Posted by: @mike-patrickMany on this site quote their achieved COP ratings and I wonder how. Do some makes provide the heat output figure or is it more complicated than that?
My installation has a Sontex heat meter wired into it and I think the numbers I eventually see (after a trip through some cloud services) come from that.
If you don't have a heat meter, then Open Energy Monitors's EmonCMS (that @batalto mentions above) can estimate COP with fewer sensors and the simulated Carnot COP formula, but it is an estimate.
In one way, it doesn't matter what COP anyone else gets, or whether it matches what's in the data book for your pump. I think most people start off using it as a useful tool for optimising a setup, taking into account many variables, but some do seem to lose track of it: maybe COPs are the new environmentally-acceptable Miles Per Gallon to compare on enthusiast forums?
What really matters is whether you can afford the power consumed and whether the heat output is sufficient for you.
Posted by: @mjrPosted by: @mike-patrickMany on this site quote their achieved COP ratings and I wonder how. Do some makes provide the heat output figure or is it more complicated than that?
My installation has a Sontex heat meter wired into it and I think the numbers I eventually see (after a trip through some cloud services) come from that.
If you don't have a heat meter, then Open Energy Monitors's EmonCMS (that @batalto mentions above) can estimate COP with fewer sensors and the simulated Carnot COP formula, but it is an estimate.
In one way, it doesn't matter what COP anyone else gets, or whether it matches what's in the data book for your pump. I think most people start off using it as a useful tool for optimising a setup, taking into account many variables, but some do seem to lose track of it: maybe COPs are the new environmentally-acceptable Miles Per Gallon to compare on enthusiast forums?
What really matters is whether you can afford the power consumed and whether the heat output is sufficient for you.
Agree. Power consumed is all that really matters. Just like petrol consumed in your car.
If you know how much water is in your CH system you could measure how much energy is consumed to raise it from X to Y degrees and compare that with the amount of energy theoretically required. The flow temps are available from your control panel. You'd have to make some corrections for heat loss so I'm not sure how accurate it would be. Doing it for DHW would be easier.
Posted by: @mjr...
In one way, it doesn't matter what COP anyone else gets, or whether it matches what's in the data book for your pump. I think most people start off using it as a useful tool for optimising a setup, taking into account many variables, but some do seem to lose track of it: maybe COPs are the new environmentally-acceptable Miles Per Gallon to compare on enthusiast forums?
What really matters is whether you can afford the power consumed and whether the heat output is sufficient for you.
Yes-ish.
I got a heat pump rather than a replacement boiler primarily as a lower burden on the world's resources whilst keeping us warm. That's also why I got the solar PV. The latter means I can "afford" a rather lower efficiency in the heat pump than otherwise, but anything I can do to increase the heat pump's efficiency will still reduce the amount of energy I pull from the grid and, therefore, the carbon emissions I'm responsible for. As a result, I'd say I don't care much about what anyone else's COP is other than providing a benchmark. I do, however, care very much about what my COP is compared with what it has been, because that's a useful measure of how well the heat pump is being managed and maintained, and a useful early warning if things may need to be changed.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokanything I can do to increase the heat pump's efficiency will still reduce the amount of energy I pull from the grid and, therefore, the carbon emissions I'm responsible for.
Yes-ish, back at you! 🙂 I could achieve better efficiency by not allowing the pump to shut off or cycle on sunny afternoons and thereby avoiding the less-efficient startup phase, but we don't really need even the 3ish kW minimum output then, so it would be a waste of energy.
Posted by: @mjrPosted by: @majordennisbloodnokanything I can do to increase the heat pump's efficiency will still reduce the amount of energy I pull from the grid and, therefore, the carbon emissions I'm responsible for.
Yes-ish, back at you! 🙂 I could achieve better efficiency by not allowing the pump to shut off or cycle on sunny afternoons and thereby avoiding the less-efficient startup phase, but we don't really need even the 3ish kW minimum output then, so it would be a waste of energy.
Agree entirely. I'm not after the heat pump running at its most efficient, I'm after the most efficient use of the energy at my disposal. There is a difference, as you point out.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Here’s some food for thought.
How many distribution pumps do you have connected to your heat pump system at the moment and do you know how much power they consume?
I’ve just tallied ours up, and it’s a frightening amount in kW usage and running costs. I’ll post some figures tomorrow, and this doesn’t make it into COP calculations.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
i think its hilarious that our industry worries about cop when all that matters is run cost. The pumps are there to do a job, they would be there if you had a boiler too. The boiler lads dont take any electrical consumption into consideration when talking about efficiency and despite what you are told neither do the heat pumps. The cop your machine measures is just for the compressor, no pumps, valves, controls nothing else is measured. Get over it. its so bloody dull.
all i care about is what it costs and am i warm, now lets move on.
Heat pump builder
@editor We have two pumps that use ~35w each. The idle power consumption of the unit is also substantial I think. However, the "energy consumed" figure my Mitsubishi Ecodan reports slightly over-estimates compared with the actual meter in the garage (which the pumps run off as well I believe). The COP therefore is probably slightly higher in reality than reported in my heat pump's figures.
