I've been running the system now on weather compensation only for a few weeks and as I said before, it's working well for us. Some of that time I've had the heating running 24/7 and some off for 5 hours 12-5am.  I've messed around a bit with the HW but we use so little at the moment (electric showers and dishwasher) it should make little difference. This is the story so far
Â
Blue is running the ASHP 24 hrs a day, red is 5am to midnight. I removed a couple of early outliers from when I was experimenting. An exponential trend is the best fit. You can see that at the colder end, it makes a difference with the heating off at night; at the warmer end less so. I think this is because when it's cold, having the ASHP off for 5 hours makes a big dent in overall consumption. This is offset a bit by a big peak at 5am to heat the flow from cold but not completely. When it's warmer the overnight consumption is low, so not so much saved and at 5am the ASHP still has to raise the flow from room temperature to its target.Â
The other thing to bear in mind is that I don't force the house to warm up; it does it as and when with the weather compensation flows. If I were using auto adaptation I think the flow temp would increase until the house warmed up, which would give me a warmer house but lessen any saving from having the 12-5am break. We're happy with this as we don't want the house too warm at night. (We also have TRVs on the bedroom radiators that we can adjust if we want.)
What I'm going to do next is try something I've never done, which is to use a fixed flow temperature of 45C and control the house via the thermostats.  This is something a lot of people do with ASHPs and how some suppliers set up new installations. The next week or so looks quite benign for weather so an ideal time. I'm willing to experiment but don't want to bankrupt myself. I'll set both my zones for 21C constantly and I'll leave the heating off 12-5am as I've been doing most recently. I'll put the thermostats where the temperature is most stable, i.e. not in the hall/kitchen. I'll plot the results on the chart above and see what I get. Â
Any predictions? Mine is that it will cost me more! My average flow temp is about 35C to bumping it to 45C is going to make a difference. What I'm not sure about is the effect of the thermostat switching the ASHP on and off but we'll see.  Â
  Â
Posted by: @kev-mAny predictions? Mine is that it will cost me more! My average flow temp is about 35C to bumping it to 45C is going to make a difference. What I'm not sure about is the effect of the thermostat switching the ASHP on and off but we'll see.  Â
  Â
I did a similar experiment but using a 50ºC flow. That used 930kWh over 30 days vs 855kWh using the compensation curve. Both 30 day periods had an average 6.4ºC ambient outside temp.
Posted by: @kev-mAny predictions? Mine is that it will cost me more!
  Â
I would agree. Also, thanks for keeping this thread updated, very useful data.
Â
I wonder what your current weather compensation curve is set to?
Doesn't seem to making a huge difference. Couple of kW?Â
Here are the results of my experiment to compare (1) Weather compensation only and (2) Constant flow temp and thermostats. Both methods kept the house at c. 21C and switched the heating off 12-5am.Â
The weather compensation method seems to use less energy. If you look at some detail, you can see why. Â
The weather compensation energy use is very steady, apart from a blip due to HW. The thermostat energy use is much more variable. The flow is allowed to cool several times and it takes a lot of energy to raise the temperature. 100 on the left scale corresponds to 6kW.Â
In terms of 'feel'; the thermostat method results in noticeable rises and falls in room temperature with radiators varying between hot and cold whereas with weather compensation the room is more constant and the radiators are always warm.Â
The house warms up in the morning a little quicker using the thermostats. However, my previous experiment showed that I could leave the weather compensation method running all night at very little increased cost.
In terms of COP, my actual COP is showing as 7.1 (weather comp) and 5.4 (thermostats). I don't believe these numbers (someone is coming today to investigate) but their relative sizes are probably right. If I said 3.55 and 2.7 that might be believable. Â
Anyway, I'm convinced by weather compensation and I've now gone back.Â
Any requests for further experiments? 😉 I may try bumping up the weather compensation curve a couple of degrees and letting the thermostats limit the room temperature as a bit of a compromise. Â
 Â
Â
Â
I have one of those and still await delivery of the Mitsubishi wireless receiver unit. When i arrives the intention is to swap out the Heatmiser Neostat the installer thought was preferable.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
I thought you were getting the full monty wireless controller. This is just a room thermistor. I have to wire this in to the main FTC6 control box and mount it in the living area. I can then use the wired in controller in the airing cupboard to control the temperature. This is the cheap (£16.99) version!
@kev-m you’re correct Kev. My mistake.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 25 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@heat-pump-newbie as I suspected. I measure/monitor my ...
By Old_Scientist , 46 minutes ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 5 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 1 day ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 1 day ago
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 2 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 2 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 3 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 4 days ago
-
RE: How much am I ‘saving’?
@old_scientist like for like comparisons are almost imp...
By Tim441 , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 4 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 6 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 6 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 6 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 7 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 1 week ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 1 week ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 1 week ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago