Mitsubishi Ecodan 11kw Defrosting Issue.
Hello, i am new here and also a newbie on air to water heat pumps.
I recently bought a Ecodan / Zubadan split system manufactured 2019 and installed 2021, it was too cheap (500€) so i could not help my-self from buying it and try to get it working. Outside unit is Zubadan PUHZ-SHW112YAA with the pre plumbed inside unit EHST20C-YM9CR2.UK.
I installed it in June and found lots of small problems, outside unit dip switches configured wrong and also some settings in the FTC5 controller that made it run really inefficiently, when i first got it running the COP was about 2.0 or worse even tho it was summer and warm weather. Then made some changes to the settings and got the COP up to about 3.2 and that was not too bad, now when the weather has become colder the real problem started to show.
When the outside temperature gets below 0 degrees C the defrosting seems to have some weird issue. I saw that the unit had frost on it so i waited until a defrost cycle started and it worked fine, but then when it got even colder to about -4 to -6 degrees it defrosted many times every day and i noticed that the defrost cycle is much to short so it just starts to melt the ice then stops and resume with the heating causing the unit to freeze completely in a day or two.
My first guess to the problem would be the 4-way valve but i really cant see how that could be the issue when it clearly do go in to defrost mode but mostly seem to "finish" the cycle in well under 10 minutes which seem to be a very short defrost cycle.
So now with the colder weather the outside unit is frozen and the COP goes down under 2 and won't completely defrost until the ambient temperatures are just below 0
Here are some Melcloud and SD card graphs.
Could this be a sensor problem or something else? Grateful for any advice on this issue.
And greetings from Finland.
I had a problem with my ecodan unit freezing up having to literally put a hot air gun on Christmas Eve at 10pm 2 years ago.
Took various engineers over a month to sort out.
Low and behold after all the headaches it mounted to a dodgy temperature sensor mounted at the outside or the outside unit at the rear.
Basically it was sending the wrong signal.
good luck
@westkent Thank you for the info, this was exactly what i was thinking about. i have a Beamex temperature calibrator and a dry well temperature generator at hand so i will check the service manual what kind of thermistors they use and then check the temperature curve and compare with the manual. Best to check them all as they seem prone to failure / drifting.
I did not have the time to check the thermistors Yesterday but i am now almost certain that's the problem. I enabled the cooling function on the heat pump and manually "defrosted" the unit by cooling the home. Worked great, had it on about 12 minutes and all the ice was gone.
At least the 4 way valve should be ok, worst case there is low refrigerant but would not bet on that as the pump both heat and cool very good.
Also i noticed that when using weather compensation i got really bad COP, then when using room auto adapt i got much better COP which also points to the outside unit thermistors.
This weekend i will test ALL thermistors and hopefully find a faulty one.
@thundermink can you give us an update on your tests?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Sorry for the slow reply, it looks like a happy new year to me. 4 days ago it was a bit warmer so i got to start trouble shooting a bit more, i noticed that if i completely shut down the system the LEV electronic expansion valves open fully, then the unit defrosted ok for a while so and i started thinking if it is the valves that skip some steps causing the defrosting issue over time when the valves misses steps and is in the wrong position.
I removed the valve heads and noticed one was not fully in place and another one was stuck to the valve body so i sprayed some wd40 to loosen it and then cleaned the stepper motor coils, also the cables was zip tied to the copper tubing and the cable shrink seemed to have shrinked and caused very much tension on the valves wich also can have been why one of the valves was rotated out of place, 4 days now and no problem, it has not been too cold yet but it is now -4 degrees C and i have not seen any frosting what so ever on the outside unit. Also the COP is much better so it seems that this has worked. Still need to wait and see how it behave the coming days as colder weather is on its way (friday forcast -11)
Hopefully the system will work 100% for the rest of this winter 🙂
A bit of a follow up on the progress of the Ecodan pump, while finding and correcting the issues i faced last winter we are now getting in to heating season again 😀 the repairs done this winter had a big difference at cop values going from under 2 some days to always over 2.5 and the defrost problems was minimal, but last month i thought it is time to remove the panels from the outside unit completely to get a real good look at everything. I found that Mitsubishi is not very good when it comes to temperature sensors, they where all just clipped to the pipes with copper clips, no isolation and no thermal paste at all. noticed a problem specially with Liquid sensor TH3 facing outward while it should face away from the pipe that is next to the sensor to not cause false readings. i removed all sensors and cleaned the pipes, added thermal paste and isolated the sensors using pipe foam insulation. THIS WAS A BREAKTHROUG, COP values had been 3.0-3.6 the past weeks, now after the modifications COP has been between 3.95 and 4.70!! Before the mods i had never seen cop over 3.9. Everyone owning a Ecodan unit should check the sensors and modify them and check the behaviour. atleast for the Ecodan shw112 this was a game changer. Hope this helps some of you out there.
