Inventor (Midea) Heat Pump short cycling advice
Hello, I have a Inventor (Midea) 8kW with a 800meters Φ10 pipes under-floor heating system of total ~50L water volume (there is also a magnetic filter and an electronic vavle to switch between dosmetic waters boiler and the ufh. No extra expansion vessel (just the HP's) no extra circulation pump (just HP's internal). Currently, in COOL mode (Greece 😀 )
At manifold I have the "glass things" turned full for max flow (pump after 5-6 mins run shows 1.52m³/h). I have tried everything water temp target for start/stop (T1), thermostat for start/stop (with cooling curve for water T1S C1 to 18C) but it always the pump will cool the water very much under the water temp target T1 which fire the stop or the T1S C1 temp (so thermostat is still on but compressor stops) which results in compressor running only for 5-17mins TW_O goes 17 and TW_I 20 or 21 (ΔΤ 3-4) and pump stop since it drops under the 18C even though room temp is 27 and the thermostat set temp is 24.
It supposed the heat pump's inverter would kick in and instead of overshooting to 17C temp it should slow down (decrease Watts) and run the TW_O close to 18.XC but not lower than that. I have also tried to power limit it (Midea advanced users know) to step 5 which reduce Ampers to 12 but still nothing heat pump will cooldown the TW_O below the water temp target and make the heat pump stop for 5 mins.
Only time it ran more than 20 mins was when I set water temp to 12C and it dropped the water temp to 15C and stop it to avoid develop water all over the house xD.
House in Greece (warm climate) with A+ isolation (EP<0,33Rr)
I have been told to install a 80L tank in series(2 pipes) in returning water pipes (just before reaching back to heating pump). Should that help? Is there any other configuration I'm missing that would slow down the compressor/inverter?
Thanks in advance
Below is the power consumption of the heat pump which shows the short-cycling
Your short cycling is occurring because the heat pump can't modulate down enough to match the demand.
If you increase the system volume as suggested it still won't be able to modulate low enough but the cycles will get longer and less frequent, which is desirable.
So yes that should help.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Yes exactly, that's what stubborn. Pump doesn't modulate to work in "idle" because that's why the inverter is right? to drop "low rev" consume low power and just try to keep the water temp constant (so when target water is set to 18C it tries to stay 18.X but in my case it also drops to 17.X which cause a compressor stop.
Would adding an extra pump (apart of HP's internal) will help? By increasing the water flow will be able to bring back more "high" temp water (we are in cooling mode 😀 ).
Manufacturer manual also shows install cases without buffer but my current install is ~ 40L water for 8kW pump (5L/kW instead of 15+L xD )
Thanks James for the heads up xD I will install the tank monitor and maybe contact the manufacturer directly (well not the real manufacturer since the "brand" is inventor but it's built by Midea)
Do we know how the modulating works? If pump checks the outgoing water temp TW_O or incoming water temp TW_I or both (ΔΤ TW_I-TW_O)?
Posted by: @immunityYes exactly, that's what stubborn. Pump doesn't modulate to work in "idle" because that's why the inverter is right? to drop "low rev" consume low power and just try to keep the water temp constant (so when target water is set to 18C it tries to stay 18.X but it also drops to 17.X which cause a compressor stop.
Yes but... it can only modulate so low. If the demand is less than the min modulation the water temperature will overshoot(heating)/undershoot(cooling) and the heat pump will stop for a while, then restart (ie cycle).
Posted by: @immunityWould adding an extra pump (apart of HP's internal) will help? By increasing the water flow will be able to bring back more "high" temp water (we are in cooling mode
).
No. Assuming your emitters are large enough the demand is determined by the room temperature in relation to the flow temperature.
Posted by: @immunityManufacturer manual also shows install cases without buffer but my current install is ~ 40L water for 8kW pump (5L/kW instead of 15+L xD )
Indeed. If your system volume is sufficiently large there is no need for a volumiser.
There are actually two factors which depend on system volume namely defrost and cycling. Manufactures generally quote the minimum system volume needed for defrost. At this (quite low) system volume its quite likely the heat pump will short cycle when the demand exceeds the minimum modulated output, but the heat pump can cope with that by having a min cycling time, so manufacturers dont necessarily consider that its necessary to insist on sufficient colume to extend the cycles.
40l is a low system volume for 8kW. My system volume is 200l for a similar capacity pump.
Note increasing the system volume will NOT stop cycling, it will merely reduce the frequency. Neither will it significantly change the on/off ratio. Fundamentally it must cycle to match average output to demand.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
40l is a low system volume for 8kW. My system volume is 200l for a similar capacity pump.
Ye I see you have 7kW pump xD and 200L hm I might need a bigger volumizer tank xD.
Note increasing the system volume will NOT stop cycling, it will merely reduce the frequency. Neither will it significantly change the on/off ratio. Fundamentally it must cycle to match average output to demand.
I've also tried the power limitation with no luck (maybe when I add the extra 80L might work) I see compressor amp 4 when it start the circle, 3A-2A afterwards (probably trying to modulate)
So will probably need to go to smaller HP 4kW or 6kW?
Posted by: @jamespaThere are actually two factors which depend on system volume namely defrost and cycling. Manufactures generally quote the minimum system volume needed for defrost. At this (quite low) system volume its quite likely the heat pump will short cycle when the demand exceeds the minimum modulated output, but the heat pump can cope with that by having a min cycling time, so manufacturers dont necessarily consider that its necessary to insist on sufficient colume to extend the cycles.
