Hi @snuffy , I have an Ecodan - slightly larger than yours- 8.5kw. You have one of the most readily adaptable sized heat pumps for retrofit applications which can be plumbed in with only 22mm primary pipes. It has a design flow rate range of only 9 -17 litres per minute (LPM) which, if operating at that kind of flow rate should be very quiet. Bigger heat pumps have to operate at much faster speeds.
So it might be worth asking your installer what is your current flow rate on your primary circuit? And.. What is the targeted temperature difference between flow pipe and return pipe? This should be averaging 5c
Another few questions might be - how do I control my pump speed? Do I really need a low loss header since a 6kw heat pump might only have a short run of radiators? Could it be reconfigured to operate off just one pump at a quiet 10 or 12 LPM depending on the DT target?
That would save you £200 for the low loss header and £200 for the second pump and around £100 per year in electricity driving the second pump.
There may be a valid reason for high pump speed such as too much resistance through the pipework. But that would point to issues with pipe sizes etc.
If you can talk to your installer now you may get a better understanding on how your system works and you may get a better set system commissioned properly.
PS. If you’ve got a Honeywell thermostat you can still operate your system using weather compensation.
Hope this helps and gives you confidence to ask some important questions.
pps you can switch off the system briefly to allow air bubbles to clear before switching it on again. Some pumps have methods of bleeding trapped air.
@snuffy don't give up , it sounds like your installer is "reasonable" - its a good thing that some radiators were mentioned as being in need of replacement, it suggests that heat emitter sizing and design flow temp has been thought about at least to some degree . I used to have those fin things in my house as well, they are not the best (think mine dated back to house build time, 1970's - they are gone now though).
A spirovent is about 120 quid + his time to fit (easy job for a pro) and is guaranteed to remove air as a source of noise.
also its worth getting themto look at the design and control of the flow rate - are the pump(s) setup to modulate down when there is minimal load? they should. in which case at that point the flow noise will drop to next to nothing.
oh and mine's a retro fit from a gas boiler with 100% radiators. It can work. bigger house bigger unit but still a lot of the old pipework. Mostly new rads though. It can work. but I do have 1 group of rads on a supply pipe that is slightly too small to be ideal - those are where I do get flow noise. So you may find there are just 1 or two places where pipework needs an upgrade.
But look at the air noise (really easy to solve) and flow rate (pump speeds) first.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @snuffyI'm thinking if any are causing a problem, it's the one we have in the bedroom.
You shouldn't be left to ponder this.
Before a heat pump gets installed there should be an energy survey conducted (often by the installer).
That's how they know the size of the ASHP and heat-emitting surfaces for each room.
There shouldn't be any unknowns regarding whether a particular radiator is capable to delivering sufficient heat.
Such energy surveys are conducted to the PAS2035 standard.
Posted by: @sunandairIf you can talk to your installer now you may get a better understanding on how your system works and you may get a better set system commissioned properly.
Quite!
It is a requirement of the Building Regulations, Part-L that you are provided with this information.
Save energy... recycle electrons!
@snuffy I thought that for comparison, you might care to see a few shots of the lagging from the ASHP to the entry point into the house. I’m also putting a shot of the pipework fixings in the airing cupboard. The grey flexi pipes top centre were existing feeds to the shower unit. If you see some black lagging at the bottom edge of this photo, they are the lagged pipes from the Sunamp Thermino that is out of shot. Photos don’t seem to transfer, I’ll have another try with reduced filesize. Regards, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
And finally, the airing cupboard, overall, the system is very quiet and the only sound heard from any internal components is a faint pump noise if listening carefully with the airing cupboard open. Naturally, there is fan noise from the ASHP in the back garden but, this is drowned out by the ambient noise level from
nearby roads. I need to stand within a metre of the Daikin to hear it running above the ambient sound level. Regards, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I wouldn't be happy with the level of insulation or the fitting on the photos from @toodles
- The brass isolation valves behind the ASHP remain entirely uninsulated
- The insulation is compressed at a number of points by the use of nylon cable ties. (I can't tell if these are actually supporting the pipes, or holding an electrical wire to them).
- That external pipe run is at least 5m, possibly 6m. I would expect to see 25mm wall thickness on insulation across that distance.
The internal bare copper pipes clearly don't comply with Building Regulations, Part-L 4.24
Save energy... recycle electrons!
@transparent Thank you, I’ll take up the matter of insulating the brass valves with the installer, the ties are holding an electrical ‘trunking’ that carries everything non water based - and yes compression at these points does nothing to improve the overall insulation:-( The insulation is 70 mm diameter. The copper pipe is approx. 28 mm dia. Regards, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Sorry, I didn’t see the final comment about the compliance with buildings regs and insulation of pipes.The DHW system is a totally separate system and the pipework is insulated as required; the pipework you see is all there is to supply / lose background heat for the airing cupboard itself. The Sunamp Thermino DHW system has a specified heat loss of no more than 0.75 kW over 24 hours. We used to have a conventional insulated DHW tank and the overall heat loss was higher than the total we experience with the new system. There is only a small area of external wall to the side of the airing cupboard which is cavity insulated - the cupboard backs onto the bathroom and the ceiling in the cupboard has the usual plasterboard and above this is 600mm of loft insulation plus some boarding sandwiched between older and additional insulation. The heat loss from this pipework does supply some residual warmth in the cupboard - but as I say, far less than the previous gas CH and DHW arrangement. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Building Regs Part-L 4.24 covers pipework insulation for both DHW and space heating.
There are some comprehensive online guides to insulation which are worthwhile reading.
It's unfortunate that most of them are USA-based and the charts are in inches.
Note that heat looses are specified in watts per metre: W/m
The longer the pipe run, the greater the loss.
Since the difference between Flow and Return is around 5°C
you really don't want to lose even 1°C before the water has even entered the house!
Save energy... recycle electrons!
Regarding the external pipe-run, I did attempt to have as short a run as possible to reduce losses; I wanted to install the ASHP much closer to the airing cupboard area but no installer I tried felt it wise to install at height on the back wall. There would have been issues with access for servicing as well as possible vibration and noise transference. Reluctantly, I accepted the position it is in now and the longer pipe-runs. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 22 Forums
- 2,057 Topics
- 44.9 K Posts
- 72 Online
- 3,299 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
There are various ways to look at things related to CoP...
By Johnmo , 46 minutes ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
@abbote thanks for that advice.There was a bit of air i...
By tdudgeon , 1 hour ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
One manufacturer Viessmann has to have their buffer, as...
By Johnmo , 3 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 22 hours ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 1 day ago
-
RE: Is your heat pump insured?
@johnmo sorry it comes across like that. The post is au...
By KevinPotts , 1 day ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo Perhaps a little detail might explain my reason...
By Toodles , 1 day ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 2 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 2 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 2 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 2 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 2 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 2 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 2 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 3 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 3 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Took a while to find on the OFGEN site: ”The FIT sche...
By AgentGeorge , 3 days ago
-
RE: why solar diverters for HW instead of the heat pump?
For me there are few factors why you may want to heat w...
By Johnmo , 3 days ago