Posted by: @thunderminkA bit of a follow up on the progress of the Ecodan pump, while finding and correcting the issues i faced last winter we are now getting in to heating season again 😀 the repairs done this winter had a big difference at cop values going from under 2 some days to always over 2.5 and the defrost problems was minimal, but last month i thought it is time to remove the panels from the outside unit completely to get a real good look at everything. I found that Mitsubishi is not very good when it comes to temperature sensors, they where all just clipped to the pipes with copper clips, no isolation and no thermal paste at all. noticed a problem specially with Liquid sensor TH3 facing outward while it should face away from the pipe that is next to the sensor to not cause false readings. i removed all sensors and cleaned the pipes, added thermal paste and isolated the sensors using pipe foam insulation. THIS WAS A BREAKTHROUG, COP values had been 3.0-3.6 the past weeks, now after the modifications COP has been between 3.95 and 4.70!! Before the mods i had never seen cop over 3.9. Everyone owning a Ecodan unit should check the sensors and modify them and check the behaviour. atleast for the Ecodan shw112 this was a game changer. Hope this helps some of you out there.
@thundermink can you provide photos to illustrate your fixes please? I wouldn't know where to start looking for temp' sensors or liquid sensor TH3 on my Ecodan. My COP is often barely over 2 and never over 3.
Pictures would be helpful if possible.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Hello, unfortunately i did not take any photos, but you should check the service manual of your pump, In the puhz-shw112yaa service manual they have photos and instructions how to remove the sensors and there you will clearly see where the sensors are placed. Here is a screenshot from the manual of TH3 liquid sensor. i removed it, put thermal paste in the sensor clip and isolated it using pipe isolation then repeated the procedure on all other sensors
I think this is an interesting observation and aligned with what a few of us have been saying for some time: the sensors are only as good as they've been installed. The best sensor in the world wrongly installed will still give you poor data.
Interesting case study!
CEO and co-founder at HavenWise
Posted by: @hcasI think this is an interesting observation and aligned with what a few of us have been saying for some time: the sensors are only as good as they've been installed. The best sensor in the world wrongly installed will still give you poor data.
Interesting case study!
@hcas all well and good but the majority of us, myself included, have no idea how to even identify, locate and then fix the issue with these sensors. The issue then, were I to sign up to Havenwise, which I’m seriously considering, is that your calculations and settings to operate my system ‘efficiently’ is based on flawed information. I haven’t a scooby where to even look for said sensors never mind decide if they’re installed correctly.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@morgan Fully agree with you. It shouldn't be the homeowner's job to do this. The installer should. When I went to site with @ashp-bobba some time ago, he mentioned he makes sure the sensors are all "installed" correctly to the best standard. He knows this based on his experience installing many Mitsubishi heat pumps before.
When it comes to Havenwise, the accuracy of the flow or return temp measurements don't matter so much for the optimisation. Whether the flow temp is 35C or 36C doesn't matter much in practice for the operation of the heat pump.
It does matter for the reporting because small errors in measurement can have an impact on the reported COP. A 1C difference on the flow temp measurement would be 20% difference in reported COP, even though the actual COP probably was almost exactly the same.
CEO and co-founder at HavenWise
-
New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
10 hours ago
-
Ecodan with FTC7 - True Weather Compensation
4 days ago
-
Ecodan unable to hit legionella target temp - what's the consensus?
2 weeks ago
-
Ecodan consuming 100kwh per day in new build!!!
6 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
9 months ago
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 592 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
Thanks for the clarification.
By JamesPa , 54 minutes ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
OK, TBH I dont know enough about MLCP to comment with a...
By JamesPa , 1 hour ago
-
RE: Predicted Heat Loss from MCS calcs vs EPC vs actual
My gut feeling is that the heat pump is right sized. ...
By Tim441 , 1 hour ago
-
RE: Heat pump not reaching flow temperature
Peak Energy Products most recent accounts (to June 2024...
By JamesPa , 2 hours ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Agreed, which is no more nor less than a customer shoul...
By Majordennisbloodnok , 3 hours ago
-
RE: Running from backup generaor in powercut?
@batpred In our case, 3 times each day when the Octopus...
By Toodles , 3 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Hi @sheriff-fatman Cycling at 5C and below is usuall...
By RobS , 4 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Here's the latest Fogstar ready built pack....
By Bash , 5 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick yes, even though the current system is ru...
By Tim441 , 5 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Solis confirmed that the S6 works with a single battery...
By Batpred , 6 hours ago
-
RE: Who has a V2G EV installation
I am wondering if in any V2X, would the car battery eve...
By Batpred , 7 hours ago
-
RE: Setback savings - fact or fiction?
Yes, by calculating it manually from the minute data, w...
By cathodeRay , 8 hours ago
-
Fan unit Making terrible noise HELP!!
One of a pair of fan units on an Earth Save Classic II ...
By GutoFfowc , 8 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
OK. I think your system, which seems well designed, is...
By JamesPa , 10 hours ago
-
RE: Heatpunk Floor plan issues
It's usually the complete opposite... seldom that Safar...
By Mars , 24 hours ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 1 day ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 1 day ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 1 day ago