Thank you very much again for the info 😀
Posted by: @immunitySo will probably need to go to smaller HP 4kW or 6kW?
Whoa. Is it also used for heating? If so then it needs to be sized to meet your heating demand. Also beware, some low output heat pumps are simply high output ones derated in firmware. That reduces max output but doesnt change min output. Personally Id fit a tank and let it cycle unless there is a good reason to do otherwise. Is it cooling sufficiently?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaWhoa. Is it also used for heating? I
Yeap also for heating (25-26C room temp, set water temp 27-28C, renovated appartment 15cm isolation, very good isolated windows etc :D)
Heating is working better xD I have 2-4kWh consumption per day. the Cooling is that hitting 10-12kWh per day and I want to fix this (it short-cycling every 10-16 mins)
Posted by: @jamespaIs it cooling sufficiently
Nope. On hot days 40C I wasn't able to drop room temperate under 30C and that's because it short-cycling so the indoor floor (ufh only, no fan coils) can't drop temperature under 23-25C. I have added ceil fan/lights (reverse sucking) which helped drop the room temp 1-2C. I tried to switch from uhf to fancoil and set the water temp 12C for like 1-2 hours which then dropped the temp and was "able" to cool but the power increased to 1.6kW (from ~700kW) and of course I feared water will start developing in surcafes and don't know if the tiles develop any problem with that low temp xD [compressor didn't stopped water reached till 14C before I stop it my self]
Posted by: @immunityHeating is working better xD I have 2-4kWh consumption per day
Do you mean kWh/day? Thats essentially nothing unless its just for DHW? You arent doing any material space heating on 2-4kWh/day!
Is it possible you are confusing kW with kWh?
Posted by: @immunitythe Cooling is that hitting 10-12kWh per day and I want to fix this (it short-cycling every 10-16 mins)
Thats not necessarily unreasonable
Posted by: @immunityOn hot days 40C I wasn't able to drop room temperate under 30C and that's because it short-cycling so the indoor floor (ufh only, no fan coils) can't drop temperature under 23-25C.
Short cycling shouldn't really affect that much how low the floor temp will go, the heat pump is simply not seeing sufficient load hence the cycling and if you want it lower you will need to reduce the flow temperature to increase the load (which will also help with short cycling).
There is debate over how effective UFH is for cooling, practically it seems to be OK in the UK but of course we don't generally get as hot as you. The problem you have (same with radiators/coiling) is that cool air sinks, so (unlike with heating) there is no convection current to mix up the air in the room, so the cool air stays near the floor thus limiting the output of the emitters. Adding fans just to circulate the air may well help.
Posted by: @immunityI tried to switch from uhf to fancoil and set the water temp 12C for like 1-2 hours which then dropped the temp and was "able" to cool but the power increased to 1.6kW (from ~700kW) and of course I feared water will start developing in surcafes and don't know if the tiles develop any problem with that low temp xD [compressor didn't stopped water reached till 14C before I stop it my self]
Whats the dew point at your location. if you run a couple of degrees above dew point your shouldnt get too much condensation. Some heat pumps can measure the dew point so do this automatically, not sure if Midea has this feature.
It sounds like you have two problems namely
1. Insufficient output from your cooling to give adquate cooling. To fix this you have to cocus on increasing the output from the emitters by (a) fans, (b) lower flow temperature (c) increasing the area of the emitters
2. Short cycling. If you fix this then problem (1) may go away. If not then a volumiser will help.
I would concentrate on (1) before getting too hung up on (2)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Yeap 4kWh/day for heating (not DHW) for keeping room temp 24-26C (water target 27-28C)
(2340- 2093kWh in 31 days in graph there is also the power consumption for DHW although some days solar cylinder had enough hot water so HP didn't heat its DHW boiler)
Heat pump short-circling also on winter (HEAT mode) but need to work much less times in a day so that's why the low daily comsuption.
Of course uhf is worst for cooling (cold air acts as isolation at the bottom, the opposite in heating that helps circlulate hot air in room) That's why I added the ceiling fans(a) 😀 to add that circulation and it helped.
(c) is not possible since can't modify the ufh now 😀 and (b) I am not that afraid of dew point more of doing damage overtime to tiles, tile's glew etc + it's not that nice to feel 15C on your feet xD
I have dehumidifier trying to keep humidity 50% or lower (getting full 1-2 times per day [5l tank])
So 1(a) and (2) 😀
Thanks again!
Posted by: @immunityit's not that nice to feel 15C on your feet xD
True!
Posted by: @immunitySo 1(a) and (2)
I think so, or fit fancoils! From your figures the system is more for cooling than it is for heating.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I switched to "fan coil mode" to be able to set water temp lower than 18C.
I used 15C to increase the load as you mentioned together with power limit and currently it modulates ? 😀 (outside it's 32C)
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 23 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 2 hours ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 6 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
Hello, unfortunately i did not take any photos, but you...
By ThunderMink , 7 hours ago
-
RE: Solar Thermal DHW and ASHP
Since you already have the ashp it makes little financi...
By Judith , 15 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
I think you’ll find it depends on the room heat loss. A...
By Judith , 16 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 16 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil Fwiw I have the 7kW model with which I'm, ver...
By JamesPa , 17 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@grahamf you appear to value your recirculating loop de...
By Judith , 17 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 18 hours ago
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 21 hours ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 22 hours ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 2 days ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 3 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 3 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 3 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 3 days ago