@heacol In which case what model Mitsubishi unit would you recommend to pair with a Mitsubishi Ultra Quiet Ecodan 11.2L ASHP and Tempest 250L HW cylinder?
I have to wonder why an experienced company (JL Phillips) would recommend as they have.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
@morgan As I have stated, Mitsubishi's own wireless internal thermostat. I am not surprised at the thermostat they have recommended, we see them all the time (and put them in the bin). It appears that they are boiler installers, not purely heat pump installers, Boilers and heat pump are completely different, like cars and motorcycles.
Professional heat pump installer: Technical Director Ultimate Renewables Director at Heacol Ltd
Hi Morgan,
Let me explain what Heacol is saying in layman terms.
As stated, a thermostat is an on - off device, which most people may think gives accurate control of temperature. This is not correct for the following reasons.
Thermostats have a built in deadband, which on most thermostats appears to be set at 1C, which may not seem much but can have quite an effect on how a heating system performs. Say a thermostat is set at 20C, and the temperature in the room is at 20C, and the thermostat is off. If the setting is now increased to 21C, the thermostat will switch on and the central heating pump and ASHP will start. As warm water flows from the ASHP, the heat energy will be transported to the heat emitter (say radiator), which will fairly quickly warm up to the temperature of the water. If the ASHP is set to provide water at 40C, then within maybe 5 to 10 minutes the cool water from the radiator will have flowed back to the ASHP and been heated up to 40C. So after probably 10 minutes the water flowing around the system will be at 40C, but the temperature in the room will have barely changed.
Air is quite a good thermal insulator, so it could take an hour or more for the heat energy to transfer from the radiator to the air in the room, during which time the central heating pump and ASHP will continue to operate. When the air temperature reaches 21C, the thermostat will switch off and the pump and ASHP will stop. Because the radiator is still at 40C, it will continue to heat the air in the room and will take the temperature in the room above 21C.
As the radiator cools, a point will be reached where it is no longer heating the air, and the air temperature will start to fall due to heat losses. This will continue until the air temperature falls to 20C at which point the thermostat will once more switch on and start the heating system. Because it takes time for the heat energy to be transferred from the radiator to the air, the air temperature in the room will actually fall below 20C before it starts to warm.
Personally, I am at a loss to understand why thermostat manufacturers insist on incorporating a deadband of 1C or even higher in some cases, which is no longer necessary with modern electronic thermostats. I can feel a change in temperature of 0.5C, and I suspect probably many other people can also do so. If a person is comfortable at 20C, then it is necessary to set the thermostat at 21C to maintain the temperature at around 20C or above.
What Heacol is suggesting is to use the thermistor, which is built into the FTC controller, or even better a remote thermistor which can be mounted in the most appropriate location.
A thermistor is a temperature sensor, which varies its resistance with variation in temperature, and hence can be used to measure the actual changes in temperature. This temperature measurement is used by the FTC controller to adjust the water flow temperature produced by the ASHP.
If, in the above example, a FTC controller with a thermistor is used in place of a thermostat, the following will occur.
If the setpoint on the FTC controller is raised from 20C to 21C, the controller will instruct the ASHP to slightly raise the water flow temperature, but probably not as high as 40C. If after a period of time the controller does not detect an increase in air temperature, it will raise the desired water flow temperature a little more. Once the controller detects that the air temperature is starting to increase it will stop increasing the water flow temperature. If the air temperature now starts to reach the desired 21C, the controller will start to lower the water flow temperature. Over time the controller will therefore balance the heat output from the ASHP to match the heat losses at the desired indoor air temperature. If the desired air temperature is 20C, then the FTC controller should maintain this temperature fairly accurately, with the minimum required water flow temperature and hence most efficient operation of the ASHP.
Without carrying out detailed tests, using both methods of control, it is difficult to quantify exactly how much efficiency improvement can be achieved.
Morgan, if you required any further clarification then please get in touch.
I've just found a whole section on heat pumps for Nest thermostats - quite interesting!