It is quite frustrating that this isn't just measured as standard.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
@grahamh, and therein lies the biggest issue for me with the ASHP industry. Running costs don't correlate with the heat they produce (and the manufacture's promise to produce), especially in poorly designed systems, because the heat pump industry does not want to take ownership of its incompetence.
I'll use us an example. When water flow through the system drops below 28 litres per minute our air source heat pumps goes full berserker mode with alarms. So what did our installers do when we complained, they came and put in a bigger Grundfos distribution pump that runs at 190 watts per hour. Bish, bosh, bang. Problem solved. This is in addition to two other distribution pumps in the heating system already. That makes three. If they all run at 190 watts per hour that's 570 watts per hour.
When we wanted to run the system bivalently last winter on HVO, we were getting more flow dramas and errors. Solution. Add another distribution pump. That takes the tally to four: 760 watts per hour – 18kWh per day – approx. 547kWh per month, which costs £200 per month.
There's nothing hilarious about that Graham – the heat pump installer base seeps with incompetence. Most installers are literally slapping heat pumps in and hoping for the best. There's no thought, design or planning. Just do the job, get paid, move on. If things go wrong, they compound expensive running costs by "remedying" the issue by adding more things to the system that make it even more expensive to run and no one factors that it in and even raises it. It's a dishonest practice.
And to be clear, all these distribution pumps were not factored into our running costs and these additional pumps would not be required with a boiler because it doesn't care about flow, but they are very much a part of our running costs because they are costing a lot of money to keep running.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@batalto - can you by any chance let me have the email address for MSmartHome Tech Support, or point me to where I can find it (google hasn't been my friend). I want to suggest they add an option to download data as a csv file, and (not sure how this one will be received) suggest they make a browser based version that can be accessed using a browser on a PC (or any other browser capable device for that matter), reason being I am not getting very far with my python attempts to access the Midea server.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @grahamhi think its hilarious that our industry worries about cop when all that matters is run cost.
On the subject of COP, I have to disagree because it should matter greatly. Each and every MCS-accredited heat pump in the UK has a published COP for different flow temperatures. This is the benchmark for homeowners to know that if I buy product X it'll deliver x-amount of heat and it'll use x-amount of power. This helps to understand running costs.
If I'm sold a heat pump that can deliver a COP of 4 at 45C flow to deliver 21C in the house, that's what I'd expect. If the system is installed poorly and must run at 50C or higher to deliver the required 21C I've been mis-sold the equipment and I'm paying a lot more than I should for running costs. That lowers COP, so COP does matter. It's a metric that should hold the installer base accountable for the quality of their installations.
So far, from hundreds of emails and messages I've received over the past three years, no one's heat pump comes in even close to delivering on the published COP figures from manufactures which the MCS has on record, and everyone's running costs are higher than what they've been sold.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,300 Topics
- 51.6 K Posts
- 227 Online
- 5,965 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Firstly you are getting your units mixed up which is a ...
By JamesPa , 25 minutes ago
-
RE: Electricity price predictions
Until people understanding the problem with electricity...
By Diverted.Energy , 26 minutes ago
-
RE: Buffer tank bypass on EDF Ideal heat pump installation
I would bypass the buffer tank in one of flow or return...
By JamesPa , 40 minutes ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
I agree with all of that. 220 pages is perhaps 210-215...
By JamesPa , 50 minutes ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
One of those brilliant ideas that is obvious with hinds...
By Lenny , 52 minutes ago
-
RE: Don’t Install a Heat Pump Until You Read This
@davidnolan22 Perhaps you could post some more info a...
By JamesPa , 57 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
OK. I have 2.8 for DHW and 3.4 for space heating runni...
By JamesPa , 1 hour ago
-
RE: 10kw heat pump run in 24*7 data?
Some observations: 1. I for one don't know the Vailla...
By cathodeRay , 2 hours ago
-
Heat Pump on Flat Roof Low Frequency Noise from Detached Neighbor
Hi, I have been noticing a steady 120Hz noise inside ...
By People_Noise , 9 hours ago
-
RE: Commencing on an ASHP Installation Process
Given that this thread ultimately turned out to be a di...
By Sheriff Fatman , 11 hours ago
-
Ecodan - Flow temperature spiking causing shutdown
Hi everyone, looking for some help. I am in a new bu...
By Gl3484 , 12 hours ago
-
Solis AI is on the right track to leverage the battery:...
By Batpred , 13 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Thanks James, its honestly hard to keep it tog...
By Crimson , 15 hours ago
-
RE: Extend the colder range of the weather compensation curve?
Thanks for replies. That's good to hear and wanted to ...
By TheBinMan , 15 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: KevB Manufacturer: Ideal Model: 5kW ...
By KevB , 16 hours ago
-
RE: DHW heat loss through pumps.
Hi @ngillam I don't have anything as sophisticated for ...
By Marzipan71 , 19 hours ago
-
RE: Has anyone seen this problem before? Huge anticycling times
For the information of others. Vaillent came today, che...
By jamesh , 19 hours ago
-
RE: Here is my heat pump installation with questionable COP in Italy
Hi, and welcome to the forum. I cant quite u...
By JamesPa , 1 day ago
-
I signed up to Havenwise control on the day after the h...
By Sheriff Fatman , 1 day ago
-
That's not always the case.Let's see what they say once...
By Transparent , 2 days ago