Mitsubishi Ecodan stuck on immersion symbol
They could be defrosts but unlikely at that Frequency.
do you have the MELCloud app that can show the flow and retune temps for those times?
There is an hourly chart that is useful
That’s definitely cycling do you have UFH or rads regardless of which it would suggest you have only a very small proportion of the heating system calling g for heat. Do you have a lot of zoning in the house?
I have UFH on ground floor and rads on 1st floor. 2 Zones have been setup, ground floor and 1st floor. There are also individual thermostats for UFH in each room.
That will be the cause then, with only 1 thermostat calling for heat the water volume is too small it heats quickly and the heat pump has to turn off then back on again when it cools. Ideally you want all circuits calling at the same time. What make of thermostats are the UFH zones on? Do they connect to a wiring centre that turns the actuators on for each circuit? If so you can unscrew the actuators for the UFH loops that will mean they are all open all the time so when one zone calls for heat water will flow round them all. This will mean you have more water volume for the heat pump to react to giving it more chance to find the correct input power before the water over heats
I have 1 of each of the right Mitsubishi controller, one on the ground floor and one on the 1st floor. The EPH controllers control the actuators. I have a EPH controller in every room, around 5, on the ground floor for the UFH. The Mitsubishi is wireless and the EPH is hardwired.
So presumably the EPH thermostats are wired back to a controller near to the UFH manifold? Do you have a picture of that?
@gary That's in an awkward place, hard to get to. The EPH do control the actuators, but the underfloor heating won't come on until the Mitsubishi controller temperate is set above the current room temperature..
Yep that all makes sense the easiest solution is to remove all the actuators from the UFH manifold they should just unscrew them all loops will be open when thermostats call for heat.
Or as you need the mitsi thermostat to be calling for heat for the heat pump to fire up. Then just increase the temp on all the 5 zone stats to a high level then the UFH will only come on when the mitsi thermostat calls for heat. Depending how it’s wired then downside of that may be that there is an extra circulation pump for the UFH that will run constantly once you set the zone thermostats to constantly call for heat
Ideally you want it all to come on at the same time. When my hall thermostat calls for heat all of the UFH loops downstairs come on and all the rads upstairs come on. Upstairs can be kept cooler than downstairs by turning down the lock shield valves to reduce flow. If you have more water volume you can run at lower flow temps without cycling
- 26 Forums
- 2,111 Topics
- 46.4 K Posts
- 40 Online
- 3,402 Members
Join Us!
Latest Posts
-
RE: No-code, plug-and-play monitoring for your heat pump
@benson It is a shame, I was looking at these when I wa...
By Grantmethestrength , 6 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 7 hours ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 7 hours ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 10 hours ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 11 hours ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 12 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
When i was looking I encountered one installer who does...
By JamesPa , 12 hours ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 3 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 4 days ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 4 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 5 days ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 5 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 5 days ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 5 days ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 6 days ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 6 days ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 1 week ago
Members Online
No online members at the moment