Hi Batalto,
I think you will find this is aimed at the North American market, hence the Fahrenheit temperature and dollar costs. They get much lower temperatures than the UK (when I was working in Montreal it often hit -20C), and hence the need for auxiliary heating (read direct electric) to help out an ASHP. I suspect it would be of marginal benefit in the UK, and could possibly increase consumption and costs if the ASHP is working harder during the coldest part of the night.
@heacol and @derek m. Thank you both. In a quandary now. Do I tell the installer I don’t want the Neostat and insist he fits as you describe? Or do I take the installation as is and buy, instal and do the set up as you describe post instal? Is it easy enough for somebody such as myself to achieve?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
@morgan Personally I would tell him to install the proper equipment, the Neostat is about half the price, you may have to fork up another £100.00 but it will be worth it.
Professional heat pump installer: Technical Director Ultimate Renewables Director at Heacol Ltd
Hi Morgan,
You can google and download the following, and see if you understand the concept and the equipment.
I may be wrong, but I suspect your supplier understands thermostats, but not wireless remote controllers and how to configure them.
If you or he gets stuck, just ask.
@heacol which one? Is the wireless bit for it to talk to already installed in the Mitsubishi ASHP? To be honest I’m lost and out of my depth here. But I do know I cannot do another winter without central heating.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
@morgan The Mitsubishi wireless thermostat is a 2 part system, it is an add-on to the FTC5 controller. It communicates with data to the main controller ant tells it exactly what the room temperature is and what the required room temperature is in Degree C.
The Neostst is a wireless on-off switch, just like a light switch. It does not communicate any information to the heat pump controller other than switching it on or off. It is like trying to control the speed of your car with the key.
They do however look similar, but they are not. If you want a good job, do it properly or do not expect it to work properly. Mitsubishi would not have made the thermostat if they intended you to use a third party thermostat. Just tell them you want the Mitsubishi thermostat.
Professional heat pump installer: Technical Director Ultimate Renewables Director at Heacol Ltd
@derek-m Thank you, it is difficult to describe in layman terms.
Professional heat pump installer: Technical Director Ultimate Renewables Director at Heacol Ltd
Hi Morgan,
If you google the following and download. Then look at diagram 3.1 on page 5, which shows how the equipment needs to be connected.
Ecodan_FTC5_-_PAC-IF062B-E__PAC-SIF051B-E_Installation_Manual_Instruction_Book__BH79D449H03_.pdf
Your installer should know how to install and configure the equipment.
It may pay you to ask why they have specified a neostat in preference to the Mitsubishi controller.
- 25 Forums
- 1,442 Topics
- 30.2 K Posts
- 33 Online
- 1,225 Members
Join Us!
Latest Posts
-
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Yes, it is one of those two who first alerted me to the...
By IvanOpinion , 14 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
The fact that the MCB is rated 16A tells us what we nee...
By Transparent , 14 hours ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
Thanks, @editor. Ideally it’d be someone who would li...
By Majordennisbloodnok , 16 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Unless adequately controlled it could devour your bank ...
By Derek M , 17 hours ago
-
RE: Effect of buffer tank or volumiser on heat pump system
I think that you will find that the best location for a...
By Derek M , 17 hours ago
-
RE: ASHP Commissioning: What Questions Should I Ask the Installer?
@derek-m thanks - will look out for the point regarding...
By Declan90 , 1 day ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor @kenbone Thanks, I would be very interested ...
By Elton , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
This is all a bit too frequentist for my liking. The pr...
By scrchngwsl , 1 day ago
-
Relax with 4K drone footage of lawn mowing to a smooth Motown tune
Sending out some chilled weekend vibes to everyone. Lis...
By Mars , 2 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
The starting point of that discussion on Camelot-Forum ...
By Transparent , 2 days ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 2 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 3 days ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 3 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 3 days ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 4 days ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 4 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 4 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 4 days ago
Heat Pump Humour
Latest Topics
-
By David999 13 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 7 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 7 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago