Massive Electricity Cost for Running My Air Source Heat Pump
I don't think the insulation around those four external pipe runs is adequate.
Although I can't see how they arrange themselves to pass through a 100-125mm outer sleeve, the pipe clips have already compromised the wall thickness before the flow even gets there.
I also wonder if the installer has used Split-Insulation.
If so, then the split will be gaping open on the side which faces into the wall.
The approved method is to use adhesive to join the splits,
and for all bevel-cut ends around pipe elbows.
This then gets an outer layer of 'tape' to further cover the joins.
Armaflex and Kaiflex both manufacture UV-resistant external insulation.
It's usually sold as "solar insulation" because it gets used on roof-mounted solar-thermal collectors.
Save energy... recycle electrons!
As for the steel shed, I would expect to see around 100mm thick insulation sheet for the roof,
and around 75mm for the walls and door.
It must be draft-proof,
which may require neoprene rubber gaskets to be cut and glued around the pipe-exit holes.
I can provide further construction details if required.
The adhesive will be a 'contact' type such as this from Screwfix
Pipe insulation is usually best undertaken as a DIY task...
... preferably by someone with OCD!
Save energy... recycle electrons!
@transparent Hi, I spend most of my time on international travel through work.
However, I have taken some time to check what you guys are saying and you're entirely correct.
See pics!
My first avenue was simply to get it all corrected, however I see now I will have to find the time to do most of it myself if I want it done well.
If I posted pictures of the horrific work they did in my house I think you guys would turn up with pitch forks outside their office!
If you're going to take a DIY route to fixing the pipe insulation, then you should be asking for a rebate from the installer.
To calculate this, first ask them how long it will take them to remove what's there and do it again properly.
Then use £45/hour per person and add in the cost of buying the insulation yourself.
That should provide you with a good starting point.
They'll be super busy and wanting to get on with their next job rather than fix yours.
So the option of repaying you in cash will be tempting for them.
One possibility for you to consider is to make a rectangular box around those external pipes and seal them in...
... at least for the main vertical run.
There are PVC parts used by window-fitters and firms who clad facia boards, which could be fashioned into suitable boxing.
Save energy... recycle electrons!
@transparent I couldn't agree more, my first idea when looking at it was to box it in.
There isn't enough clearance between the pipes and wall to insulate it much better.
My sons arm was recently injured quite badly, but as soon as he is fit I will lob him up in the loft to check the pipe insulation in there. I wouldn't be at all surprised if it is just the rockwool!
Absolutely!
Child labour is well suited to the task of pipe insulation in confined spaces.
To seal where pipes enter the steel shed, I'd be using offcuts of EPDM rubber roofing material.
It's excellent for shaping around joins, and easy to cut.
You can glue it directly onto existing vertical surfaces.
So it's also a good choice to seal the top of your boxing.
Save energy... recycle electrons!
I know I'm late to this but I thought it would be worth pointing out that insulation of pipe runs outside the thermal envelope of the house is a building control matter. The installers should be responsible for complying with those regulations.
The relevant sections are 4.24 to 4.26 of approved document L:
It's worth noting that the insulation thicknesses described in that document are for very high quality insulation (i.e. very low thermal conductivity and low emissivity). The building regs defer to BS 5422 for lower performance insulation, and that can have a huge influence. See the attached two tables for low and high emissivity insulation, cribbed from a verv old copy of BS 5422.
If we take 22mm pipe as a reference. The really high quality insulation would require only 8mm thickness, but if it was high emissivity then that would increase to 11mm and if it then had high thermal conductivity typical of the sort of neoprene like insulation (~0.04 W/mK) then you'd need 23mm insulation to meet the regulations. That's a big jump from 8mm!
As an aside, the building regs are a great source in some areas like this. IMHO they're easy to read and a model of clarity.
I agree @mark-h The Building Regs are now very readable...
... although I do miss the sections of 'advisories' and illustrations of acceptable practices which used to be present.
There's an additional problem when selecting external pipe insulation because it has to be UV resistant of course.
The range of sizes available for installers to choose from is therefore reduced,
and especially so if they wish to use larger bore insulation around valve bodies.
Pipe Lagging offer a selection of 'solar' pipe insulation online, but it's expensive once you opt for sizes outside the common pipe diameters.
Another option is to swathe UV-resistant tape around the odd-sized sections and bends.
But my own experience with this approach is that the adhesive on the tape isn't good enough to hold firm around tight corners.
It needs supplementing with contact-adhesive at the edges.
There are also anti-UV paints which can be applied on top of existing insulation...
... provided it hasn't already been degraded of course!
Save energy... recycle electrons!
Currently viewing this topic 1 guest.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 59 Online
- 3,410 Members
Join Us!
Latest Posts
-
@jamespa Thanks. I did not instruct them not to insul...
By Eliuccio , 3 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
To update an ESP device using ESPHome in Home Assistant...
By Grantmethestrength , 4 hours ago
-
RE: Compressor and Evaporator Stratification
@trebor12345 I must admit I noticed that about Hitachi ...
By ASHP-BOBBA , 5 hours ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 3 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 3 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 4 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 4 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 6 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 1 week ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 1 week ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 1 week ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 1 week ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago
Members Online
No online members at the moment