board.

2) The PWM output signal from the control board does not work on my heat pump!

3) The French Samsung Engineer "did not know , or understand How the PWM control works", that being only known to the Germans".

4) I have made my own PWM signal generated by an Arduino. The Actual flow rate is here controlled as a function of the Delta_T across the primary Heat Exchanger ports.

5) I have just bought a replacement control board hopefully giving a working  Samsung Generated PWM Signal.

ian  

 

 



   
ReplyQuote
(@iantelescope)
Reputable Member Contributor
Joined: 4 years ago
Posts: 418
Topic starter  

@cathoderay 

Many thanks for your input.

I use the Open-office Calc spreadsheet sourcing and producing CSV files.

I use GNU PLOT for  DATE_TIME extraction .

 

Date -Time Format handling?

I have tried several graphical programs for producing graphs from odd Date - Time formats but have run into a fundamental problem.

My Data logger, for example, produces the DATE-Time in the form Year-Month-Day--Hour-Minute-second

eg "2024-02-17-34-35-12"

This has proven to be  difficult or unreliable for many programs in handling and generating a time base from a plethora of DATE-TIME FORMATS.

Except  for "GNUPLOT" which can process most Date-Time Formats.

My Sharky produces another text embedded version with "start  script" hour-min-sec-Year-Month" " end script".

Again , only GNUPLOT extracts the date /Time from the text often  producing an excellent graph in the process.

Can you recommend a Graph making  program replacing GNUPLOT for it's ability to  read most Date/Time formats?

ian

 



   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 6 years ago
Posts: 4425
 

@iantelescope

The serial number is not the same as the model number.

You will find the model number on the nameplate on the side or rear of the outside unit.



   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 6 years ago
Posts: 4425
 

@iantelescope

What value is set for parameter 2091, you have asterisks indicating both :2 and :4?



   
ReplyQuote
(@iantelescope)
Reputable Member Contributor
Joined: 4 years ago
Posts: 418
Topic starter  

@derek-m 

The type number on the tank is

AE050RXYDEG/AE00RNWMEG

The 2091 Field settings reflect several of my attempts when changing all the parameters in the 2091,2092 ans 2093. Just in case.

I initially thought , just like Craig , that my 8 minute Short cycling period was set by the fourth option.

When asked, the French Samsung Engineer said that he did not understand any of these options having no background in Electronics or Electronic  logic.

He added that , in any case, these options did not do very much, again saying that "only the Germans understood the  PWM and the 2091 options".

Franco Prussian War of 1871 is still , apparently , being fought !

ian

 

 



   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 6 years ago
Posts: 4425
 

So what is the actual setting of 2091?

I am aware of the competence of some french 'engineers', having worked with a number in the past.

Where are you located by the way?

 



   
ReplyQuote
(@iantelescope)
Reputable Member Contributor
Joined: 4 years ago
Posts: 418
Topic starter  

@derek-m 

Hi Derek,

I have mostly used 2091 with "Water pump App no 3 " the fourth option.

This option produces a temperature surge some 7 minutes after the start of the cycle.

This surge was presumably designed to increase the Cycle time .

This option also produces a 2 C Hysteresis , again, designed to further increase the Cycle time.

The Samsung Software is here deigned to mimic the behaviour of the best hardware Thermostats.

My cycle time is increased slightly when using 2091 ,Water Pump App no 3.

This morning I changed the setting to Water Pump App no 2 , for experimentation again.



   
ReplyQuote
(@iantelescope)
Reputable Member Contributor
Joined: 4 years ago
Posts: 418
Topic starter  

@derek-m 

Hi Derek,

I am located in Inchinnan ( The INCH , or Island of St Innan ) a town  between the Cart and the Clyde although no longer an island.

Officially, Inchinnan is part of Renfrew.

Underneath my house , are the remains of "Criegiehall" a former croft owned by the Scottish  Knights Templar from 1158.

ian

 



   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 5 years ago
Posts: 3126
 

@iantelescope - date-time formats can be very tricky, especially with software that likes to be 'clever' - and then gets, for example, month and day mixed up, or tells you the date time is 456930 and then just for a joke tells you the 4th of January is April Fools Day. Spreadsheets can be especially creative in this way. There are various options:

1. Treat the date-time stamps as categories not date-time. They need to be in order, and equally spaced, which of course they are often not.

2. Process the date-times into an acceptable format in a spreadsheet. This is an option that works well for folks that don't get out very often. For example, force the date-time into a string (eg add spaces/text characters) and then do string extraction to get the various parts eg chars 1-4 are year etc.

3. Use python. This is what I do. You can tell python what format your date-time strings should have:

>>> from datetime import datetime

>>> now = datetime.now()
>>> print(now)
2024-02-23 15:48:51.027361
>>> print(type(now))
<class 'datetime.datetime'>

>>> now = now.strftime("%Y-%m-%dT%H:%M:%S")
>>> print(now)
2024-02-23T15:48:51
>>> print(type(now))
<class 'str'> 

which takes a python datetime and coverts it to a string of my choosing.

You can also (this can be very useful) tell python what format your existing date-time strings have (I have changed the hour from 34 to 14), and make them into datetimes:

>>> telescopeTime = '2024-02-17-14-35-12'
>>> print(type(telescopeTime))
<class 'str'>

>>> telescopeTime = datetime.strptime(telescopeTime, '%Y-%m-%d-%H-%M-%S')
>>> print(telescopeTime)
2024-02-17 14:35:12
>>> print(type(telescopeTime))
<class 'datetime.datetime'>
 

Note the key methods are very similar, only one letter different: strftime and strptime.

The above examples are for single variables to show the conversion process. In practice, you read the CSV data into a pandas dataframe (in effect an internal invisible spreadsheet inside python) and do the manipulations on columns. Pandas also has it's own datetime conversions.

The best plotting system I have found so far that produces pleasing charts without needing painfully complicated code is python's plotly express module, which I use to produce charts like this (last weeks data) from CSV files via pandas dataframes:

image

 

BTB for those who notice the slightly slow recoveries after recent setbacks, I suspect these are wind/rain chill: my house does not like the wet windy weather it has been subject to of late.


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@iantelescope)
Reputable Member Contributor
Joined: 4 years ago
Posts: 418
Topic starter  

@cathoderay 

Great stuff , I will have to try python for my graphs.

I would still recommend you try GNUPLOT with it's old fashioned 1970's Shell script format.

But , Thanks , I will have a look at python again, having tried  several different programs, languages and apps with my DATE/TIME Problem.